    A LEAf battery is not LFP or really anything close to it. One reason commercial EV manufactures do not use LFP batteries is because they cannot easily control SOC. No commercial EV manufacture allows the customer to fully charge the Traction Battery. They could not offer or honor any warranty if they did that. The Leaf uses NMC, and unlike a LFP battery has a very defined Charge/Discharge curve. I use them in my racing golf cart as many DIY EV builders now use Leaf, Volt, and Tesla packs because there are so many used EV's out there collecting dust no one wants. Other source is salvaged yards which is where I look to get the newer models after 2012 failures.

    WIW Nisan limits to 10/90. Nissan limits charge voltage to 4.1 vpc, full SOC is 4.3. On the discharge side has a few levels

    Charge Terminate at 4.1 volts.
    Very Low at 3.625
    Limp Home or Turtle Mode at 3.22
    Call Tow Truck or Shutdown at 3.2
    Destroyed at 3.0 volts.

    They will never let you go to 4.3 volts (100% SOC) or 3.0 volts (0% SOC). My controller is set to Float at 103 volts, and Motor Controller LVD at 90 volts. I run 25S aka 96 volt battery @ 66 AH

    See that nice Slope. It is not FLAT like LFP. Makes it real easy to charge to any SOC you want.
    Last edited by Sunking; 06-23-2017, 05:42 PM.

    Leave a comment:


  • karrak
    replied
    Thanks, interesting information. Three percent per year is a little alarming. They are supposed to have improved the batteries, having a look at what the latest warranty has to say should show if this is the case. I am sure that there are many more improvements in lithium ion battery technology yet to come.

    My friend's LFP based off-grid system that I designed and built spent its first three years on the north wall (in the southern hemisphere) of an uninsulated dark blue tin shed where the temperatures would have been above 100F on a regular basis in summer which caused me some concern but at the end of this I tested one of his cells and it still had its rated capacity of 90Ah. This is the cell that I did the charge/discharge tests on. It is quite possible that it had more than 90Ah when new and I would be surprised if it hasn't lost some capacity. My guesstimate is that our batteries are loosing between 1%-2% PA, probably closer to 1%. It will take a few more years of monitoring to get a better idea.

    Simon
    Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
    BMS - Homemade Battery logger github.com/simat/BatteryMonitor Latronics 4kW Inverter,
    homemade MPPT controller

    Leave a comment:


  • ASprinter
    replied
    Originally posted by karrak
    I would be interested to know some details of your Leaf battery capacity change with time and temperature.
    I will start by saying the Leaf was a great car and although there was a capacity loss as measured through a bluetooth OBDII reader and the app "Leafspy," the range loss was not noticeable. It seemed to go just as far on a charge and used the same percentage of the battery on my daily commute that it did when new.

    In logging the amp-hours every couple of weeks over 3 years (my lease length) it lost 9% of the total amp-hours. In the winter time, and particularly when it first turned cold, there would be a slight temporary amp-hour loss, but that capacity came back as the temperatures came back up. However in the summer in northern California, temps are often over 100 degrees. It seemed to loose all of its capacity during those 3 hot months. In other words, it lost about 3% of its capacity from the beginning of summer to the end (permanent loss), each year, and losses during the winter were temporary and generally restored when temps came back up.

    Leafs do not have a temperature controlled battery. Based on my results with the car I wouldn't want to own one longterm in a hot climate unless the battery were temperature controlled or the battery chemistry improves to the point that summer degradation is reduced. I actually have a deposit on a Tesla Model III, but likely won't go through with it only because my life circumstances have changed since I put down the deposit. Electric drive is fantastic.

    Leave a comment:


  • karrak
    replied
    I would be interested to know some details of your Leaf battery capacity change with time and temperature.

    As far as I can see within reason it is not so much the SOC that the battery is charged to but how long it spends at that SOC and whether or not there will be loads on the battery that are the important factors.

