Was just wondering is ther a limit to how many panels you can join up in parellel using mc4 Y branch connectors before using a combiner box
Try our solar cost and savings calculator
Mc4 connectors
Collapse
X
-
-
Current limit is determined by the size of the wire used. The more you have in parallel the higher the current.3.6 kw PV, Classic 150, Radian GS4048A, LFP 195A -
Comment
-
Comment
-
Comment
-
Comment
-
Two strings is usually the limit, because above that the individual strings need over current protection anyway. I have found the MidNite combiner boxes to be a good value and it helps keep all the wiring neat and indentfiableComment
-
Ok thanks heaps I was just trying to make it easy for myself I have a heap of branch connectors but no combiner box the nearest shop is 400km away so all my new toys will have to wait cheersComment
-
The limit is based on the current rating of the connectors, usually 20-30 A. If you combine more than two panels, you can still avoid a junction box if you put an mc4 inline fuse on each panel.CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment
-
Yes, the inline fuses can be done but it can soon become a hornet's nest of ugly wiring, and then there's no good disconnect, no good string isolation for troubleshooting or upgrades... not to mention a good space for labeling etc.Comment
-
No probs was thinking I might make my own combiner box to save some coin ...would putting 2 bus bars +&- putting all cables in and having a 40amp breaker fuse between it and charge controller should work ehComment
-
Each string needs it's own breaker. By the time you have everything together the MidNite combiner looks like a relative bargain. Plus it already will pass inspection when wired correctlyComment
-
Ha ha didn't realise that I wonder if all them blokes on YouTube still have houses ... cheers b17 your advice has been invaluableComment
-
Just watched a YouTube video of a guy from renogy which is supposed to be a good company using branch connectors to connect 4 strings together with no fuses ... now you guys are confusing meComment
-
No fuses with more than two parallel panels is a bad idea, not compliant with the panel's installation instructions or any applicable code.CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment