WE Energies to Squash Distributed Renewables with their latest rate case.

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • bcroe
    Solar Fanatic
    • Jan 2012
    • 5247

    #151
    Originally posted by Sunking
    Well crap, that happens when you figure it in your head and forget to move decimal points.
    I enjoy watching you shoot from the hip! Bruce

    Comment

    • SunEagle
      Super Moderator
      • Oct 2012
      • 15210

      #152
      Originally posted by bcroe
      I enjoy watching you shoot from the hip! Bruce
      I have made some incorrect statements myself. It happens to most of us.

      I was surprised to see that any Utility would use 7.2kv for long distance power distribution. Usually that voltage is more for local or subdivision power. Usually you see 13.2kv or 13.8kv but even at that voltage 100 miles seems like a little too long to go. But hey I don't live up in Wisconsin so who knows what they use.

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #153
        Originally posted by SunEagle
        I have made some incorrect statements myself. It happens to most of us.

        I was surprised to see that any Utility would use 7.2kv for long distance power distribution. Usually that voltage is more for local or subdivision power. Usually you see 13.2kv or 13.8kv but even at that voltage 100 miles seems like a little too long to go. But hey I don't live up in Wisconsin so who knows what they use.
        Not possible to do 100 miles at 13.2 at any usable amperage. REA's are limited to 10% losses. Typically for Rural you would transport power at 69, 135, or 750 KV to a local distribution transformer centrally located, then run 13.2 laterals. Late night last night so I messed that up. Came up last Wednesday to Dallas to celebrate my b-day and go to the OU/TX game. Time to go back to paradise.
        MSEE, PE

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #154
          Originally posted by bcroe
          I don't see how putting the 3 phase Delta through 3 single phase transformers helps balance
          phase loads. Bruce Roe
          Sorry I should have answered this. Let's use a real life example. Say a 480 Delta input transformer with Wye 208/120. Pretty typical setup in a commercial application. So lets say we load up Phase A to 100 amps line to neutral loads (120 volts). What is the current on the Delta Primary side?

          Correct answer is Phase A = Phase B = Phase C = 8.3 amps. In a delta system all three phase currents have to be equal regardless if the secondary is balanced or not. The way to handle such a situation is to use what we call a K rated transformer which is made to be used on non linear loads where the neutral return conductor is larger than the phase conductors, and the core is made heavier to handle the extra heat generated.

          Hope that helps.
          MSEE, PE

          Comment

          • SunEagle
            Super Moderator
            • Oct 2012
            • 15210

            #155
            Originally posted by Sunking
            Sorry I should have answered this. Let's use a real life example. Say a 480 Delta input transformer with Wye 208/120. Pretty typical setup in a commercial application. So lets say we load up Phase A to 100 amps line to neutral loads (120 volts). What is the current on the Delta Primary side?

            Correct answer is Phase A = Phase B = Phase C = 8.3 amps. In a delta system all three phase currents have to be equal regardless if the secondary is balanced or not. The way to handle such a situation is to use what we call a K rated transformer which is made to be used on non linear loads where the neutral return conductor is larger than the phase conductors, and the core is made heavier to handle the extra heat generated.

            Hope that helps.
            A harmonic mitigating transformer also has a different winding configuration where the phase angles (or vectors) will cancel out the harmonics on each phase and reduce the current on the neutral wire. That reduces the amount of heat generated as well as the losses in the transformers and actually saves the user by reducing the amount of kW used.

            Comment

            • ChrisOlson
              Solar Fanatic
              • Sep 2013
              • 630

              #156
              Originally posted by SunEagle
              I was surprised to see that any Utility would use 7.2kv for long distance power distribution..
              They did it up here 40 years ago because back then there was only about 6 subscribers on it. It's never been upgraded as they added loads to it. So now the entire area browns out every time somebody turns something on.
              off-grid in Northern Wisconsin for 14 years

              Comment

              • SunEagle
                Super Moderator
                • Oct 2012
                • 15210

                #157
                Originally posted by ChrisOlson
                They did it up here 40 years ago because back then there was only about 6 subscribers on it. It's never been upgraded as they added loads to it. So now the entire area browns out every time somebody turns something on.
                Heck at that distribution voltage I would expect a brown out if someone flushes a toilet. No wonder a lot of people up there have gone off grid.

                Comment

                • ChrisOlson
                  Solar Fanatic
                  • Sep 2013
                  • 630

                  #158
                  Originally posted by SunEagle
                  Heck at that distribution voltage I would expect a brown out if someone flushes a toilet. No wonder a lot of people up there have gone off grid.
                  Off-grid is the only practical solution for many cabins and part-time or seasonal homes here. Most of the weekend cabins just have a generator with a few batteries and an Outback inverter with a transformer on it to run a well pump. Few of the weekenders have solar or wind power.