    Simon
    Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
    BMS - Homemade Battery logger github.com/simat/BatteryMonitor Latronics 4kW
    Inverter, homemade MPPT controller

    Leave a comment:


  • ASprinter
    replied
    I have read a lot of Maine Sail's posts but had not seen that particular one. I am very familiar with the temperature-related aging as I was able to access and read battery stats from my Nissan Leaf and could see the effects of our hot summers on that car's battery capacity. Unfortunately this van will be stored out in the sun in 100+ degree weather at times, nothing I can do about that. I used similar charging practices with my Leaf to what you described for my camper van--I rarely ever charged the car and left it at a high SOC.

    The van will be used roughly every-other weekend and one trait I really like about LiFePO4 is the fact that I can bring it home with a partial charge, park it (for a week or two) and not worry about keeping a lead acid battery topped off. I will likely shut off everything when it's parked and turn it on a day or two before a trip to 'fill' the battery. If I had a boat that sat for months I probably would do the very low voltage float you suggested.

    At the end of the day, it's just a battery and I plan to use it. I like learning about technology, hence this thread. But as stated, one challenge I'm finding is the two different charging devices produce fairly considerably different SOCs based on the path taken to reach that target voltage (charge rate, time, etc).

    Leave a comment:


  • karrak
    replied
    Originally posted by Sunking
    The only way to really know SOC is to fully charge each cell to 3.6 volts until current tapers to 2 to 4 amps. Rest it, then fully discharge it and measure AH of each cell. Say a cell measures 100 AH. Now you recharge and only put in 93 AH to get to 90% SOC. Your batteries are roughly 97% efficient charging meaning it will take 103 AH in to have 100 AH capacity.
    You can also charge them to 3.45V until the current tapers to C/50 (in the OP's case ~2A) and call this 99%. This is what I do, although I call it 100%. If you use the stated capacity of the cells rather than discharging them to calculate the 0%SOC you will not be far out with new cells. The coulomb/current efficiency of LFP batteries is not 97%, it is around 99.5%.

    You can use a Coulomb counter, but even that is flawed because of battery charge efficiency. They have to be recalibrated every cycle or two to be useful.
    If you can input the efficiency of the battery into the coulomb counter it could remain accurate for up to a week or even better if it learns what the efficiency is it could go several weeks or tens of cycles without getting too inaccurate.

    Life is much simpler if you just Bottom Balance and charge to 13.4 to 13.6 volts and quit worrying about minor meaningless details. As long as you are not taking your cells above 3.45 volts, no stress. That is why A123 Systems recommends float charging LFP cells to 3,45 vpc for extended battery life accepting less than fully charged.
    Even simpler I would have thought because it doesn't need a bottom balance and might make the battery last longer and will charge the battery up as quickly as possible is for the OP to:
    • When out camping and the battery is in use set the Victron to bulk charge at 13.8V-13.7V with an absorb time of 0-15 minutes and drop to a float voltage of 3.35V-3.30V depending on what SOC you want to float the battery at.
    • When the unit is sitting at home not being used set the Victron (if it will let you) to a bulk and float voltage of 12.8V. This of course assumes that the solar panel remains out in the sun.
    • A couple of days before you use the battery again set the Victron back to the in-use settings to recharge the battery.
    • If you notice that the individual cell voltages are diverging when the charge voltage is at 13.8V do a balance by doing a charge at 14.2V with a longer absorb time to give the balancing boards time to balance the battery.
    • If there is not enough sunshine to match your usage, wait till the battery has discharged to ~20% (which will be less than 13V) and use the magnum to charge the battery up to 40%-50% either by timing the charge or setting a low charge voltage on the Magnum.

    Simon
    Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
    BMS - Homemade Battery logger github.com/simat/BatteryMonitor Latronics 4kW
    Inverter, homemade MPPT controller

    Leave a comment:


  • karrak
    replied
    You are finding out that it is very hard to charge an LFP battery to an SOC that is not in the high 90% region with low charge rates in a reasonable time, especially if the charge current is not constant.

    I can understand your reluctance to charge your battery to >95%SOC. When I first set my off grid system up with an LFP battery the accepted wisdom seemed to be not to charge above 90% and to not float the battery. My first charge settings were to charge to 3.375V/cell and terminate the charge and not start a new charge till the next day. This regime meant that my battery might be anywhere between ~75%-~95% at the end of the day even if there had been enough solar power to fully charge my battery. This is not very helpful if you don't know if there will be enough sun in the next few days and do not want to use a generator.

