This is almost correct, actually no it's not. If your shop only has a 40A load, you could install a 40A breaker on the feeder in the service and install a 80A backfed breaker for the PV. The shop feeder and bus would need to be rated for 100A and would need to backfeed a 40A breaker for the main of your shop. This would satisfy the 120% rule for the service panel, shop panel, and shop feeder conductors.
Try our solar cost and savings calculator
Backfeeding SubPanels from Solar Arrays
Collapse
X
-
-
He was actually answering my question about just a main service panel and not a sub. Sorry to the OP I kinda jumped in with a related question, didn't mean to confuse.This is almost correct, actually no it's not. If your shop only has a 40A load, you could install a 40A breaker on the feeder in the service and install a 80A backfed breaker for the PV. The shop feeder and bus would need to be rated for 100A and would need to backfeed a 40A breaker for the main of your shop. This would satisfy the 120% rule for the service panel, shop panel, and shop feeder conductors.
GreenComment
-
No worries! I'm soaking up information too!
I got my basic question answered. It's possible, but would just have to make sure the installers electricians know how to read the NEC and get everything safe and legal.
I don't plan on doing this myself, just want to know enough to make sure the guys are doing it correct.
JimComment
-
Actually it is correct. I was not responding to the question of backfeeding the shop sub panel but backfeeding the main 100A service not the sub panel.This is almost correct, actually no it's not. If your shop only has a 40A load, you could install a 40A breaker on the feeder in the service and install a 80A backfed breaker for the PV. The shop feeder and bus would need to be rated for 100A and would need to backfeed a 40A breaker for the main of your shop. This would satisfy the 120% rule for the service panel, shop panel, and shop feeder conductors.
This was another question by another poster that was a bit off this topic.NABCEP certified Technical Sales Professional
[URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]
[URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)
[URL="http://www.gaisma.com"]www.gaisma.com[/URL]Comment