Set up problem or full battery?
Collapse
X
-
Leave a comment:
-
is worth The manufacture says maximum charging is 50 A.Last edited by kingofbanff; 08-21-2019, 10:51 PM.Leave a comment:
-
Is the 19V the voltage of the panel, or the battery?Leave a comment:
-
Leave a comment:
-
I found another battery and hook it up. Then I was getting 19 V and 18 A which makes sense.
Thank you for your advice on the battery.
Leave a comment:
-
Is the 20V the panel voltage or the battery voltage ? The controller manual should state how to display specific valuesLeave a comment:
-
Those numbers are all coming from the charge controller. How can I figure out the amps on a solar panel with a multimeter?Leave a comment:
-
First guess, is the battery is full.
Question "charge controller was still saying roughly 20 V and roughly 2 A."
When you measure the 20V, is that at the battery or the PV panel ? The 2 amps, at the panel or the battery ?Leave a comment:
-
Set up problem or full battery?
635C06BC-D1ED-43C7-8BC3-1C70182A533C.jpeg I have four Renogy 100 W panels wired in parallel.
I tested each panel individually, while hooked up to a battery that is 100% full. Each individual panel was giving me 20 V and approximately 2 A
when I hooked all four together the charge controller was still saying roughly 20 V and roughly 2 A.
do I have a problem somewhere or is the battery so full that the charge controller is not putting more into it?