                  Many years ago they were going to run a big transmission line from someplace down south to Duluth. They had problems with people setting up on hillsides a mile or more away with a Barrett 50 and shooting the insulators off as they were trying to build the line. The line crew quit the day a lineman was working on a pole and suddenly an insulator right next to him exploded, thanks to a 500 grain, 50 caliber Browning Machine Gun round that came from a hillside like a mile away. They pretty much abandoned the whole idea because the Scandinavians that live up here are a little on the independent side, and the rest of it is Indian Reservations along with 1.5 million acres of woods in the Chequamegon.
                  off-grid in Northern Wisconsin for 14 years

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #159
                    Originally posted by ChrisOlson
                    Many years ago they were going to run a big transmission line from someplace down south to Duluth. They had problems with people setting up on hillsides a mile or more away with a Barrett 50 and shooting the insulators off as they were trying to build the line. The line crew quit the day a lineman was working on a pole and suddenly an insulator right next to him exploded, thanks to a 500 grain, 50 caliber Browning Machine Gun round that came from a hillside like a mile away. They pretty much abandoned the whole idea because the Scandinavians that live up here are a little on the independent side, and the rest of it is Indian Reservations along with 1.5 million acres of woods in the Chequamegon.
                    Sounds like a good place for Moonshiners.
                    MSEE, PE

                    Comment

                    • Sunking
                      Solar Fanatic
                      • Feb 2010
                      • 23301

                      #160
                      Originally posted by ChrisOlson
                      They did it up here 40 years ago because back then there was only about 6 subscribers on it. It's never been upgraded as they added loads to it. So now the entire area browns out every time somebody turns something on.
                      Chris I assume the POCO is a CooP? If so has anyone gone to the REA to file a complaint? CooP's get their funding from Uncle Sam in the form of low interest loans. To qualify minimum standards must be followed and one of those is a +/- 10% voltage regulation. On a Single Phase service operating voltage is 250/125 so on the low end you are looking at 225/112 and 275/138 on the high end. All are within operating limits of any thing made or sold in the USA that is UL listed to use AC power.
                      MSEE, PE

                      Comment

                      • bcroe
                        Solar Fanatic
                        • Jan 2012
                        • 5247

                        #161
                        3 phase transformer

                        Originally posted by SunEagle
                        A harmonic mitigating transformer also has a different winding
                        configuration where the phase angles (or vectors) will cancel out the harmonics on each
                        phase and reduce the current on the neutral wire. That reduces the amount of heat generated
                        as well as the losses in the transformers and actually saves the user by reducing the amount
                        of kW used.
                        I'm no expert on transformers, but I believe this is about a transformer with a single iron core
                        (with branches) common to different windings for all phases? Not 3 separate transformers?
                        Bruce Roe

                        Comment

                        • ChrisOlson
                          Solar Fanatic
                          • Sep 2013
                          • 630

                          #162
                          Originally posted by Sunking
                          Chris I assume the POCO is a CooP? If so has anyone gone to the REA to file a complaint? CooP's get their funding from Uncle Sam in the form of low interest loans..
                          Plenty of complaints, but basically there's no money and no right-of-ways to run lines. The residences are so spread out that it costs in the millions to upgrade for just a few homes on one feeder. The towns like Hayward and Cable, or Ashland, have good power. But out in the rural areas it's pretty sketchy. People will complain one day about poor electrical service, then the next day they're all carrying rifles and shotguns ready to shoot anybody that tries to come on their property to string electric lines across it, or cut one of their trees down.

                          It costs any electric utility in the millions just to get an easement across all the private land, and even if they do win a day in court and get one they have to face gunfire in order to act on it. So nothing much has changed here in the last 40 years. There is not a place around here that doesn't have at least a generator. Farm & Fleet and Menards sells those worthless Generac 8 and 12 kW Guardian units by the trainload up here.
                          off-grid in Northern Wisconsin for 14 years

                          Comment

                          • ChrisOlson
                            Solar Fanatic
                            • Sep 2013
                            • 630

                            #163
                            Originally posted by bcroe
                            I'm no expert on transformers, but I believe this is about a transformer with a single iron core
                            (with branches) common to different windings for all phases? Not 3 separate transformers?
                            Up here they put a transformer on each phase for three-phase service. And they don't pay much attention to which phase they tap off of for single phase service drop. They usually tap off a single phase service on which ever wire is closest to the residence. And there's a couple places where they put in a transformer then run low-voltage 240V split-phase overhead to 5 or 6 houses with a single 50 kVA transformer, and hope the people don't all turn all their stuff all at the same time.
                            off-grid in Northern Wisconsin for 14 years

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #164
                              Your area needs a SWER system like they use in Alaska, Canada, Africa, Brazil, Upper Midwest USA, New Zealand, and Australia Outback. . Super easy cheap conversion. Can even be done with HVDC.
                              MSEE, PE

                              Comment

                              • SunEagle
                                Super Moderator
                                • Oct 2012
                                • 15210

                                #165
                                Originally posted by bcroe
                                I'm no expert on transformers, but I believe this is about a transformer with a single iron core
                                (with branches) common to different windings for all phases? Not 3 separate transformers?
                                Bruce Roe
                                Correct. Most transformers that create 208y/120v are a single 3 phase type.

                                The harmonic mitigating type are sometimes call Z winding and can be configured for multiple phase angles depending on what you are trying to do.

                                Comment

                                Working...