    Advice Plz! Cable Size for 400ah battery string??? with room to grow?

    Here is a quote from another thread
    "On the other hand, a bank of 2-3 strings of 6 volt @ 220 AH "Golf Cart" batteries is not a bad bank. It is cheap, relatively rugged and reliable, and will probably last you 3-5 years"
    looked like a good/reasonable plan IMO... I'm just starting, so my system is small (2 60 cell panels with a 40a CC) so it was recommended to use 4 x 6v golf cart batteries (which i already have some good golf cart batteries) in my cart they are wired with 4awg wire in series (36v golf cart) so i'm planning on pulling the 4 best to compose my battery bank... what size cabling should i use? I saw a video where a guy had some huge cable 2/0 looked like? I'd like to go big enough to reuse down the line (so i'm not having to rebuy/make new cables later, should i decide to grow my battery bank. Is there a certain size that is "big enough" to handle most reasonable sized battery banks? thanks!!!
  • NEOH
    Solar Fanatic
    • Nov 2010
    • 478

    #2
    Review some websites that describe "Wire Size vs Ampacity"

    like this one ...
    Ampacity is the maximum current that a conductor can carry continuously under the conditions of use without exceeding its temperature rating. Cerrowire's ampacity chart helps calculate the load requirement for a circuit.



    Comment

    • texman38
      Junior Member
      • Sep 2017
      • 38

      #3
      Originally posted by NEOH
      Review some websites that describe "Wire Size vs Ampacity"

      like this one ...
      Ampacity is the maximum current that a conductor can carry continuously under the conditions of use without exceeding its temperature rating. Cerrowire's ampacity chart helps calculate the load requirement for a circuit.


      thanks but i don't get it??? i know use-2 is the column (i guess) for pv wire but what about battery cables, they are fine strands as well. and still just would like an answer to my question 4 6volt batteries in series 24v system what size cabling? with room to grow? i can wire A/C all day long no worries, dc stuff is still a mystery, with different loads, so with a 1000w inverter hooked up, powering a refrigerator and maybe a few other small things what kind of wires do i need for my battery bank?

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        A 1Kw inverter, on 24v system, should be able to surge 2Kw. At 24V. that's 85A Then you factor the Cable length into that, so that you have less than 3% loss in the cable

        using 4 feet from the battery (* Please use one-way distance to the load. Not round trip distance.) I get #6 cable would do the job

        This free voltage drop calculator estimates the voltage drop of an electrical circuit based on the wire size, distance, and anticipated load current.


        HOWEVER - looking up the ampacity chart, #6 wire will overheat at 85A, so you must use #4 wire, good for 85A and place no larger than an 85A breaker or fuse on it.
        Ampacity is the maximum current that a conductor can carry continuously under the conditions of use without exceeding its temperature rating. Cerrowire's ampacity chart helps calculate the load requirement for a circuit.


        If you use fine strand wire, you need special lugs and crimpers rated for fine strand, or buy the wires pre-terminated from a reputable vendor (not always Joes WIre Shack on flea bay)
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • texman38
          Junior Member
          • Sep 2017
          • 38

          #5
          Originally posted by Mike90250
          HOWEVER - looking up the ampacity chart, #6 wire will overheat at 85A, so you must use #4 wire, good for 85A and place no larger than an 85A breaker or fuse on it.)
          thanks mike! great info exactly what i'm looking for... the wire has to be the fine strand type or what type is it that takes the regular copper lugs that can be made with an inexpensive crimper sold on ebay for $20... are those acceptable for wiring the batteries and/or inverter???

          Comment

          • texman38
            Junior Member
            • Sep 2017
            • 38

            #6
            Originally posted by texman38
            thanks mike! great info exactly what i'm looking for... the wire has to be the fine strand type or what type is it that takes the regular copper lugs that can be made with an inexpensive crimper sold on ebay for $20... are those acceptable for wiring the batteries and/or inverter???
            i just bought 4awg wire, terminals and the crimper, heat shrink... do i need to cancel it?
            Color: Red, Black, or 50% Black / 50% Red
            Conductor Size: 4 AWG
            Length (ft): 5 to 1000 ft
            Feet Per Pound: 6.8
            Stranding (qty. x dia): 364 / 30
            Nominal O.D. (in.): 0.331"
            Conductor Material: Copper
            Insulation Material: High Grade EPDM
            Max. Amps: 150
            Max. Voltage: 600
            Min. Temperature Rating: -50

            Comment

            • texman38
              Junior Member
              • Sep 2017
              • 38

              #7
              Is this the right stuff for making my own battery cables and to inverter?
              TEMCo 4 Gauge AWG Welding Lead & Car Battery Cable Copper Wire | MADE IN USA
              1/2" heat shrink tube

              Attached Files

              Comment

              • texman38
                Junior Member
                • Sep 2017
                • 38

                #8
                or do i need these crimpers?
                Attached Files

                Comment

                • Richiep
                  Junior Member
                  • Sep 2017
                  • 28

                  #9
                  Hey Texman,
                  I'm wrestling some of the same questions and also shopping for wire and crimping tools.

