Try our solar cost and savings calculator
generator not charging..a battery of questions..lol
Collapse
X
-
-
Thanks for all of the input so far....I was out there again yesterday, voltage was holding at 12.37...
tried the generator again, and once again, no change in voltage occured with generator running...,
I then swept off the panel, as it was covered in snow, the panel is actually 2 sections at 80 W each.
No time for diagnostics, I did however bring one of the batteries home to test its worth. now I will do some reading to see how I could go about that. If someone know a quick guideline in determining if the battery is still good, please do tell.!!
Comment
-
Comment
-
Red flag!
If the hydrometer did not suck in any fluid, most likely the level of electrolyte in the cells has dropped below the top of the plates, where the rubber tube cannot reach it.
Carefully look down the fill hole. If you don't see the liquid surface, add distilled water until you do, the rock or shake the battery awhile (or let it charge for awhile) and try the hydrometer again.
Although first checking to see whether your new hydrometer can suck water from a glass would be a good first step.
If the level of the electrolyte has gone below the tops of the plates, the batteries have suffered at least some damage and will need to be checked carefully and possibly replaced.
The acid level in the batteries was maintaince throughout the summer, I can clearly see fluid near the top of the cap when I open them up..I honestly think I bought a botched hydrometer. I brought it home along with once of the batteries to do some testing, the spontaneously broke on the ride home. The glass bulb inside erupted. Im thinking these things cant freeze..lol, the first time I tried it when it didnt suck it was right out of the package...not frozen.Comment
-
Here are the specs on the batteries: There are Pow-R-Surge.
No. 2200
Series 1200
Rating: 225 AH
Rating: 115 RCComment
-
According to Trace DR specs...
"Automation: Plug into utility power or rev-up your generator and the DR model inverter starts charging your batteries and automatically transfers your AC input power to your AC electrical system. It charges rapidly and completely without overcharging and maintains the full charge indefinitely. The high power sychronous-rectification design charges batteries in three stages -- bulk, absorption, and then float. When your AC input power fails, transfer to inverter power is also automatic and typically within 16 milliseconds."
... you wouldn't even need to throw a switch to change from battery to generator power while charging batteries at same time.
You mentioned, "I visit the cabin about once every couple of weeks, and on arrival the voltage is in its boots." May be the batteries are ruined by now and they're not taking a charge? That ONE 3x2 ft panel (100watt?) you say you have would barely maintain that 600+AH battery bank while you're away.
Hope you have that generator exhaust routed outside your power room. Having that fuel tank so close to the electrical system would make me nervous.
could it be that I simply havent let the generator run long enough?? I only let it run for max 1 hour with not change in voltage..and simply gave up. perhaps it needs more time to make up for the amount amount of bulk charging it has to accomplish??Comment
-
Instead of just watching the voltage you need to look at current into the battery. If no current is flowing, no charging will take place no matter how long you leave it running.
Once again, I ask the question of how the power from the generator is getting to a charger which is then connected to the batteries.
An inverter-charger can only charge from generator power if it is connected in some way to the generator. If your external transfer switch isolates the generator from the inverter-charger and there is no other charger on the load side of the switch there is no way the generator can charge the batteries!SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
Did you determine the batteries are still useful?
Follow the wiring. Is the transfer switch hard wired to the generator or is it just plugged into an outlet... or not plugged in? Did the original installation include battery fusing that may have blown?
Do you own a volt meter? You can check terminal voltage before and after generator is started in minutes.
Download the Trace DR owner's manual, make sure the settings are correct.
haha, don't give up. Understand your system and what it's doing. May take time but it will save much headache in the future.
Be safe. If you really feel too freaked to deal with it get some local, experienced help.Comment
-
For a quick reality check, get an inexpensive AC battery charger (the kind you need to manually supervise since it does not have all of the 3 stage charging bells and whistles), plug it into the generator or the house wiring and connect it to the battery. See if that does anything for them.
To get the Trace to charge the batteries off the generator, the generator output has to be run to the grid/generator AC input of the Trace rather than using an external transfer switch.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
Instead of just watching the voltage you need to look at current into the battery. If no current is flowing, no charging will take place no matter how long you leave it running.
Once again, I ask the question of how the power from the generator is getting to a charger which is then connected to the batteries.
An inverter-charger can only charge from generator power if it is connected in some way to the generator. If your external transfer switch isolates the generator from the inverter-charger and there is no other charger on the load side of the switch there is no way the generator can charge the batteries!
If you take a look at the picture of the entire setup, you can see that the inverter/charger is connected to the generator via the black cable which is plugged into the generator. That cable runs to the transfer switch, which is wired to the inverter/charger and down to the batteries.
As far as voltage, I thought this was a way to at the very least see if charging is taking place. When using the sun this change in voltage occurs rather quickly.
Now when you say monitor the current, I would do this exactly how. Im sure it is rather simple. Would I do that by simply monitoring this on my solar boost 2000E display? I have the option to monitor battery voltage, solar panel current, and output charge current.
