New Setup... lot of questions
Collapse
X
-
-
I hope its work. Not sure if ts rated for 48V
as for the from of the inverter to the main panel, its recommended a sub panel. That's basically a one or two space breaker box with what size of breaker. This is the AC side so following the same calculations would be a 75Amp. I'm correct?Comment
-
Your inverter has both an AC input and an AC output. The input can be either your main circuit breaker panel or a generator. NOT both at the same time. The fxr3048 manual goes over how to set up a manual changeover switch. The fxr3048 has a maximum AC input of 60a AC.
On the output side, a sub panel, where you power all your AC loads off the inverter:
3000w / 120v = 25a AC minimum. Outback recommends 10 AWG for AC loads so your maximum is 60a AC.
Dont cheap out on the fuses. You have spent good money on your equipment to risk it on an improper fuse. Make sure they are rated for the intended purpose.Last edited by Suprasoup; 02-04-2018, 03:26 AM.Comment
-
Hi all,
I need advice.
OK, FINALLY I got power from the POCO since hurricane Maria pass. I'm still going to made the switch to solar.
Yesterday i got the 48v Outback FXR3048A Inverter, so I think it's a good chance to turn off the system and upgrade it to 48v.
About the batteries, now that I will be disconnecting all 4 batteries and make the 48v bank using the other 4 I got waiting for, it's recommended to do a EQ on the batteries before disconnect the 12v system or I should wait until the new system and use the outback inverter and the POCO to do EQ on all the batteries?
Thanks in advance
Comment
-
I'd get a grid power 12V charger and fill up each battery on it's own. That way, you are starting from KNOWN GOODPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
I agree. Charge each 12v battery (2 x 6v wired in series) using a 12v grid charger. Once they are fully charged then assemble your batteries into a 48v battery (8 x 6v in series). At this point you can use your Outback Inverter/charger to EQ if its needed. Use your temperature compensated hydrometer to check the SG of each cell.
Your Outback FXR3048 can function Grid Tied if your POCO allows it. IF not you can Grid Zero to utilize your solar panels while still staying on grid. Let us know if you need anymore help.
Supra
Comment
-
OK, thanks for the tip. I would do that.
I need to purchase the Display Mate3 so I can change the setting on the inverter. It default mode is in support. Reading the manual I can use it in support mode as ButchDeal suggested in my 48V Inverter Suggestion threat.
Suprasoup Use your temperature compensated hydrometer to check the SG of each cell.
Now, this is not the case for the other 4 batteries waiting to be connected in the 48v bank. I measure with the hydrometer and all are at 1.250 SG
So with the 12V grid charger I can put all of them to 1.275 SG
Suprasoup Let us know if you need anymore help.
20180205_071257.jpgComment
-
https://www.amazon.com/gp/product/B0...J8MC7PE8&psc=1
Also I don't have any protection from the CC to the Battery bank. Do I use the same fuse?Comment
-
The Inverter and the Charge controller need their own separate fuses. Personally I am not a fan of circuit breakers for DC. Take a look instead at Blue Seas MRBF fuses. They bolt directly to the battery terminal and they come in 2 fuse models:
Get a 150a fuse for the Inverter and a 100a (80a x 125%) for the charge controller.
Comment
-
Comment
-
Hi all,
First thank for the replies and help and special thanks to Suprasoup , Mike90250 and ButchDeal
Here are some update information of what I have been doing with the upgrade process...
Yesterday I complete what I call "phase 1" that consist of the following- Charge all batteries individually (2 x 6v in series) using a 12v grid charger and a temperature compensate hydrometer.
- Eliminate the cheap pwm charge controller
- Putting together the batteries and fuses for a 48V @ 370HA bank
- Reconfigure the panels to a 3S2P configuration
- Reconfigure the Outback CC for 48V, set the absolve, float and re-bulk to 59.2V. Not sure about the re-bulk, Should I leave it as default value of 48V?
- Eliminate the 12V Inverter
- Made the connection on the Outback FRX3048A Inverter.
- Test all connections to make sure everything is ok
- Power on system
- install pvc conduit to the new sub-panel and re-configuring the AC wiring to separate multiple house in the main panel.Only my house wiring will be in the sub-panel.
- From the main panel to the AC input on the inverter
- From the AC output to the sub-panel.
- Grounding from the main panel to a ground bar, then to all the system
- Some cosmetic... Paint the battery box
Feel free to contribute and comments
Good dayComment
-
Set the charger back to the factory settings, otherwise you will be in bulk 90% of the time, consume excessive water and damage your batteries
If your battery came with CYCLE duty charge specs, use those. But you will eventually need to monitor voltage and work out ABSORB time setting to insure the batteries get fully charged, this will depend on your loads and solar supply.Last edited by Mike90250; 02-21-2018, 02:01 AM.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Set the charger back to the factory settings, otherwise you will be in bulk 90% of the time, consume excessive water and damage your batteries
If your battery came with CYCLE duty charge specs, use those. But you will eventually need to monitor voltage and work out ABSORB time setting to insure the batteries get fully charged, this will depend on your loads and solar supply.
Change back to manufacturer settings, I do have the manufacturer charge specs, was following the sticky tutorial "Are you killing your batteries" I indeed lower the voltaje yesterday after reading SG, the result was high (1.275) the manufacturer state a 1.265 for 100% charge.
I will start monitoring and keep records of the readingComment
-
after reading SG, the result was high (1.275) the manufacturer state a 1.265 for 100% charge.
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar