Wire Gauge
Collapse
X
-
Originally posted by Aussiemike View PostNo coconut crabs but plenty of mud crabs. About $2 a kilo. Sorry about cubicles and computing. Never done it myself. Spent most of my life spearfishing for a living.
Anyhow, I wish you success with your solar project in that beautiful locale.
2.2kw Suntech mono, Classic 200, NEW Trace SW4024Comment
-
Originally posted by Aussiemike View Post
Your panels are 30V panels, not 12v, 12V panels produce Vmp at about 18V. These are Grid-Tie design panels.
Last edited by Mike90250; 03-11-2018, 12:06 PM.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Post a fresh pic of the panel spec label.....Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Sorry Mike, when you guys told me I had the wrong panels with those two 24v I decided to use tow different systems as in #46 and #47.
I am now concernarating on a 24v system using the 4 x 12v 200w panels I have as in the diagram below.
I am going to use the 24v panels in a 12v system which I will figure out after I put in place the 24v system.
The one now is this one.
If by any chance there is a way to incorporate the grid tie panels I am all ears.
Thank you for being so patient with me.
solar 24.jpgComment
-
Still need a pic of the stickers off the back of each style of panels that you want to use.telling me it's a 12V panel is next to meaningless, like I have a 300W peak stereo.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Originally posted by Aussiemike View PostThanks Mike but the panels in question are down in Tanzania and I am in Kenya..AFAIK They are normal 12v 200 watt panels.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Thanks Mike.
Have I bought another white elephant?
40A specifications:
Size: Approx. 24.9x17.9x15.6cm/ 9.80x7.05x6.14"
Nominal system voltage: 12/24V auto work
Rated charge current: 40A
Rated discharge current: 40A
Battery input voltage range: 8V~32V
Max. PV input power: 520W(12V); 1040W(24V)
Self-consumption: ≤20mA (12V); ≤16mA (24V)
Discharge circuit voltage drop: ≤0.18V
Temperature compensation coefficient: -3mV/Comment
-
Originally posted by Aussiemike View PostThanks Mike.
Have I bought another white elephant?
40A specifications:
Size: Approx. 24.9x17.9x15.6cm/ 9.80x7.05x6.14"
Nominal system voltage: 12/24V auto work
Rated charge current: 40A
Rated discharge current: 40A
Battery input voltage range: 8V~32V
Max. PV input power: 520W(12V); 1040W(24V)
Self-consumption: ≤20mA (12V); ≤16mA (24V)
Discharge circuit voltage drop: ≤0.18V
Temperature compensation coefficient: -3mV/
Here's a link to a real MPPT controller
https://www.morningstarcorp.com/products/sunsaver-mppt/
and some of it's specs https://2n1s7w3qw84d2ysnx3ia2bct-wpe...ENG10_1111.pdf
Battery Voltage Range 7-36 volts
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
Comment