Set up problem or full battery?

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • Set up problem or full battery?

    635C06BC-D1ED-43C7-8BC3-1C70182A533C.jpeg I have four Renogy 100 W panels wired in parallel.

    I tested each panel individually, while hooked up to a battery that is 100% full. Each individual panel was giving me 20 V and approximately 2 A

    when I hooked all four together the charge controller was still saying roughly 20 V and roughly 2 A.

    do I have a problem somewhere or is the battery so full that the charge controller is not putting more into it?

  • #2
    First guess, is the battery is full.

    Question "charge controller was still saying roughly 20 V and roughly 2 A."
    When you measure the 20V, is that at the battery or the PV panel ? The 2 amps, at the panel or the battery ?
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment


    • #3
      Those numbers are all coming from the charge controller. How can I figure out the amps on a solar panel with a multimeter?

      Comment


      • #4
        Is the 20V the panel voltage or the battery voltage ? The controller manual should state how to display specific values
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment


        • #5
          I found another battery and hook it up. Then I was getting 19 V and 18 A which makes sense.
          Thank you for your advice on the battery.

          Comment


          • #6
            Originally posted by kingofbanff View Post
            I found another battery and hook it up. Then I was getting 19 V and 18 A which makes sense.
            Thank you for your advice on the battery.
            Hopefully that battery is rated around 200Ah. If it is less than 150Ah those 18 charging amps can cook it.

            Comment


            • #7
              Is the 19V the voltage of the panel, or the battery?

              Comment


              • #8
                Originally posted by SunEagle View Post

                Hopefully that battery is rated around 200Ah. If it is less than 150Ah those 18 charging amps can cook it.
                170Ah Lithium. For what it
                is worth The manufacture says maximum charging is 50 A.
                Last edited by kingofbanff; 08-21-2019, 10:51 PM.

                Comment


                • #9
                  Originally posted by sdold View Post
                  Is the 19V the voltage of the panel, or the battery?
                  I believe that is the panel.

                  Comment


                  • #10
                    Originally posted by kingofbanff View Post
                    I believe that is the panel.
                    I believe you might be right . or you might be wrong. I don't care. I'm an engineer and I deal in facts. You can believe the fuse is not lit, but the dynamite won't care what you believe.

                    I believe the fire is out, and it's OK to fill the gas tank. Do you get what I mean ?
                    I believe the lane next to me is empty . Whoops.

                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    Working...
                    X