Tiny House Solar, Wiring Inverter to AC Electric

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Falsa_Nominis
    Junior Member
    • Mar 2018
    • 20

    #16
    Originally posted by jflorey2
    Perhaps learning more before giving bad advice on line would be wise. You'd probably regret it if your advice resulted in an injury or a fire.
    I see this board has its share of idiots that try to beat down the new guys.

    If the GFCIs would not work that way, the engineers that design inverters would not include GFCIs in the inverters. You insulted the design engineers. Good luck in convincing anybody with more then three active brain cells, that you know what your talking about.

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #17
      Originally posted by Falsa_Nominis

      It is built in to the inverter, If you could relocate it, doing so would leave a branch unprotected. Are you trying to get the OP killed? However GFCI outlets would not be a bad idea.
      GFCI is NOT always built into the inverter. While you may know something about electricity, you obviously are new to solar power I've got 2 major brand, top of the line inverters, that do not contain GFCI in them, only internal DC overload protection.
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • J.P.M.
        Solar Fanatic
        • Aug 2013
        • 15015

        #18
        Originally posted by Falsa_Nominis

        I see this board has its share of idiots that try to beat down the new guys.

        Sure does, and not that he and I always agree, but to my observation, jflorey2 probably isn't one of them.

        There are also a lot of newbies and others who are inexperienced with respect to the in/outs of solar electricity.

        Know what you're talking about around here or accept the risks that go with posting to the forum of few(er) illusions.

        While there are a lot of ill/mis informed folks who show up here, there are also a lot of experienced technical types who sometimes argue stuff out and usually get a workable consensus on the technical stuff or at least some exchange of informed information.

        Comment

        • erblasco
          Junior Member
          • Mar 2018
          • 5

          #19
          I appreciate all the feedback it's giving me a good sense of what not to do.

          all I currently have is a small cabin with 2 standard 14/2 lines wired to 3 receptacles and the other to 2 led overhead lights on switches

          I have not purchased any panels or an inverter. I wanted to get a sense of what was a safe way to do this off grid.

          I'd like to know why folks don't like 100watt panels? And what would be an appropriate set up for a cabin where I'm running a few lights a laptop and no major appliances.


          what I gather so far isstarting from the battery bank I need to have:

          a sine wave inverter that can be hardwired to

          ? Gauge wire

          hardwired to a breaker box (with neutral and ground fused here?)

          with electric lines going into the breaker box


          Comment

          • jflorey2
            Solar Fanatic
            • Aug 2015
            • 2333

            #20
            Originally posted by Falsa_Nominis
            I see this board has its share of idiots that try to beat down the new guys.
            More like making sure the new guys get to be old guys.
            If the GFCIs would not work that way, the engineers that design inverters would not include GFCIs in the inverters.
            Inverters intended for installation into structures do not have GFCI's for the reasons I listed.

            Inverters used for portable applications sometimes do have GFCI's - because if all you are doing is plugging an appliance in (or using an extension cord, and then plugging the appliance in) then a GFCI improves the level of safety.

            Some inverters are used for both. For example, I have a Prosine 1000 that I use for portable applications (margaritas at the beach for example.) It has a GFCI outlet on it. It also has a version that is intended for hardwire installations, like RV's or small homes. It does not have GFCI protection on the output, for reasons I listed above.
            You insulted the design engineers. Good luck in convincing anybody with more then three active brain cells, that you know what your talking about.
            No worries there. I hope you make it to being one of those old guy "idiots" - and hopefully not through trial and error.

            Comment

            • jflorey2
              Solar Fanatic
              • Aug 2015
              • 2333

              #21
              Originally posted by erblasco
              I'd like to know why folks don't like 100watt panels?
              There's nothing wrong with 100 watt panels from a functional standpoint. They are just more expensive than grid tie (200+ watt) panels. In general you are better off getting cheaper larger panels and using an MPPT charge controller to match the battery voltage.

              However, if you have a stack of old 100 watt panels that still work, or can get them for free, then no worries - they will work.

              Comment

              • Falsa_Nominis
                Junior Member
                • Mar 2018
                • 20

                #22
                all I currently have is a small cabin with 2 standard 14/2 lines wired to 3 receptacles and the other to 2 led overhead lights on switches
                If you want GFCI protection you need X/3 lines. We don't know where in the world you are therefore, we cannot deduce if your appliances are 115V/120V or 230V.