Would I keep an eye on the output charge current? or its it something that has to be done with a multimeter?
Finally, I would like to apologize for my ineptitude on these topics. I like to think Im fairly intelligent, I have education under my belt, but my areas of expertise is health care. This solar/electrical stuff is interesting though.Comment
-
Did you determine the batteries are still useful?
Follow the wiring. Is the transfer switch hard wired to the generator or is it just plugged into an outlet... or not plugged in? Did the original installation include battery fusing that may have blown?
Do you own a volt meter? You can check terminal voltage before and after generator is started in minutes.
Download the Trace DR owner's manual, make sure the settings are correct.
haha, don't give up. Understand your system and what it's doing. May take time but it will save much headache in the future.
Be safe. If you really feel too freaked to deal with it get some local, experienced help.
Not 100% sure if the batteries are still good...They do charge with the solar panel though, I take that as a good sign. Transfer switch wired with a plug, which I plug into the generator.
I see fuses on the transfer switch, one for "generator" one for "normal" (solar) both fuses were intact last time I was out.
I have a voltmeter yes.
Now correct me if this is a poor assumption. I assume that the voltage reading on my solar boost 2000E display is the voltage of the batteries themselves. (If I took a voltmeter, I assume I would get the same reading from the battery terminals as the display shows.)
How many minutes after should I check the battery terminal voltage? depending on your answer to the above assumption I made. If it is a correct assumption then I can just use my display. If not I can use the voltmeter, either way, should I see a major charge in the voltage after a few minutes?
Thanks for understanding that this isnt easy...Im trying to wrap my head around the whole system. With time I hope to understand my system enough to know what is normal, and what is not right.
Comment
-
I don't know where/how the solar boost is wired, but if it is only between the panels and the batteries, it will not measure the charging current coming from the Trace, just the current coming from the panels. The ideal thing to do is get a clamp-on ammeter that specifically measures DC current through the clamp. (This will probably cost somewhere around $80 or up, but will be a very useful tool to have down the road too.) Most clamp-on ammeters will only measure DC current through the test leads, and that would require disconnecting one of the battery wires. I do not recommend you do that at this stage of your education.Now when you say monitor the current, I would do this exactly how. Im sure it is rather simple. Would I do that by simply monitoring this on my solar boost 2000E display? I have the option to monitor battery voltage, solar panel current, and output charge current.
Would I keep an eye on the output charge current? or its it something that has to be done with a multimeter?
Another way to get a very rough idea of whether the batteries are charging is to put the voltmeter leads one at each end of the wire between the Trace and one of the battery posts. The wire will act as a crude shunt and by measuring the (hopefully small) voltage between the leads you can at least get an idea of which way the current is flowing.
If you put the + lead at the + on the Trace and the - lead at the - post of the battery, then if you read a positive voltage the battery is being charged. If you read a negative voltage, the Trace is pulling current from the batteries. If you read nothing at all, then either the setup is wrong or the batteries are not being charged.
Do NOT try to do this with the multimeter on an amps setting!
Can you come up with a wiring diagram rather than just a photo? From the picture it looks like the wire from the generator is going directly into the transfer switch box rather than directly to the Trace, so the details will all depend on how the inside of the transfer switch box is wired. For a simple installation, there would be no need for a separate transfer switch since that function would be provided by the Trace itself. That means that we really need to know how the transfer switch is wired!SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
I'm not familiar with that 2000E inverter either and haven't looked at it's owner manual but there may be a way of checking voltage in, battery voltage, a function like my inverter has. If you have a volt meter then check the voltage at battery terminals and compare.Not 100% sure if the batteries are still good...They do charge with the solar panel though, I take that as a good sign. Transfer switch wired with a plug, which I plug into the generator.
I see fuses on the transfer switch, one for "generator" one for "normal" (solar) both fuses were intact last time I was out.
I have a voltmeter yes.
Now correct me if this is a poor assumption. I assume that the voltage reading on my solar boost 2000E display is the voltage of the batteries themselves. (If I took a voltmeter, I assume I would get the same reading from the battery terminals as the display shows.)
How many minutes after should I check the battery terminal voltage? depending on your answer to the above assumption I made. If it is a correct assumption then I can just use my display. If not I can use the voltmeter, either way, should I see a major charge in the voltage after a few minutes?
Thanks for understanding that this isnt easy...Im trying to wrap my head around the whole system. With time I hope to understand my system enough to know what is normal, and what is not right.

Hard to read the writing on that pic (098.jpg) but... is that a Trace Disconnect/Overcurrent Module installed between inverter and batteries? Is it in the 'on' position?
You'll get it figured out. If the previous owner did not leave you with owner manuals they are available to download online. You need a copy of everything for future reference, a system schematic drawn up by you and it will all sort out.
