  • texman38
    Junior Member
    • Sep 2017
    • 38

    #16
    Originally posted by Mike90250
    I have no idea of the layout of your bank, and what the interconnects are going to be. Map it out, the inverter cables are the ones that end up being critical, because they are usually longer.
    Use the caculators I listed in post #4 of this thread, and you can figure it out yourself and run it past us for a sanity check.
    mike i found these on ebay that look good with ul stamp? AWG #2/0 Black Battery Interconnect Cable 12" with 3/8" Lugs ASSEMBLED IN USA

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #17
      Again, from post #4, 4ga is OK, 2ga is a bit better and 1/O overkill. 2/O is going to be real clumsy to handle. I don't know the overall lengths, things could be long enough that 2/O is not large enough, you are the man on the spot, figure the lengths and put that into the calculator, is it less than 3% loss ?
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • texman38
        Junior Member
        • Sep 2017
        • 38

        #18
        Originally posted by Mike90250
        Again, from post #4, 4ga is OK, 2ga is a bit better and 1/O overkill. 2/O is going to be real clumsy to handle. I don't know the overall lengths, things could be long enough that 2/O is not large enough, you are the man on the spot, figure the lengths and put that into the calculator, is it less than 3% loss ?
        Thanks Mike, OK, what I was saying was I plan to use 2awg for the CC (you suggested 4awg) My CC will be near the battery bank so no need for a calculator, I was just up-sizing the cable from what you suggested for efficiency and possible future upgrade. The 2/0 cabling I was wanting to use on the battery interconnects, my question again is this, is 2/0 cabling "good enough" for now and for future builds??? 2/0 is huge, only 1 size bigger from what I've seen, but what puzzles me is the crappy 5/16 ring terminal that connects it to the battery??? is there not a better way of interconnecting batteries, just seems ridiculous, giant cable, funneled into dinky ring terminal. I'm use to dealing with the A/C side, 2/0 cable would be under a huge lug on a bus bar... something is missing in the D/C world, or I'm just not getting it. Thanks Again Mike!!!

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15164

          #19
          Originally posted by texman38

          I think Mike convinced me to buy them... And yes, i saw the 16 ton hydrolic crimpers on ebay for like $35, i think i read the 70mm die would do 2/0, but, I really dont care to make all of them either (time is money) so would you mind giving me a breakdown of the cables and lengths and gauges needed for my 4 x 6v battery bank? and where to get some UL stamped lugs/wires at an affordable price (i was headed down the path of 2/0 wires, is that too big? not big enough, or just about right? thanks Sun Eagle... getting closer... additionally what size wire would i run from my battery bank (4 x 6v in series = 24v) to the power inverter if it were 1000w or 1200w or even 1500w and last if you were to recommend any particular brand or size power inverter? Thanks Sun Eagle!!!
          Wire size is determine by the amount of amps that can go through it as well as the distance that can affect the voltage to drop.

          For a quick calculation to determine the amount of amps the wires will see between your battery and your inverter would be to divide the highest wattage rating of the inverter by the battery voltage. ie. 1500w / 24volt = 62.5amps.

          Now be aware that most inverters have 2 ratings. The second is higher than the first and is usually based on the amount of watts that the inverter will see during a "surge". It may be only for a short time but your wires can get real hot very quickly if they are not sized for that surge amp.

          While it might help shorten your time for me to give you a specific wire size and type I also do not want to provide you bad information based on not knowing how long the wires are and how they are being connected to your equipment. I would suggest you look at the calculations that Mike90250 has given you so that you can come up with the wire size first.

          Comment

          • texman38
            Junior Member
            • Sep 2017
            • 38

            #20
            Originally posted by SunEagle

            Wire size is determine by the amount of amps that can go through it as well as the distance that can affect the voltage to drop.

            For a quick calculation to determine the amount of amps the wires will see between your battery and your inverter would be to divide the highest wattage rating of the inverter by the battery voltage. ie. 1500w / 24volt = 62.5amps.

            Now be aware that most inverters have 2 ratings. The second is higher than the first and is usually based on the amount of watts that the inverter will see during a "surge". It may be only for a short time but your wires can get real hot very quickly if they are not sized for that surge amp.

