Thanks for this replay.
Current is shared in an ATX power supply (I have extensive experience with those) All ground wires are connected together at both ends inside the ATX PSU and on the motherboard.
Same is valid for the 4 pin or more recently 8 pin connector providing power to CPU or those for GPU.
Also the 4 pin molex or SATA connector uses the ground as common for 5V and 12V even if in that case current is small enough that a single wire can safely transport that current.
But I think inside a case a different code apply. That leads me to the question what code apply to connections inside a panel where this BMS should me mounted.
I found the NEC 310.4 but that is not specific for this use inside a panel.
There are a few solution I think that can allow me to keep current power connector (changing is not an option).
One simple is to have 20A fuses on each parallel wire in that way if there is an imperfect connection the fuses will not allow current on a single wire to exceed the limit. This I think will prevent any possible problem related to safety but just got the idea I need to investigate more.
You can only have multiple parallel connections outside the BMS or inside there is no way around since I need a minimum of 4 MOSFET's even if they are not PCB mount and you use a large heatsink as a conductor there is still current sharing.
Target is to keep this device as small and light as possible.
In the installation instruction I can state that this is a component and not a device and that needs to be installed inside a fireproof cabinet where the parallel connections can be made. In that case even without fusses for each individual wire if any of the wires or more than one gets disconnected will be protected from fire since is inside the fireproof cabinet or box.
What do you think about this or are there any other solutions that allows me to keep the current design.
Current is shared in an ATX power supply (I have extensive experience with those) All ground wires are connected together at both ends inside the ATX PSU and on the motherboard.
Same is valid for the 4 pin or more recently 8 pin connector providing power to CPU or those for GPU.
Also the 4 pin molex or SATA connector uses the ground as common for 5V and 12V even if in that case current is small enough that a single wire can safely transport that current.
But I think inside a case a different code apply. That leads me to the question what code apply to connections inside a panel where this BMS should me mounted.
I found the NEC 310.4 but that is not specific for this use inside a panel.
There are a few solution I think that can allow me to keep current power connector (changing is not an option).
One simple is to have 20A fuses on each parallel wire in that way if there is an imperfect connection the fuses will not allow current on a single wire to exceed the limit. This I think will prevent any possible problem related to safety but just got the idea I need to investigate more.
You can only have multiple parallel connections outside the BMS or inside there is no way around since I need a minimum of 4 MOSFET's even if they are not PCB mount and you use a large heatsink as a conductor there is still current sharing.
Target is to keep this device as small and light as possible.
In the installation instruction I can state that this is a component and not a device and that needs to be installed inside a fireproof cabinet where the parallel connections can be made. In that case even without fusses for each individual wire if any of the wires or more than one gets disconnected will be protected from fire since is inside the fireproof cabinet or box.
What do you think about this or are there any other solutions that allows me to keep the current design.