Trace DR owner's manual, http://www.solarcellsales.com/techin...30-5DRV3.2.pdf
Like inetdog suggested a clamp on ammeter will give direct results. Not sure which model Trace inverter you have but should be putting out over 50 amps?, 14.6 volts at bulk charge Find the model number, get the specs, see what it's supposed to do. Hooking up a smaller, 10-20amp, AC battery charger would do in a pinch but would take many more hours to reach a full charge.Comment
-
The Solar boost is wired between the panels and the batteries. I am confident I can pull of your second suggestion:I don't know where/how the solar boost is wired, but if it is only between the panels and the batteries, it will not measure the charging current coming from the Trace, just the current coming from the panels. The ideal thing to do is get a clamp-on ammeter that specifically measures DC current through the clamp. (This will probably cost somewhere around $80 or up, but will be a very useful tool to have down the road too.) Most clamp-on ammeters will only measure DC current through the test leads, and that would require disconnecting one of the battery wires. I do not recommend you do that at this stage of your education.
Another way to get a very rough idea of whether the batteries are charging is to put the voltmeter leads one at each end of the wire between the Trace and one of the battery posts. The wire will act as a crude shunt and by measuring the (hopefully small) voltage between the leads you can at least get an idea of which way the current is flowing.
If you put the + lead at the + on the Trace and the - lead at the - post of the battery, then if you read a positive voltage the battery is being charged. If you read a negative voltage, the Trace is pulling current from the batteries. If you read nothing at all, then either the setup is wrong or the batteries are not being charged.
Do NOT try to do this with the multimeter on an amps setting!
Can you come up with a wiring diagram rather than just a photo? From the picture it looks like the wire from the generator is going directly into the transfer switch box rather than directly to the Trace, so the details will all depend on how the inside of the transfer switch box is wired. For a simple installation, there would be no need for a separate transfer switch since that function would be provided by the Trace itself. That means that we really need to know how the transfer switch is wired!
"If you put the + lead at the + on the Trace and the - lead at the - post of the battery, then if you read a positive voltage the battery is being charged. If you read a negative voltage, the Trace is pulling current from the batteries. If you read nothing at all, then either the setup is wrong or the batteries are not being charged.
Do NOT try to do this with the multimeter on an amps setting!"
Thanks for that tip. I am heading out there on Monday or Tuesday for some snowshoeing with the dog...shes is driving me crazy, I need to tire her out! While Im out there ill see what I can do about getting a wiring diagram. I know it is difficult to see whats going on from the pics I posted.
I have already disconnected one of the batteries thinking I would be able to test its worth in a warm basement...It required some cleaning of the +ve and -ve terminals. It had minor white corrosive builup on the posts. As do all of the batteries. Im thinking that its probably not a bad idea to clean up all the posts next time im out.Comment
-
I'm not familiar with that 2000E inverter either and haven't looked at it's owner manual but there may be a way of checking voltage in, battery voltage, a function like my inverter has. If you have a volt meter then check the voltage at battery terminals and compare.
Hard to read the writing on that pic (098.jpg) but... is that a Trace Disconnect/Overcurrent Module installed between inverter and batteries? Is it in the 'on' position?
You'll get it figured out. If the previous owner did not leave you with owner manuals they are available to download online. You need a copy of everything for future reference, a system schematic drawn up by you and it will all sort out.
Trace DR owner's manual, http://www.solarcellsales.com/techin...30-5DRV3.2.pdf
Like inetdog suggested a clamp on ammeter will give direct results. Not sure which model Trace inverter you have but should be putting out over 50 amps?, 14.6 volts at bulk charge Find the model number, get the specs, see what it's supposed to do. Hooking up a smaller, 10-20amp, AC battery charger would do in a pinch but would take many more hours to reach a full charge.
Yes in (098.jpg) that is a Trace Disconnect/Overcurrent Module. It is in the ON position, and it is wired to the batteries below, and to the inverter/charger to the right.
I found the owner manual online, all 51 pages of it. I was most interested in the battery charging section of the manual, and I made some interesting discoveries:
"The inverter automatically becomes a battery charger whenever AC power is supplied to its AC inputs. There is a 40 sec. time delay from the time the inverter senses that AC is present at its input and when the transfer is made"
Also in the "Three stages of battery charging" section:
Stage one being Bulk Charge. It states: " This stage is initiated when AC is applied to the AC input of the inverter, and it terminated when the batteries reach the BULK CHARGE VOLTAGE. During this stage the Charge LED glows steady orange.
The part that stood out to me was the line about the LED glowing steady orange. There are 4 LED's on the front of the inverter. The only LED I have ever seen lit up is the one labeled "Inverter Mode" I have never seen the Charger LED light up except briefly during the self test when I hit the on/off button on the inverter.
So, as it appears to me, the inverter is not going into "charger mode" WTF! Its seems like the inverter/charger is not sensing the AC power that is being applied to it....dunno, I think ill have to get someone who knows about these things to take a look. But in this small town...it will be hard to find someone who knows alot about this kind of stuff.
Comment
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 11:51 AM.
Comment