            While it might help shorten your time for me to give you a specific wire size and type I also do not want to provide you bad information based on not knowing how long the wires are and how they are being connected to your equipment. I would suggest you look at the calculations that Mike90250 has given you so that you can come up with the wire size first.
            Thanks sun eagle, being that I want more than what my puny 1000wat inverter will pull even with surge, my question is will 2/0 battery interconnectors (not talking about wiring to the inverter, just between batteries) be sufficient? and if the inverter is within 4ft lets say of the batteries, what size inverter could i basically run b4 2/0 battery interconnectors would be insufficient? 2000w, 3000w, 4000w or more? in other words i doubt seriously that id ever be running anything over 2000 watt inverter (and i understand my system is not big enough at this point to run an inverter more than 1000w, but my point is to factor future growth so i'm not buy all this crap again down the line.... so 2/0 battery interconnectors seems way way overkill to be connecting 4 x 6v 200ah batteries.... but later as i decide to grow, again i just want something sufficient, and obviously having bigger connectors between batteries will be more efficient in terms of charging and discharging. Now here is the question in my mind that makes me say "what the heck" so if 2/0 cabling between batteries is standard practice (again ????) then haveing such large cables running through dinky ring lug type terminals with a 5/16 or 3/8 hole drilled so you can screw them on to you battery seems ridiculous to me (giant wire, dinky connector) seems like this is the weakest link in the system, is this just widely accepted or is there a better way of interconnecting batteries. anyway, again thanks a bunch i've come a long way in a short time thanks to you and mike...

            Comment

            • SunEagle
              Super Moderator
              • Oct 2012
              • 15164

              #21
              Originally posted by texman38

              Thanks sun eagle, being that I want more than what my puny 1000wat inverter will pull even with surge, my question is will 2/0 battery interconnectors (not talking about wiring to the inverter, just between batteries) be sufficient? and if the inverter is within 4ft lets say of the batteries, what size inverter could i basically run b4 2/0 battery interconnectors would be insufficient? 2000w, 3000w, 4000w or more? in other words i doubt seriously that id ever be running anything over 2000 watt inverter (and i understand my system is not big enough at this point to run an inverter more than 1000w, but my point is to factor future growth so i'm not buy all this crap again down the line.... so 2/0 battery interconnectors seems way way overkill to be connecting 4 x 6v 200ah batteries.... but later as i decide to grow, again i just want something sufficient, and obviously having bigger connectors between batteries will be more efficient in terms of charging and discharging. Now here is the question in my mind that makes me say "what the heck" so if 2/0 cabling between batteries is standard practice (again ????) then haveing such large cables running through dinky ring lug type terminals with a 5/16 or 3/8 hole drilled so you can screw them on to you battery seems ridiculous to me (giant wire, dinky connector) seems like this is the weakest link in the system, is this just widely accepted or is there a better way of interconnecting batteries. anyway, again thanks a bunch i've come a long way in a short time thanks to you and mike...
              You are correct that the battery connection point can be your weak link if you draw more amps than what they were designed for. That information should be available from the battery manufacture.

              But I doubt that you need something that can handle more than 200 amps for a 24v 200Ah system so a #1/0 awg in air would be over kill and a #2/0 a waste of your money.

              Something also to think about is that some inverters are very inefficient and will consume a % of their watt rating. The bigger the inverter the more watts it wastes just being turned on.

              I have 3 different inverters (250w, 400w & 600w) and use the size I need for the application. I had a 2500w 12v unit but since it could draw over 200amps I felt it was a little dangerous so I got rid of it.

              Comment

              • texman38
                Junior Member
                • Sep 2017
                • 38

                #22
                Originally posted by SunEagle
                .I had a 2500w 12v unit
                so are you running a 12v battery bank? if so, do you prefer to run 12v for specific reasons?

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15164

                  #23
                  Originally posted by texman38

                  so are you running a 12v battery bank? if so, do you prefer to run 12v for specific reasons?
                  I guess my reason is because the system is easily portable and was designed to also charge my RV coach battery system (which is 12volt) if the need should arise. I also built my 2 small systems about 4 years ago before I knew any better.

                  If I decide to enlarge the system and keep it fixed in my work shed I will more than likely go to 24volt