14/3 wire has four conductors, usually two hots (red and black) a neutral (white) and a separate uninsulated ground. If it's Romex (most common) it is then wrapped in a white plastic sleeve to hold it all together.
From what you've said, you won't need more than 14/2. (Which is probably what you have.) That's three wires - one white and one black (for power; hot and neutral) and a bare ground.
You only need GFCI one per outlet string. All the outlets downstream of the first GFCI outlet are protected by the first one.
Nothing. (Breakers don't either.)
What Mike meant is that regular breakers won't trip. Let's say you go with the Suresine 300, which is an excellent inverter BTW. The most power it will put out is 600 watts, which is 5 amps. So if you have 15 amp breakers, they will never trip, because the current will never get above 5 amps for any amount of time. And those breakers need 15 amps to trip.
So what happens? The inverter, rather than the breaker, provides the protection. In this case it's safe because 14/2 can easily handle the fault current that the SureSine can provide.
GFCI receptacles don't give you surge protection either.
Quick aside on terms - there are a few things you might be talking about when you say "surge." The electrical meaning of that is an overvoltage caused by generator overspeed or flyback voltage or lightning strike; this can damage devices that are plugged in. Surge protectors clamp this voltage to a safe level.
You might mean overcurrent, which is what circuit breakers normally protect against. In this case you are relying on the inverter for that.
You might mean ground fault, which is a situation where some current is returned to ground rather than the real return. To use your 14/2 Romex as an example, all the current flows through the two power leads - it flows out through black (hot) and returns through white (neutral.) None should ever return through ground. If some does, then there's a good chance that something is wrong. Maybe you grabbed the hot prong of a cord while you were unplugging it. Maybe you were trying to use a metal knife to get some toast out of a toaster and touched the heating element. And now some of that current is flowing through you to ground instead of through the neutral like it's supposed to. It's a tiny current - more like 15 milliamps than 15 amps - so a regular breaker won't blow. GFCI's detect that small amount of current and trip open, thus protecting the person with the knife.
From what you've said, you won't need more than 14/2. (Which is probably what you have.) That's three wires - one white and one black (for power; hot and neutral) and a bare ground.
are you saying I should use all gfci receptacles?
and what would protect the ac line that is hardwired to the inverters from surge?
What Mike meant is that regular breakers won't trip. Let's say you go with the Suresine 300, which is an excellent inverter BTW. The most power it will put out is 600 watts, which is 5 amps. So if you have 15 amp breakers, they will never trip, because the current will never get above 5 amps for any amount of time. And those breakers need 15 amps to trip.
So what happens? The inverter, rather than the breaker, provides the protection. In this case it's safe because 14/2 can easily handle the fault current that the SureSine can provide.
in this situation I'm relying on the gfci receptacles as the surge protection?
Quick aside on terms - there are a few things you might be talking about when you say "surge." The electrical meaning of that is an overvoltage caused by generator overspeed or flyback voltage or lightning strike; this can damage devices that are plugged in. Surge protectors clamp this voltage to a safe level.
You might mean overcurrent, which is what circuit breakers normally protect against. In this case you are relying on the inverter for that.
You might mean ground fault, which is a situation where some current is returned to ground rather than the real return. To use your 14/2 Romex as an example, all the current flows through the two power leads - it flows out through black (hot) and returns through white (neutral.) None should ever return through ground. If some does, then there's a good chance that something is wrong. Maybe you grabbed the hot prong of a cord while you were unplugging it. Maybe you were trying to use a metal knife to get some toast out of a toaster and touched the heating element. And now some of that current is flowing through you to ground instead of through the neutral like it's supposed to. It's a tiny current - more like 15 milliamps than 15 amps - so a regular breaker won't blow. GFCI's detect that small amount of current and trip open, thus protecting the person with the knife.