Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister -
How are Lazard's figures inaccurate?
Karrak quoted their unsubsidized figures, so it's not that they're hiding costs that way.
Maybe it's that they're quoting prices for new generation, but there's already sufficient fossil generation in place?
Or maybe you mean Lazard doesn't include the cost of conditioning the power for retail use?
For that you'd also need to add storage, peaker plants, and/or demand management... which aren't cheap.
It's fair to say that renewable is not competitive for "baseload" power except in special circumstances yet.
But now that utility scale storage is proving itself, and as costs keep falling, it's going to be a practical option in more circumstances as time goes on.
(Data from LBL confirms the low daytime solar prices listed by Lazard.
blogs.scientificamerican.com/plugged-in/the-price-of-solar-is-declining-to-unprecedented-lows
says "The latest data show that the 2015 solar PPA price fell below $50 per megawatt-hour (or 5 cents per kilowatt-hour) in 4 of the 5 regions analyzed"
It also confirms their wind price figures;
emp.lbl.gov/publications/2015-wind-technologies-market-report says "the average [subsidized] levelized long-term price from wind power sales agreements has dropped to around 2 cents per kWh.
I think the PTC is about 2.3 cents per kWh, so that puts both wind and solar around 4 to 5 cents per kWh in regions where they are plentiful.
Wholesale electricity is 3 to 4 cents per kWh, so costs need to fall by a cent or so, or about 25%, to really bite into old fossil's market share.
Removing the existing subsidies for fossil fuel would also help.
Another interesting site that just popped up: energy.utexas.edu/the-full-cost-of-electricity-fce/ has a report on cost of energy, and a map of the cost of various kinds of energy that lets you fiddle with things like co2 pricing to see at what carbon price does wind or solar become competitive.)
Utility storage via batteries has a way to go to prove itself. It ain't a done deal yet. Until the price of battery storage to/from the grid becomes less than gas peaker power to the grid, with the same reliability, battery storage will not be widespread, or only more common where that inequality holds.Comment
-
(7,200 MW)*( 8,760 hr./yr.)* (.90 capacity factor) = 5.68 mWh/yr.
So, 200/(5.7 EE 7) ~ = 3.5 EE -6 or .0004 % or so, or 1/285,714 of potential total system output.
A better question to you might be: Do you think that a new technology that can supplant ~ 1/285,714 of a system's annual generating capabilities, or 44 min. out of an entire year's capacity qualifies as proven and working, or mainstream? That's about like spit in the ocean for a lot of us, and may knock battery storage out of the "qualifies as mainstream" box for now.
I'm not sure how many affirmative answers you'd get if you put the question that way. Potential for the future ? Probably. Proven ? ? ? Keep working on it and playing the devil's advocate seems a wiser course to me rather than the Pollyanna, rose colored glasses outlook you usually have.Comment
-
Once Aliso was offline, what would you have done?
it could hold 86 billion cubic feet. Not sure how much a steel tank would cost; might need to liquify the gas to get enough into a practical tank. I suspect an LNG tank costs $200 million per billion cubic feet of gas. Batteries may well be cheaper... At 33 cubic ft per kWh, 300 MWh = 10 billion cubic feet. Check my math, but it seems a tank would have been more expensive.
I wonder if the reason they went for batteries rather than storage tanks was time-to-completion, rather than cost.Comment
-
It isn't the technology. That has been around a long time. It comes down to how much does it cost to generate a kWh from a high density battery system and is that cost being paid by the consumers?
What I hear from a lot of forum members is that the cost of electricity from their POCO is high which is why they want to install solar so they can pay less.
Well what if the cost goes up 25% to cover those grid tie battery systems? I expect more of the members will complain and say the POCO is stealing from them. But the truth is that going with more RE with battery storage and less fossil fuel is causing the cost of electricity to go up. It happened in Germany and it is happening in CA.
Why don't you admit to that fact or are you so wrapped up with what you want you chose not to be honest about it?Comment
-
If I look long enough I bet I can find all kings of "data" that will prove my point but go ahead and believe what you want. Just remember that most other countries still use fossil fuel because they can't afford RE.
I am not against using RE to generate power. I just know that it can't provide what the earth consumers 24/7/365 so you better have something else that works all the time.Comment
-
Originally posted by SunEagleDan please stop looking for articles that are pie in the sky. I would rather see proven technology that is already working.
...
It isn't the technology. That has been around a long time.
