pv system connected to sub-panel
Collapse
X
-
Leave a comment:
-
since virtual net metering is not supported by the POCO, an alternate possibility is to relocate the main power to the 'jump pole' about 75' closer to the transformer. the sub-panel can also be relocated and wire the PV array to it with about a 125' hop to the transformer from the PV array. but this would be a lot of work and possibly a greater hassle by having to bring the 'old stuff' up to most recent code. and i'd want to keep the old primary panel on the pole as a sub-panel for the well & house and to run the supply line overhead from pole to pole. don't know if this is allowed & it might cost a bunch of $.Leave a comment:
-
on this note, then how likely is it that the grid voltage here might hit 261vac and cause disruption to the inverters?Leave a comment:
-
some areas are more stable than others but here is a typical example from one of our inverters in PA a little west of Philadelphia.
so just from the 25th to the 26th you have an average day time swing from 248V to 243V Chart.jpgLeave a comment:
-
I would also add in the fact that the grid voltage tends to go up at the end of the day or on weekends when commercial & manufacturing loads are turned off.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
If you mount the string inverter near your main panel, you can run the 500 Vdc the long distance with less loss and just have a short AC run.Leave a comment:
-
i looked tonight at some string inverter specs. it seems that the 'ceiling' for 240vac is 264vac. the range is given 211v-264v. how is this different from the micro-inverter?Leave a comment:
-
The grid voltage is not constant so you will need to measure them at the same time or at least a few times close to the same time.Leave a comment:
-
i measured the sub-panel voltage this a.m. @ 249vac even.Leave a comment:
-
Leave a comment:
Leave a comment: