    Originally posted by eyyopomps
    Wouldnt I be able to still obtain the credit for all equipment purchased new? I got the panels for $100 a piece. and the inverter new for $400, so I figured even if I dont qualify the cost to do this myself will be much lower than having a company put a new array in. I figured with with the remainder of the stuff I still need the cost will be around 2500 for a ~3.5kw system so payback period should be pretty low.
    The answer to your question is probably yes, at least for equipment that you can prove to the IRS is not used should an audit or question come up.

    But, I'm not a CPA qualified and knowledgeable about the IRS code, and don't play one on TV, so anything I write or offer as information in the tax realm is purely speculation and not to be taken as fact. Consult your qualified tax advisor.

    Comment

    • eyyopomps
      Junior Member
      • Feb 2019
      • 20

      #62
      Originally posted by J.P.M.

      The answer to your question is probably yes, at least for equipment that you can prove to the IRS is not used should an audit or question come up.

      But, I'm not a CPA qualified and knowledgeable about the IRS code, and don't play one on TV, so anything I write or offer as information in the tax realm is purely speculation and not to be taken as fact. Consult your qualified tax advisor.
      Right, well thanks for the info, i'll worry about the tax credits once I get this baby in operation!

      Was wondering if you could give me any other pointers/ advice. I was looking at the iron ridge system, cause i'm also in hurricane county. I'm not really entire sure which mount id use for this system, I have a corrugated metal roof, so I dont think I need flashing and I cant use the clamp mount system.
      My house is brand new with a hip style roof, so I can everything mounted south and the trusses should be adequate for the weight.

      Comment

      • eyyopomps
        Junior Member
        • Feb 2019
        • 20

        #63
        Like I had mentioned before, I was looking at using channel struts since they're cheap and I can get them locally, however I dont think that'll pass considering they probably dont have wind ratings.

        Comment

        • ButchDeal
          Solar Fanatic
          • Apr 2014
          • 3802

          #64
          Originally posted by eyyopomps
          I was looking at the iron ridge system, cause i'm also in hurricane county. I'm not really entire sure which mount id use for this system, I have a corrugated metal roof, so I dont think I need flashing and I cant use the clamp mount system.
          My house is brand new with a hip style roof, so I can everything mounted south and the trusses should be adequate for the weight.
          S5! has several mounts that will work with most metal roofs. https://www.s-5.com/products/clamps-brackets/
          Ironridge has an online site designer that will help you get it set up. just use the L-Foot option since you will add the S5! mounts under the L bracket and not the ironridge flashfoot.
          OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

          Comment

          • eyyopomps
            Junior Member
            • Feb 2019
            • 20

            #65
            Originally posted by ButchDeal

            S5! has several mounts that will work with most metal roofs. https://www.s-5.com/products/clamps-brackets/
            Ironridge has an online site designer that will help you get it set up. just use the L-Foot option since you will add the S5! mounts under the L bracket and not the ironridge flashfoot.
            Thank you!

            Comment

            • J.P.M.
              Solar Fanatic
              • Aug 2013
              • 14926

              #66
              Originally posted by eyyopomps

              Right, well thanks for the info, i'll worry about the tax credits once I get this baby in operation!

              Was wondering if you could give me any other pointers/ advice. I was looking at the iron ridge system, cause i'm also in hurricane county. I'm not really entire sure which mount id use for this system, I have a corrugated metal roof, so I dont think I need flashing and I cant use the clamp mount system.
              My house is brand new with a hip style roof, so I can everything mounted south and the trusses should be adequate for the weight.
              For what, if any, value the info may have, you are most welcome.

              Other than rereading my 11/17/2017 post to this thread, I'd only further suggest you see what your local AHJ may want or will accept and so avoid any surprises, and then consider Butch's suggestions, and go from there.

              I'd also consider a look at ASCE 7-13, etc. for a taste of what a good wind design/review may require.
              Last edited by J.P.M.; 02-28-2019, 11:24 AM. Reason: Corrected ASCE 7-1 to ASCE 7-13.