As for cost: battery storage is going to save ratepayers in Kauai money, I think. That imported fossil fuel ain't cheap.
And as the costs of solar, wind, and storage continue to fall, the percent of penetration of renewable that is economically viable without subsidies will increase.
Anything dishonest about any of that?Comment
-
Fresh day, fresh coffee, time for a math and fact check. eia.gov/tools/faqs/faq.cfm?id=667&t=8 says it's 10 cubic ft per kWh, not 33. And 300,000 kWh * 10 = 3 million cubic feet, not 10 billion. Sheesh. (Check that math again!)
I wonder if the reason they went for batteries rather than storage tanks was time-to-completion, rather than cost.
I seriously doubt above ground storage of that quantity (mass) of LNG would be attempted for lots of reasons. Even with a 600 to one volume reduction, gas to liquid, the containment for LNG would still require 86*10^9/600 = ~ 1.43 *10^8 ft.^3. of what would probably be vacuum jacketed tankage. If each tank were 10 ft. in diameter and 40 ft. long, it'd require about 6,500 - 6600 such tanks. Or, if a single tank w/ height = diameter = ~ 325 ft. ! Not happening any time soon.
And BTW, where did you get that number of 33 ft.^3/kWh ? W.T.F. is that ? 1ft.^ of nat. gas has a heating value of ~ 950 -1050 BTU depending on where it comes from with 1,000 BTU/ft.^3 usually used for easy calcing.
33 * 1,000 = 33,000 BTU. 1kWh == 3,412 BTU. 33,000/3412 = 9.67kWh.
Even at 10 ft.^3 /kWh, as you've so graciously corrected, it's still way off without some details and qualifiers you are absolutely clueless about, and without which, makes the number 10ft.^3/*kWh quite and utterly senseless.
I usually suggest, but I'll tell you straight: Get your own numbers right and take some responsibility to get your stuff correct before you puke this kind of crap out without having enough common courtesy and respect for others to not check your sources or your own math. And while you're at it, get better sources, and maybe think about looking at more than one side of an issue as well.
Better yet, just stop doing it altogether. This is a typical example of your inconsiderate, irresponsible, childish behavior. Who do you think you are ? Someone who gets to clamor, throw feces all over the place, draw attention to yourself, and then leave the mess for others to correct and clean up ? And then get to do it all over again ? B.S.
I'm about the biggest R.E. fan I know of, but your behavior makes it tough to be taken seriously. You're not helping. You're hurting by giving the naysayers a poster child and a focal point for everything they see wrong with R.E., and that, sure as hell, is not leading by example. Your behavior is an embarrassment.
Grow up and knock off the B.S. - Seriously. If you were working for me, I'd have separated you and your shenanigans from my organization before it got to this level.
IMO, you actions are now long past being a distraction and have turned into a disruption. As someone who's trying to be a professional and convey useful, hopefully helpful, technically correct, experientially based, and, above all, safe information pertinent to things that have changed my life and Believe I know a bit about, I find your unprofessional, juvenile attitude and behavior sad beyond discouraging to the point of being disgusting and personally offensive.
J.P.M.Last edited by J.P.M.; 02-05-2017, 11:26 AM. Reason: Corrected SCFM to SCF = Standard cuubic feet. Apologies. Math stays the same.Comment
-
It was a political decision, not a financial one.
Also, it hasn't been maintained for several years.
Comment
-
There's a big, careful plan for mitigating the loss of the field, and one small part
of it is those 72MW , 300 MWh batteries.
To estimate how much gas that battery would replace, and how big a tank that would take, the figure of 10 cubic feet / kWh given in http://www.eia.gov/tools/faqs/faq.cfm?id=667 is close enough for back-of-the-envelope calculations like this. (Might be off by some small factor, but that's fine.)
So: battery capacity of 300,000 kWh * 10 cu ft / kWh = 3 million cubic feet.
If it were stored as LNG, with your reduction figure of 600, that'd be 3 million / 600 = 5000 cubic feet of LNG. Using your 10 foot diameter, 40 foot long tanks, it'd take ... 2 tanks.
Which makes liquifying seem like overkill for this application, CNG might do... if it has a reduction ratio of 100, then you'd need what, 10 of those tanks. Which seems practical.
(Also, SCFM = cubic feet per minute? If you want to talk rates, the batteries have a total power of 72MW = 1200 kWh/min, which would replace about 12,000 SCFM of gas.)
