    AC disconnect and correct wiring for Micro inverter

    We are installing our first system using M215 Enphase micronverters
    the 6 strings will go to 4 junction boxes on 4 roofs and go to a combiner box and to the main service panel

    I was told by AC disconnect is not required by a solar material dealer and confirmed it with enphase,
    I keep seeing AC disconnect on microinverter install and Solar warning labels made for that ... make me question that again

    so can you guys please confirm if I do not need AC disconnect for the M215 install?

    2nd question, if I dont need an AC disconnect... Can I connect the string directly to the main service panel with a 20amp fuse?
    I have 2 x200 amp service panels with many empty spots

    3rd question does NY - PSEG (my electric company) inspect my system before allowing me turning it on?


    Anyone know which lables I need and where for such an install?
  • NewBostonConst
    Solar Fanatic
    • Nov 2018
    • 113

    #2
    I was required a disconnect in Michigan on my microinverter install and our power company did come out to inspect through they only went to where the meter and disconnect were located and didn't look at the array. The city looked at the array and outside breaker panel and disconnect. but not inside the house connection.

    So mine has 24 panel that go into 2 strings 12 awg. They are tied to a breaker panel at the array to protect each string with a breaker. Then the small sub breaker panel is wired 10 awg to the disconnect at the meter and then run back to a 30 amp breaker in my main panel.

    Good Luck with your install....

    Comment

    • doctorman
      Member
      • Feb 2017
      • 40

      #3
      So I guess I have to call PSEG - Long island and ask them if they require the AC disconnect despite not being required by NEC and code.

      Comment

      • J.P.M.
        Solar Fanatic
        • Aug 2013
        • 15049

        #4
        Doctorman: What others may tell you is nice, but unauthoritative and perhaps uninformed and misleading. Get the information from the source. CALL THE POCO. What's the problem with a phone call ?

        Comment

        • doctorman
          Member
          • Feb 2017
          • 40

          #5
          Originally posted by J.P.M.
          Doctorman: What others may tell you is nice, but unauthoritative and perhaps uninformed and misleading. Get the information from the source. CALL THE POCO. What's the problem with a phone call ?
          true , called but they could not answer, only by email and that takes a while

          Comment

          • J.P.M.
            Solar Fanatic
            • Aug 2013
            • 15049

            #6
            Originally posted by doctorman

            true , called but they could not answer, only by email and that takes a while
            Bureaucrats who could be replaced by paper clips making life easier for themselves.

            NOMB, but I've found the squeaky wheel gets the grease. That and a friendly request for help. Apply, iterate, repeat and climb the chain of command as necessary until a result (an answer) is obtained. The goal is an answer, not an ego boost.

            In such situations, I keep calling, or keep it in my pants. Sometimes I can't get everything immediately, but I've learned nothing can replace persistence.

            To repeat: Get the information from the source. All else is hearsay. Give the other stuff credence at your peril.

            Take what you want of the above. Scrap the rest.

            Comment

            • doctorman
              Member
              • Feb 2017
              • 40

              #7
              in email the electric company confirmed no need for AC disconnect for systems under 25KW
              but they recommend it

              another question, is there a requirement for a combiner box then , I have 6 strings
              if there is no need for AC disconnect then I can go directly to the main panel then and connet the 6 strongs to 20 amps breakers and a 10amp breaker for the envoy.
              correct?

              Comment

              • Ben25
                Solar Fanatic
                • Jul 2014
                • 135

                #8
                What size array are you installing? 6 strings seems like a lot for a microinverter system unless it's quite large.

                Comment

                • doctorman
                  Member
                  • Feb 2017
                  • 40

                  #9
                  Originally posted by Ben25
                  What size array are you installing? 6 strings seems like a lot for a microinverter system unless it's quite large.
                  80 panels at around 210W

                  Comment

                  • Ben25
                    Solar Fanatic
                    • Jul 2014
                    • 135

                    #10
                    Ahh, so quite large. Is the POCO requiring any production meter outside? Also, if it's on a roof, it needs to be rapid shutdown compliant with a disconnect that initiates the rapid shutdown in an accessible exterior location. (NEC 2017 if you're on that)
                    i would lean towards installing one...

                    Originally posted by doctorman

                    80 panels at around 210W

                    Comment

                    • Ampster
                      Solar Fanatic
                      • Jun 2017
                      • 3658

                      #11
                      Originally posted by doctorman
                      ....

                      another question, is there a requirement for a combiner box then , I have 6 strings
                      if there is no need for AC disconnect then I can go directly to the main panel then and connet the 6 strongs to 20 amps breakers and a 10amp breaker for the envoy.
                      correct?
                      Check with your local building department, but it may depend on the amperage of your strings. You said "breakers" but didn't say how many. If less than 6 you will need a combiner box because NEC prohibits splices within a service panel.
                      9 kW solar, 42kWh LFP storage. EV owner since 2012

                      Comment

                      • doctorman
                        Member
                        • Feb 2017
                        • 40

                        #12
                        Originally posted by Ben25
                        Ahh, so quite large. Is the POCO requiring any production meter outside? Also, if it's on a roof, it needs to be rapid shutdown compliant with a disconnect that initiates the rapid shutdown in an accessible exterior location. (NEC 2017 if you're on that)
                        i would lean towards installing one...


                        My plans do not specify production meter and the POCO did not mention anything.
                        my envoy S will measure the production on the inside
                        Rapid shut down should be satisfied with microinverters themselves , to my understanding no other device required

                        Comment

                        • doctorman
                          Member
                          • Feb 2017
                          • 40

                          #13
                          I am using M215 and my longest string is 15 panels long
                          6 strings ,
                          15
                          15
                          13
                          13
                          12
                          12
                          they will come inside the house in conduit with #10 THWN-2 wire , iside the house there will be no conduit and run them inside the wall to the service panel,
                          each array will be connected to it is own breaker at 20 amp, total of 6 breakers
                          1 extra 10 amp breaker for the envoy S with consumption meter rings



                          Originally posted by Ampster

                          Check with your local building department, but it may depend on the amperage of your strings. You said "breakers" but didn't say how many. If less than 6 you will need a combiner box because NEC prohibits splices within a service panel.

                          Comment

                          • NewBostonConst
                            Solar Fanatic
                            • Nov 2018
                            • 113

                            #14
                            I think THWN is required to be in conduit the whole way...even inside the house. NEC requirement.

                            How long are your runs? Could you put in a sub panel and do one run of larger Romex to the main box so you don't have to do 6 small runs in conduit?

                            Romex isn't required to be in conduit.
                            Last edited by NewBostonConst; 02-11-2019, 08:26 AM.

                            Comment

                            • SunEagle
                              Super Moderator
                              • Oct 2012
                              • 15186

                              #15
                              Originally posted by NewBostonConst
                              I think THWN is required to be in conduit the whole way...even inside the house. NEC requirement.

                              How long are your runs? Could you put in a sub panel and do one run of larger Romex to the main box so you don't have to do 6 small runs in conduit?

                              Romex isn't required to be in conduit.
                              You would also need to de-rate the amp capacity of those 12 cables (6 cable runs) if they are all in the same conduit.

                              Comment

                              Working...