    After some research and seeing that there were a number of people in Australia who have been charging and floating their battery at around 98% when the sun was up with no noticeable degradation of their batteries I decided to switch to this charge regime about three years ago. In April this year which is the fourth anniversary of my LFP battery being installed and after around 1,500 cycles the SOC went down to the lowest value that I have ever recorded of ~8%. The average cell voltage at this SOC was 3.0375V which I calculate to be a real SOC of around 5%.

    But what about Maine Sails tests on the cruiser forum which is backed up by this graph?
    LiIonstorage.jpg
    If you look at the LFP cells graphs you can see that the cells they used lost ~5.5% of there capacity when stored at ~70%-100% at 25C for nine moths, ~3% at SOC between ~40%-70% then tapering down to no loss at 0%.

    The big difference between my off grid system and others like my system and these cells is that my cells are in use all the time whereas the cells being tested are not.

    The lesson here is that if you are just storing the cells discharge them down to as low an SOC as you are comfortable with bearing in mind that the cells will self discharge or float them at a voltage of around 3.0V. On the other hand if you are using the battery all the time and are reliant on an unreliable power source like solar charge them up >95% and float them at whatever you are comfortable with to get the best possible use out of the battery.

    Simon
    Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
    BMS - Homemade Battery logger github.com/simat/BatteryMonitor Latronics 4kW
    Inverter, homemade MPPT controller

    Leave a comment:


  • ASprinter
    replied
    Yes, I am not stressing at all, the lowest cell was at 3.35v and highest at 3.37v. I'm not sure how the BMS and shunt interact for the SOC display and don't care, the more I use it I will learn whether or not they mean anything at all. I am thinking I would like something that tracks amp hours in and out (like perhaps a Victron BVM702 or similar) so I have a better idea whether or not the energy I am gaining from solar is offsetting what I use. Maybe the addition of the Magnum BMK would give me the same functionality, but the fact that I don't do a full charge might not make those very effective either.

    This exercise helped prove to me just how irrelevant voltage is when determining SOC. A high charge rate over a short period of time will produce a much different result than a low charge rate over a long span of time, meaning one setting for my various chargers is not practical. I'll just have to play with each and see where I end up.

    I used your mic/chalk/axe anology in a staff meeting yesterday, love it.

    Leave a comment:


  • Sunking
    replied
    Lower the voltage.

    But warning here, just how are you determining SOC. Voltage means nothing. So f your equipment is using voltage, it is a big fat lie.

    The only way to really know SOC is to fully charge each cell to 3.6 volts until current tapers to 2 to 4 amps. Rest it, then fully discharge it and measure AH of each cell. Say a cell measures 100 AH. Now you recharge and only put in 93 AH to get to 90% SOC. Your batteries are roughly 97% efficient charging meaning it will take 103 AH in to have 100 AH capacity.

    You can use a Coulomb counter, but even that is flawed because of battery charge efficiency. They have to be recalibrated every cycle or two to be useful.

    Life is much simpler if you just Bottom Balance and charge to 13.4 to 13.6 volts and quit worrying about minor meaningless details. As long as you are not taking your cells above 3.45 volts, no stress. That is why A123 Systems recommends float charging LFP cells to 3,45 vpc for extended battery life accepting less than fully charged. Try to remember the 3 Golden Rules of design.

    1. Measure things with a Micrometer.
    2. Mark the spot with Chalk.
    3. Cut it with an Axe.

    Well there is a 4th rule and best of all. KISS (keep it simple stupid)
    Last edited by Sunking; 06-21-2017, 05:35 PM.

    Leave a comment:


  • ASprinter
    replied
    Just completed my battery's second charge cycle, but this was the first time I used the Magnum inverter/charger to do the charging . I had the Magnum set for cc/cv at 13.5v thinking I would end at a conservatively low SOC, but I manually terminated the charge early at 13.44v as I did not desire a 100% full battery. What I didn't expect was how soon the Magnum inverter/charger would start reducing current down to just a few amps (more on that in a second.) At a 2.7A charge rate, pack voltage was at 13.44V and SOC was stated at 97%. I had added a 2.5A load when the picture was taken.