              Comment

              • eyyopomps
                Junior Member
                • Feb 2019
                • 20

                #67
                In my solar design tool, it made me realize I may have missed a piece of my plan/ materials list. The rapid shut down device. Are these components pretty universal? My array is going to 2 6 panel strings, and my inverter is going to be on the other side of my house. (so way further than 10 feet) Do I just need one of these devices where all wires series'd together? are these devices compatable with all string inverters? looks like theyre relatively cheap on ebay. https://www.ebay.com/itm/Delta-Soliv....c100010.m2109

                Comment

                • ButchDeal
                  Solar Fanatic
                  • Apr 2014
                  • 3802

                  #68
                  Originally posted by eyyopomps
                  In my solar design tool, it made me realize I may have missed a piece of my plan/ materials list. The rapid shut down device. Are these components pretty universal? My array is going to 2 6 panel strings, and my inverter is going to be on the other side of my house. (so way further than 10 feet) Do I just need one of these devices where all wires series'd together? are these devices compatable with all string inverters? looks like theyre relatively cheap on ebay. https://www.ebay.com/itm/Delta-Soliv....c100010.m2109
                  You will need to determine which rapid shutdown code you need to follow NEC 2014 or NEC 2017
                  and no not all equipment is compatible. you will need to contact your inverter manufacturer to see or have a completely independent system
                  OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                  Comment

                  • eyyopomps
                    Junior Member
                    • Feb 2019
                    • 20

                    #69
                    Originally posted by ButchDeal

                    You will need to determine which rapid shutdown code you need to follow NEC 2014 or NEC 2017
                    and no not all equipment is compatible. you will need to contact your inverter manufacturer to see or have a completely independent system
                    Isn't the only difference the 10' vs 1' mounting change? What would you mean by independent system? Sorry for all the questions but specs and compatibility seem difficult to find online unfortunately. We really most of the details to creating a system are tough to uncover.. My county permitting process is also very vague. would be helpful if I knew someone that was familiar, my neighbor is a master electrician but doesnt really know anything about PV.

                    Comment

                    • ButchDeal
                      Solar Fanatic
                      • Apr 2014
                      • 3802

                      #70
                      Originally posted by eyyopomps
                      Isn't the only difference the 10' vs 1' mounting change?
                      well sort of. With NEC2017 you need PV module level rapid shutdown
                      with NEC 2014 you need panel level ( a Panel is a group of PV modules in a single contiguous plane).

                      Originally posted by eyyopomps
                      What would you mean by independent system?
                      A complete rapid shutdown system that is works completely independently of the inverter with its own triggering equipment. this may not be available if you need NEC 2017.

                      Originally posted by eyyopomps
                      Sorry for all the questions but specs and compatibility seem difficult to find online unfortunately. We really most of the details to creating a system are tough to uncover.. My county permitting process is also very vague. would be helpful if I knew someone that was familiar, my neighbor is a master electrician but doesnt really know anything about PV.
                      Your neighbor should know if your state has moved to following NEC 2017 or NEC 2014. you can also look it up on a few sites.
                      Discover which edition of the NFPA 70, National Electrical Code® (NEC® ) is enforced in your state.
                      OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                      Comment

                      • eyyopomps
                        Junior Member
                        • Feb 2019
                        • 20

                        #71
                        Originally posted by ButchDeal

                        well sort of. With NEC2017 you need PV module level rapid shutdown
                        with NEC 2014 you need panel level ( a Panel is a group of PV modules in a single contiguous plane).



                        A complete rapid shutdown system that is works completely independently of the inverter with its own triggering equipment. this may not be available if you need NEC 2017.



                        Your neighbor should know if your state has moved to following NEC 2017 or NEC 2014. you can also look it up on a few sites.
                        https://www.nfpa.org/NEC/NEC-adoptio...-adoption-maps
                        Hey Butch, I got some feedback from solardesigntools about my system, the inverter I have purchased does have positive grounding capabilities because I guess thats what the sunpower panels I bought use..(man I really got ahead of myself by buying these panels before doing all the research) also seems theyre a lot older than I thought they were.. My county uses NEC 2014, so I think I can use the independent system you mentioned. Do you know where I would purchase this system? I went ahead and reached out to someone named Doug at https://www.solarschematics.com/ to see if he can make my plans.

                        "Hi James,
                        I'm investigating why a single-line diagram could not be created for your system. The short reason is that these modules are so old that it is not possible to create a system with them that will comply with current electrical and fire codes. Therefore, the system just aborts the creation of an electrical diagram. (But it should have provided you with a more helpful note in the instructions about this)

                        This design includes a very (very) old Sunpower module (these are 10 years old or older). The old Sunpower modules were positive-grounded and could only be used with inverters that could be configured for positive-grounded DC arrays. At that time, the inverters were all negative grounded. Since these modules were very popular back in the day, inverter companies made it possible to configure some of their models for positive-ground in order to be compatible with the Sunpower modules. But these modules fell out of favor after a few years and Sunpower began manufacturing modules that did not require positive-grounded DC arrays. As a result, inverter companies stopped producing inverters that could be configured for positive-grounded systems. Then a few years later, tranformerless inverters (ungrounded) became popular and took over the market.

                        With the release of NEC 2014, systems with string inverters were required to provide something called "Rapid Shutdown". This meant that string inverter systems needed to include a new component that allow fire fighters to shut power off at the array within fractions of a second from an initiator located near the point of connection. Companies scrambled to produce this device before this requirement came into effect. Since the only residential inverters on the market at this time were transformerless inverters, all of the rapid shutdown devices were designed to work with ungrounded arrays. As a result, there are no rapid shutdown devices on the market that will work with positive-grounded arrays. Hence, our system is unable to create an NEC-compliant system for this module.

                        Other issues are that current fire codes require UL1703 compliance to ensure that the solar array does not reduce the fire rating of the roof it is installed on. These modules are not certified to this new standard. Additionally, when using any modern racking system, the preferred equipment grounding method (which is different then positive-grounded, negative-grounded, and ungrounded arrays) is to bond the module frames to the rails bonding clamps. But to use these the racking system needs to be certified to be UL2703 compliant when used with that specific module. These modules have not been tested with any racking system for UL2703 Grounding and Bonding compliance.

                        To design an NEC compliant system with this module, you may need to jump through many hoops. For the rapid shutdown device, I would suggest contacting Midnite solar and getting a custom combiner with relays and a ground bar in it and then hiring an experienced designer to draw up the SLD so it is compliant."

                        Comment

                        • ButchDeal
                          Solar Fanatic
                          • Apr 2014
                          • 3802

                          #72
                          Originally posted by eyyopomps

                          Hey Butch, I got some feedback from solardesigntools about my system, the inverter I have purchased does have positive grounding capabilities because I guess thats what the sunpower panels I bought use..(man I really got ahead of myself by buying these panels before doing all the research) also seems theyre a lot older than I thought they were.. My county uses NEC 2014, so I think I can use the independent system you mentioned. Do you know where I would purchase this system? I went ahead and reached out to someone named Doug at https://www.solarschematics.com/ to see if he can make my plans.


                          To design an NEC compliant system with this module, you may need to jump through many hoops. For the rapid shutdown device, I would suggest contacting Midnite solar and getting a custom combiner with relays and a ground bar in it and then hiring an experienced designer to draw up the SLD so it is compliant."
                          Midnight solar makes a complete system for rapid shutdown that is NEC 2014 compliant, with the addition of their "Bird house" control unit.

                          SMA has a rapid shutdown solution that will be as well with the addition of their RSC-1X-US-10 control unit.

                          There are others but I would suggest the midnite solar one as people will be most familiar with it and it has been around a while.


                          Last edited by ButchDeal; 02-28-2019, 11:04 AM.
                          OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                          Comment

                          • Batikikik
                            Junior Member
                            • Mar 2017
                            • 1

                            #73
                            Hello Tundra,
                            We have used <link removed> This tool helps you to design the system and get quotes but if you want to do yourself they provide you with Enginering package + permit for $350. I will highly suggest to use them

                            Moderator note: Posting links in your first post looks like advertising. No ads please. If that is not what you were doing, let us know and we will let you re-post the link.
                            Last edited by sdold; 02-28-2019, 12:04 PM. Reason: Removed link

                            Comment

                            • eyyopomps
                              Junior Member
                              • Feb 2019
                              • 20

                              #74
                              Originally posted by ButchDeal

                              Midnight solar makes a complete system for rapid shutdown that is NEC 2014 compliant, with the addition of their "Bird house" control unit.

                              SMA has a rapid shutdown solution that will be as well with the addition of their RSC-1X-US-10 control unit.

                              There are others but I would suggest the midnite solar one as people will be most familiar with it and it has been around a while.

                              Since im under NEC 2014, it seems like I could avoid the rapid shutdown by also just mounting the inverter within 10 feet? Not ideal for the way I wanted my design, but I could make it work. I do need to go meet with someone at my permitting office, I was just trying to have as much understanding as possible first.

                              Comment

                              • ButchDeal
                                Solar Fanatic
                                • Apr 2014
                                • 3802

                                #75
                                Originally posted by eyyopomps

                                Since im under NEC 2014, it seems like I could avoid the rapid shutdown by also just mounting the inverter within 10 feet? Not ideal for the way I wanted my design, but I could make it work. I do need to go meet with someone at my permitting office, I was just trying to have as much understanding as possible first.
                                It is possible but the inverter would need to be accessable at that location.
                                OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH