Question about SolarEdge inverter sizing and clipping
SolarEdge support was happy to make the config change to the portal on request. Not sure how much of real use there, but I like to be able to make that decision rather than have it made for me.Comment
Originally posted by qweiczzI'm not sure about this. I have the SE 7600 inverter and the other day it showed 7849 W at 10:20 AM:
What is it you are not sure about with the inverter? do you have the SE7600A or SE7600H?Last edited by SunEagle; 12-11-2018, 02:09 PM.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
Hello very new member
I live in BC Canada
I have installed 32 360 w jinko panels
in my field for a total of 11.52 kw
I wanted an EV charger for my car so I used the 7600H inverter.
This was the largest one with the car charger.
I feel I could get a lot more watts out of a larger inverter.
Is it possible to parallel two inverters to increase the output
Thanks
barrye
I live in BC Canada
Thanks
barrye
I was considering adding a 3.8 kw inverter.
Does Solaredge have line drawings on how to accomplish this .
i am a home owner and I have done my own install.
i assumed i would only get clipping in the summer months.
i have been online for 3 weeks and on sunny days i draw a straight line at 7.6kw from 10 till 4pmComment
Thanks Butch.
Solaredge install shows how to configure the inverters but it is general wiring on the combiner side.
You will need an electrician to help with this somewhat as connecting more than 7.6kW often requies a lineside tap.
What is the bus ratting on your MSP? and what is the main breaker capacity on the MSP?
I have a 200 amp service.
Cable to breaker is 6awg/3.
Breaker is 50 amp as the EV part of the inverter
is set to 40 amps.
So far I have done my own wiring. Only had to redp it once (LOL)
Do you know the gauge and distance of your house hold feed wire from the electric company?
Adding an inverter may mean a change in your buy-back/net-meter contract and you may loose any currently favorable ratesPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
8 awg/4 from the panels to the inverter 6awg/ from inverter to 50a breaker.
Not sure about meter to pole..
Fortunately when I put my application in to B C Hydro i had designed a system with a 10 kw inverter
and switched ( after much teeth gnashing) to the 7.6 EV charger.
Now my wife doesn't want to buy an electric car
c'est la vieComment
I just had a 9.855 kW panel system installed with the installer's recommended SolarEdge 7600HD inverter. I've seen two sunny days in the last week with just under 4 hours straight of clipping at 7600 W each day. I felt that I should have gotten a 10000HD inverter for my 9,855 W panel array. Should I insist on replacing the 7600HD inverter with the 10000HD or is there really a benefit with my system and will the clipping not affect things too bad with 7600HD?Comment
10000 will require a 60A breaker (10000 / 240 * 1.25 = 52; next size up == 60)
So you'll need a larger breaker, larger wire size from the panel to the breaker.
And that may require additional changes to the breaker panel (like changing to a supply-side tap, or replacing the breaker panel or ....)
We would need a lot more information about how your installation was done to tell you if this would be a fairly straightforward upgrade, or if it'd likely require significant work.
If it'd require significant work, then the benefit is you didn't have to pay for that work to be done. And that extra work/cost may not have had a reasonable payoff time (maybe even never)Comment
7600 requires a 40A breaker. (7600 / 240 * 1.25 = 40)
Also, they have a solar array main shutoff before it connects to the outside electric meter. (Inverter is outside mounted to house)
Does that help answer your question?
JeffComment
7.6 kW output sounds low for a 9.9 kW array, and it's probably due to the inverter being undersized, especially if the output for 4 hrs. is dead flat at 7.6 kW. Was the reduced or flat output somewhat symmetric around solar noon +/- some ?
There's a small and quite unlikely chance the low output may be due to shading, but stranger things have happened. What was the daylong output in kWh for those two sunny days ?Comment