    As stated in an earlier post, the moment the Magnum inverter/charger detects shorepower (120vac) it checks the battery voltage and if that voltage is over 13.0V it skips bulk/absorb and goes straight to float "to not overcharge the battery" (lead acid thinking). Obviously 13.0V is a low SOC on my battery, so it started in float and floated at 18A until battery voltage was around 13.37 then started reducing amperage. By 13.39 volts it was only sending about 6 amps to the battery. By 13.44v it was down to 2.7A. The low-C float was going to fill the battery with only a 13.5V float setting.

    This inverter/charger has more settings than most, but it's not the right equipment for the job, mainly due to that 13.0V forced-float-at-startup thing. Luckily I won't be using this to charge much, so the work-around is probably to set a super low float of 13.3. It also means I loose out on the ability to do a quick battery recharge due to the missing bulk phase. I'll continue to experiment.

    Leave a comment:


  • Sunking
    replied
    Originally posted by karrak

    Using your Ri formula and a Voc of 3.3V I get the following Ri values for the various charge rates
    0.5C Ri=1.8mOhms
    1.0C Ri=1.0mOhms
    2.0C Ri=0.75mOhms
    3.0C Ri=0.96mOhms
    If your heat theory was right i don't think we would get these figures.

    You are right when you say that the battery has to obey the laws of physics and Ohms law. The process of converting the chemical energy stored in the battery into the electrical energy that goes into the external electrical circuit is a chemical process that has to obey the laws of chemistry. The chemical processes have an impact on what we see as internal battery resistance. You are right that the Ri of a battery would not vary much if there were no chemical processes going on in the battery but this is obviously not the case.
    You are in denial of facts.

    Leave a comment:


  • karrak
    replied
    Originally posted by Sunking
    Karrak Ri remains fairly constant in a lithium battery. It does not change with the amount of current directly. The deviance you are nit picking is higher currant causes higher temps which lower Ri. If you look for graphs of LFP battery Ri, the Ri looks fairly flap oveer the useful SOC range. It goes up slightly as SOC goes up, and goes down and SOC goes down. It falls off the cliff when completely discharged and shorts out which is death of a lithium battery. Lithium batteries like everything on earth and the heavens live by Ohm;s Law. Only in Karrak's twisted mind does that ever change. No matter what you say, you cannot change math or Ohm's Law. It is the law of physics, not a Speed Limit or No Smoking Sign that can be ignored.
    Using your Ri formula and a Voc of 3.3V I get the following Ri values for the various charge rates
    0.5C Ri=1.8mOhms
    1.0C Ri=1.0mOhms
    2.0C Ri=0.75mOhms
    3.0C Ri=0.96mOhms
    If your heat theory was right i don't think we would get these figures.

    You are right when you say that the battery has to obey the laws of physics and Ohms law. The process of converting the chemical energy stored in the battery into the electrical energy that goes into the external electrical circuit is a chemical process that has to obey the laws of chemistry. The chemical processes have an impact on what we see as internal battery resistance. You are right that the Ri of a battery would not vary much if there were no chemical processes going on in the battery but this is obviously not the case.

    You say "Don't sweat the details. Make the adjustments as you go to make it work." , I say "the devil is in the detail" and "attention to detail". I would rather get the details right from the start rather than have unpleasant surprises happening later on...

    Simon
    Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
    BMS - Homemade Battery logger github.com/simat/BatteryMonitor Latronics 4kW
    Inverter, homemade MPPT controller

    Leave a comment:


  • karrak
    replied
    Originally posted by ASprinter
    Regarding the BMS coulomb counting, if both my BMS and the Magnum can share the same 50mV shunt, I might go ahead and buy the Magnum BMK (the kit without the actual shunt) just to have that amps in/out tracking on the Magnum remote screen. Amps in/out is something my BMS does not report, just a calculated battery SOC.
    Before you buy the BMK I would make sure that it will reset itself properly with your solar charging scheme. The manual says:
    The battery's state of charge which is the best indicator of the condition of the batteries is indicated on your remote/router's SOC display. This display shows that the batteries are fully charged (i.e., SOC = 100%) once the following three conditions have been met: 1. The charging voltage stabilizes over time (see Figure 3-1). 2. The charging current decreases to a low percentage of the AH capacity normally less than 2%. 3. The AH removed from the battery are within 1% of fully being returned.
    This looks like it is designed to detect a lead acid battery going into float after it has been fully charged.