                  The largest wires I'll be using right now is 2AWG so I'm looking at this crimper


                  And this cutter


                  Here's a thread I started somewhat related to this subject. It evolved into the importance of good cripms


                  Good Luck!
                  Rich
                  12V 12W panel, SolarEpic Tracer4215BN, 12V 18Ah

                  Comment

                  • SunEagle
                    Super Moderator
                    • Oct 2012
                    • 15164

                    #10
                    Originally posted by texman38
                    or do i need these crimpers?
                    Neither that hammer crimper in your other post or this crimper will get you a proper termination for your wires. You need a hydraulic type crimper similar to the one in Richiep's post but even that one (which I own) will not do the best job on some wires.

                    If you plan on trying to save money making your own cable then at least look into purchase quality (and expensive) tools.

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #11
                      If you insist on making this a DIY, then you must realize you are not going to be making good, reliable connections with the parts & tools you have selected.
                      Cable is cable.
                      Lugs are supposed to be tin plated, so the copper does not oxidize and cause high resistance connections
                      Crimps really need to be done with hydraulic crimper. Look for the 16 ton hydraulic crimper (flea bay) and make sure it has dies for your lugs and cable.
                      Make sure your die/lug/cable all work together, sacrifice a crimp. Cut it off the cable, clamp the flat part of the lug in a vice, and with a fine blade hacksaw, cut through the middle of the crimp, slowly, gently and carefully. You want to look at the strands inside the crimp. and see if the are fused together and to the shell of the lug. If loose strands fall out, you have a wrong size somewhere.
                      Ideally, you use certified dies, that imprint their UL code into the lug.
                      CrimpLugDeformed.jpg
                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • texman38
                        Junior Member
                        • Sep 2017
                        • 38

                        #12
                        Originally posted by Mike90250
                        If you insist on making this a DIY, then you must realize you are not going to be making good, reliable connections with the parts & tools you have selected.
                        Cable is cable.
                        Lugs are supposed to be tin plated, so the copper does not oxidize and cause high resistance connections
                        Crimps really need to be done with hydraulic crimper. Look for the 16 ton hydraulic crimper (flea bay) and make sure it has dies for your lugs and cable.
                        Make sure your die/lug/cable all work together, sacrifice a crimp. Cut it off the cable, clamp the flat part of the lug in a vice, and with a fine blade hacksaw, cut through the middle of the crimp, slowly, gently and carefully. You want to look at the strands inside the crimp. and see if the are fused together and to the shell of the lug. If loose strands fall out, you have a wrong size somewhere.
                        Ideally, you use certified dies, that imprint their UL code into the lug.
                        CrimpLugDeformed.jpg
                        Ok Mike, you are right, and I really dont care to make all of them either (time is money) so would you mind giving me a breakdown of the cables and lengths and gauges needed for my 4 x 6v battery bank? and where to get some UL stamped lugs/wires at an affordable price (i was headed down the path of 2/0 wires, is that too big? not big enough, or just about right? thanks mike, sorry to keep hitting you up for info, you seem like a great guy so thanks

                        Comment

                        • texman38
                          Junior Member
                          • Sep 2017
                          • 38

                          #13
                          Originally posted by SunEagle

                          Neither that hammer crimper in your other post or this crimper will get you a proper termination for your wires. You need a hydraulic type crimper similar to the one in Richiep's post but even that one (which I own) will not do the best job on some wires.

                          If you plan on trying to save money making your own cable then at least look into purchase quality (and expensive) tools.
                          I think Mike convinced me to buy them... And yes, i saw the 16 ton hydrolic crimpers on ebay for like $35, i think i read the 70mm die would do 2/0, but, I really dont care to make all of them either (time is money) so would you mind giving me a breakdown of the cables and lengths and gauges needed for my 4 x 6v battery bank? and where to get some UL stamped lugs/wires at an affordable price (i was headed down the path of 2/0 wires, is that too big? not big enough, or just about right? thanks Sun Eagle... getting closer... additionally what size wire would i run from my battery bank (4 x 6v in series = 24v) to the power inverter if it were 1000w or 1200w or even 1500w and last if you were to recommend any particular brand or size power inverter? Thanks Sun Eagle!!!

                          Comment

                          • Mike90250
                            Moderator
                            • May 2009
                            • 16020

                            #14
                            I have no idea of the layout of your bank, and what the interconnects are going to be. Map it out, the inverter cables are the ones that end up being critical, because they are usually longer.
                            Use the caculators I listed in post #4 of this thread, and you can figure it out yourself and run it past us for a sanity check.
                            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                            solar: http://tinyurl.com/LMR-Solar
                            gen: http://tinyurl.com/LMR-Lister

                            Comment

                            • texman38
                              Junior Member
                              • Sep 2017
                              • 38

                              #15
                              Originally posted by Mike90250
                              I have no idea of the layout of your bank, and what the interconnects are going to be. Map it out, the inverter cables are the ones that end up being critical, because they are usually longer.
                              Use the caculators I listed in post #4 of this thread, and you can figure it out yourself and run it past us for a sanity check.
                              Thanks Mike... i will you use probably 2awg for the inverter (as long as it fits... but again the size of the battery cables is still something i need advice on??? 2/0 sound about right? and where do I get reasonably priced UL stamped battery cables? so size and where to buy is what I need advice on? I can figure out the lengths myself, but if they are lined up like in my golf cart there is a very short cable hooking pos to neg, not sure how that would work with 2/0 cabling.... so if you have any suggestions on how to arrange a 4 battery bank so that cabling makes more sense, especially with such thick wires, plz plz plz let me know... Thanks!!!