                14 gauge solid core copper wire is rated for 15 Amps. On 115V/120V that is 1725 - 1800 watts, 3450 watts on 230V. You should limit 14 gauge it to 1500 Watts on 115/120V, 3000 Watts on 230V to be safe.


                And what would be an appropriate set up for a cabin where I'm running a few lights a laptop and no major appliances.
                Your inverter size depends the Power requirements of all your loads. Sum the power requirement of all the loads. You will need a inverter larger then that sum.

                Your solar panel array size and battery bank size depend on your Energy consumption patterns and the solar resources at your location. Map out power requirements by time of day, from that you can develop a reasonable energy consumption profile.

                Last edited by Falsa_Nominis; 03-28-2018, 03:39 PM.

                Comment

                • jflorey2
                  Solar Fanatic
                  • Aug 2015
                  • 2333

                  #23
                  Originally posted by Falsa_Nominis
                  If you want GFCI protection you need X/3 lines.
                  14/2 Romex has 3 conductors (2 power, 1 ground) and is compatible with GFCI outlets.



                  Comment

                  • littleharbor
                    Solar Fanatic
                    • Jan 2016
                    • 1998

                    #24
                    The example you have provided certainly does have a ground plus two conductors.
                    Here's a quote from Mike Holt's forum by a senior member.

                    "When nonmetallic-sheathed cable came on the scene I'm guessing late thirties or early fortys it did not have a ground. Ground wire was added Im guessing again around the early to mid fifties and it was a reduced ground. Full sized ground wire came about in mid to late sixtys along with the infamous alumium nonmetallic-sheathed cable. All dates are aprox."
                    Last edited by littleharbor; 03-28-2018, 05:38 PM.
                    2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #25
                      If you are still in the build out process of the tiny house, use standard household wiring (romex with ground wire) so that if you NEED to upgrade to a microwave, you won't have to rip wires out.

                      Morningstar has a nice efficient 300W inverter rated to be hardwired in, and will support being connected to outlets via GFCI. (suresine 300, 600w surge 10 min)

                      AC circuit breakers are less useful than one would expect, because of limited power the inverter can supply, won't always rapidly trip a breaker.. GFCI's will trip on a small leakage fault.
                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • erblasco
                        Junior Member
                        • Mar 2018
                        • 5

                        #26
                        My bad it is 14/3 wire I used. It has hot neutral. And ground

                        Comment

                        • erblasco
                          Junior Member
                          • Mar 2018
                          • 5

                          #27
                          Mike90250-

                          are you saying I should use all gfci receptacles?

                          and what would protect the ac line that is hardwired to the inverters from surge?

                          in this situation I'm relying on the gfci receptacles as the surge protection?


                          ps thanks for the post that inverter looks very good for what want to do

                          Comment

                          • Brian53713
                            Solar Fanatic
                            • Oct 2016
                            • 167

                            #28
                            With Renogy 100 watt panels being about a dollar a watt and free shipping, nobody has ever answered my question from months ago how do you get those larger panels delivered? Also much easier to deal with. And sturdier I have heard from you experts. And if it's a tiny house, easier to fit more 100 Watters

                            Comment

                            • littleharbor
                              Solar Fanatic
                              • Jan 2016
                              • 1998

                              #29
                              Buy them locally. Don't have to pay shipping.

                              You wont need more panels. They are usually 39" x 65" or 39" x 77" for the 300+ watt panels. Do these dimensions work out with your roof.
                              2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                              Comment

                              • PNPmacnab
                                Solar Fanatic
                                • Nov 2016
                                • 425

                                #30
                                I started out with 100W panels and went to grid tie. I store my panels at the end of the season and handling them isn't that bad. I run a 60V system which allows me to easily heat water with excess solar energy. I bought 280W panels locally for $170 without problems. You don't need to live like a refugee. I have everything refrigeration, hot water, even a dishwasher with heated dry with a system not much larger than that. I schedule loads on sunny days so I don't need a massive battery I have only a car battery. Panels make a nice roof or shaded outdoor area. Everybody wants to under panel. It is insane.