    I would contact Magnum and tell them what battery you have and your solar charge regime and see if they think the BMK will work for you and/or make sure you can return the unit if it doesn't work.

    Simon
    Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
    BMS - Homemade Battery logger github.com/simat/BatteryMonitor Latronics 4kW
    Inverter, homemade MPPT controller

    Leave a comment:


  • Sunking
    replied
    Originally posted by ASprinter
    The math did it for me, that makes perfect sense and I really appreciate you taking the time to explain. That actually ties this whole thread together and explains some of the concepts I was missing.
    Great, you now know more and understand better than Karrak.

    Originally posted by ASprinter
    I feel like I have a good handle on the solar, so now turning to my Magnum inverter/charger shore power source. If I use the "custom battery" setting it lets me set 13.8v absorb, float and equalize (eq can't be less than absorb) but absorb time is a min of 1 hr. I am guessing that absorb will be trying to push some level of amperage into the battery for an hour and that seems like a bad idea. There is a CC/CV mode that lets me set the voltage and has three options for terminating, Done Time, Done Amps or Hold VDC.
    Forget EQ, disable it. You want HOLD DC. Go back to the math and it will help you understand. Solve this equation of a charging battery How many amps are flowing?

    Charge Amps = [Charge Voltage - Battery OCV] / Ri

    Where

    Charger Voltage = 13.6 volts
    Battery OCV = 13.6 volts.
    Ri = Some Integer greater than 0, and less than infinity Ohms, called x

    [13.6 - 13.6] / Some number greater than 0 = 0 / x = 0 Amps

    See what is happening? For there to be any charge current there must be a difference between the charger voltage and battery OCV. 0 volts / by any number = 0 Amps on earth and heaven. Only in Karrrak' s world can there be current with no voltage potential difference. When Battery OCV and Charge Voltage are equal, the battery is Floating and/or Saturated and no current is flowing.

    What you are looking for is that magic voltage between 13.4 and 13.6 volts that gives you th eSOC you want less than 100%. If your panel wattage is right. somewhere around mid day, your battery will Float. Assuming the power demand is lower or equal to what the panels can produce, power to the loads will come from the panels. Otherwise the battery will make up for the shortage. This saves your battery power for night. Understand?

    I am not familiar with your charger, but I do know how to fool it and make it do what you want. Think outside the box. Example set Bulk/Absorb to 13.4 volts and float to 13.6 volts. Or Set Bulk = Absorb = Float = 13.6 volts.

    Now i will say this again. Don't get hung up on 13.6 volts. It is not set in stone. Experiment to find the right voltage that correlates to the SOC you want. Lastly remember this my friend. I learned this first day in college from my engineering instructor and still my fiend and golf partner today. In engineering design:

    We measure things with a Micrometer.
    We mark the spot with Chalk.

    We cut it with an Axe.


    Don't sweat the details. Make the adjustments as you go to make it work.







    Last edited by Sunking; 06-20-2017, 08:39 PM.

    Leave a comment:


  • Sunking
    replied
    Originally posted by karrak
    This completely throws your calculations out and shows that internal battery resistance is not constant and dependent on charge current, could it be something to do with charge transport?
    Karrak Ri remains fairly constant in a lithium battery. It does not change with the amount of current directly. The deviance you are nit picking is higher currant causes higher temps which lower Ri. If you look for graphs of LFP battery Ri, the Ri looks fairly flap oveer the useful SOC range. It goes up slightly as SOC goes up, and goes down and SOC goes down. It falls off the cliff when completely discharged and shorts out which is death of a lithium battery. Lithium batteries like everything on earth and the heavens live by Ohm;s Law. Only in Karrak's twisted mind does that ever change. No matter what you say, you cannot change math or Ohm's Law. It is the law of physics, not a Speed Limit or No Smoking Sign that can be ignored.
    Last edited by Sunking; 06-20-2017, 08:06 PM.

    Leave a comment: