This is almost correct, actually no it's not. If your shop only has a 40A load, you could install a 40A breaker on the feeder in the service and install a 80A backfed breaker for the PV. The shop feeder and bus would need to be rated for 100A and would need to backfeed a 40A breaker for the main of your shop. This would satisfy the 120% rule for the service panel, shop panel, and shop feeder conductors.
Backfeeding SubPanels from Solar Arrays
Collapse
X
-
-
This is almost correct, actually no it's not. If your shop only has a 40A load, you could install a 40A breaker on the feeder in the service and install a 80A backfed breaker for the PV. The shop feeder and bus would need to be rated for 100A and would need to backfeed a 40A breaker for the main of your shop. This would satisfy the 120% rule for the service panel, shop panel, and shop feeder conductors.
GreenComment
-
I got my basic question answered. It's possible, but would just have to make sure the installers electricians know how to read the NEC and get everything safe and legal.
I don't plan on doing this myself, just want to know enough to make sure the guys are doing it correct.
JimComment
-
This is almost correct, actually no it's not. If your shop only has a 40A load, you could install a 40A breaker on the feeder in the service and install a 80A backfed breaker for the PV. The shop feeder and bus would need to be rated for 100A and would need to backfeed a 40A breaker for the main of your shop. This would satisfy the 120% rule for the service panel, shop panel, and shop feeder conductors.
This was another question by another poster that was a bit off this topic.NABCEP certified Technical Sales Professional