some power meters do not run backwards they only count up. and have been known to charge you for the power you solar panels produce.
24 Volt or 48 Volt
Collapse
X
-
-
Why and Who says there Ilegal? There sure are a lot of then being sold here. They turn off if the grid goes down. IF I did use one, it would be installed on a dedicated breaker. I am going to check with my local PO CO to see what the deal is. Im not trying to power my entire house, just slow the meter down some.
It does not matter if they are being sold or not. It is your responsibility to know when you can use something legally or not. All types of things are sold but are not always allowed to be used everywhere and anywhere. You have to check the law and codes before you just use something.Comment
-
Your battery system is a 24v 212Ah which is roughly 5100watt hour. That 2200 watt inverter could drain it pretty quickly so it is a little big and you might want to look for a way to limit your loads or find a smaller wattage inverter.Comment
-
Your power company.
There sure are a lot of then being sold here.
They turn off if the grid goes down. IF I did use one, it would be installed on a dedicated breaker.
Im not trying to power my entire house, just slow the meter down some.
Comment
-
The Sun Extender battery folks say there 12 vt AGM battery can accept 1060 amps. From your comments I'm thinking I could drop down to a 1500 or 2000 watt inverter and go with the next larger size batteries @258 ah. Would this be a little more balanced? Thanks so much for your help.Comment
-
Your local POCO wont allow a non UL listed, plug in inverter. It's either the real deal or nothing. Have you considered using a small, independent, off-grid, setup for some loads? Works out real nice for me, especially when the grid goes down and we still have internet and satellite TV.2.2kw Suntech mono, Classic 200, NEW Trace SW4024Comment
-
The Sun Extender battery folks say there 12 vt AGM battery can accept 1060 amps. From your comments I'm thinking I could drop down to a 1500 or 2000 watt inverter and go with the next larger size batteries @258 ah. Would this be a little more balanced? Thanks so much for your help.Comment
-
I was trying to keep the cost down. Cant really afford to spend a couple thousand on batteries. Isn't 1200 watts a rather small system?. Looks like I just WASTED 1400 bucks on this stuff. It's funny that this government is always wanting us to so GREEN but they make it so GD difficult to do. I wanted to wire 2 of the panels in parallel, run them to a disconnect box, then to a 1200 watt GT inverter. The same with the other 2. I bought 2 inverters so there would be no chance of overloading. Both inverters were to be connected to their own dedicated circuit for further safety. .Comment
-
I was trying to keep the cost down. Cant really afford to spend a couple thousand on batteries. Isn't 1200 watts a rather small system?. Looks like I just WASTED 1400 bucks on this stuff. It's funny that this government is always wanting us to so GREEN but they make it so GD difficult to do. I wanted to wire 2 of the panels in parallel, run them to a disconnect box, then to a 1200 watt GT inverter. The same with the other 2. I bought 2 inverters so there would be no chance of overloading. Both inverters were to be connected to their own dedicated circuit for further safety. .
Comment
-
Comment
-
Looks like I just WASTED 1400 bucks on this stuff.
It's funny that this government is always wanting us to so GREEN but they make it so GD difficult to do.
Keep in mind that many of the rules that local utilities use come from the NEC (the National Electrical Code) which is published by the NFPA (National Fire Prevention Association.) Note the word "fire" in there. It's an important word, because most of the rules in the NEC don't come from bureaucratic busybodies trying to make your life more difficult. They come from fires, and electrocutions, and loss of service events. Most rules in the NEC are there because someone burned down their house (or business) by doing something foolish, and the NEC strives to prevent that in the future. Needless to say they don't always get it 100% right, but they get it right far more often than they get it wrong.
Comment
-
OK, how bout this scenario. What size inverter and charge controler and how many batteries would it take to run a load that's 1400 watts 24/7 using my 4 300 watt panels?Comment
-
IMO you would be better off just getting a 20kw propane whole house generator to run your loads.Comment
-
It would take a nearly infinite number of batteries, replaced regularly, because 1200W nominal of solar power, over at most about 5 hours per day, will not be able to make up for a 1400W load 24/7.
Was that really the question you were trying to ask?
If you are asking a more general design question about sizing a system, where you start with the design load, then select the inverter, and batteries and then the CC and panels to match your location, you will find very complete design spreadsheets in the sticky threads of the Off Grid section.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
OK, So whats the point in going solar at all, IT IS SO GD EXPENSIVE how could any home owner even justify the cost of it. I sure cant.Comment