Unless I made another boneheaded mistake, which isn't unlikely.
So... why'd they choose batteries over tanks?
There was already a plan to install batteries for other reasons, it's possible that fast-tracking that let them get it all online faster than a CNG storage facility could be designed / permitted / built (anyone know?).
The contracts were started in August ( greentechmedia.com/articles/read/california-utilities-are-fast-tracking-battery-projects-to-manage-aliso-can ), and the batteries are already online, what, six months later.Last edited by DanKegel; 02-05-2017, 03:13 AM.Comment
-
Originally posted by DanKegelAlso, it hasn't been maintained for several years.
Tom Palmisano, the plant's chief nuclear officer... said,
"I've not been maintaining equipment because it's retired...
There's no salvage value. It's all going to be removed and disposed
of as part of decommissioning."
...
A former president of the American Nuclear Society, who has called the
shutting down of San Onofre "a tragedy for California," said earlier
this year that bringing the plant back online at this point is almost
impossible.Last edited by DanKegel; 02-05-2017, 02:59 AM.Comment
-
Just remember that most other countries still use fossil fuel because they can't afford RE
I am not against using RE to generate power. I just know that it can't provide what the earth consumers 24/7/365 so you better have something else that works all the time.
The cost reductions of RE, especially energy storage have a long way to go. I think that as this cost reduction occurs, and as the grid control technology gets better we will see a greater and greater percentage of RE being able to compete with fossil fuel generated power, hopefully RE generated power will reach 100% in a reasonable time frame. In my opinion due to global warming it is imperative and will cost less in the longer term if this happens as soon as possible.
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor
Latronics 4kW Inverter, homemade MPPT controller
Off-Grid LFP(LiFePO4) system since April 2013Comment
-
Nice out you have there.
As for verification, seems to me you usually assume your stuff is on the high ground and disproof by others is required, rather than making your case and taking your chances. Instead of doing that, when you have not proven your case other than a restatement or references of what others have written, and someone calls B.S. on your stuff, you backtrack and say "prove you're right", rather than making a case why your position is better or more correct in the first place. I think it ought to be the other way around. Make your case on your interpretation of the situation based on what you know, not solely on what you read someplace. That's where your admitted not knowing much shows and gets you in trouble. Doing it right is called contributing, or adding to the discussion. What you mostly do is little more than a me-to pass through of stuff by others (which you again, assume to be an accurate reflection of reality) that adds nothing to the body of knowledge and adds nothing to the discussion except more confusion. IMO, that's disrespectful and rude.
Comment
-
They're not replacing the whole field with tanks or batteries.
There's a big, careful plan for mitigating the loss of the field, and one small part
of it is those 72MW , 300 MWh batteries.
To estimate how much gas that battery would replace, and how big a tank that would take, the figure of 10 cubic feet / kWh given in http://www.eia.gov/tools/faqs/faq.cfm?id=667 is close enough for back-of-the-envelope calculations like this. (Might be off by some small factor, but that's fine.)
So: battery capacity of 300,000 kWh * 10 cu ft / kWh = 3 million cubic feet.
If it were stored as LNG, with your reduction figure of 600, that'd be 3 million / 600 = 5000 cubic feet of LNG. Using your 10 foot diameter, 40 foot long tanks, it'd take ... 2 tanks.
Which makes liquifying seem like overkill for this application, CNG might do... if it has a reduction ratio of 100, then you'd need what, 10 of those tanks. Which seems practical.
(Also, SCFM = cubic feet per minute? If you want to talk rates, the batteries have a total power of 72MW = 1200 kWh/min, which would replace about 12,000 SCFM of gas.)
Unless I made another boneheaded mistake, which isn't unlikely.
So... why'd they choose batteries over tanks?
There was already a plan to install batteries for other reasons, it's possible that fast-tracking that let them get it all online faster than a CNG storage facility could be designed / permitted / built (anyone know?).
The contracts were started in August ( greentechmedia.com/articles/read/california-utilities-are-fast-tracking-battery-projects-to-manage-aliso-can ), and the batteries are already online, what, six months later.Comment
-
Well, is it the technology, or isn't it? Make up your mind
As for cost: battery storage is going to save ratepayers in Kauai money, I think. That imported fossil fuel ain't cheap.
And as the costs of solar, wind, and storage continue to fall, the percent of penetration of renewable that is economically viable without subsidies will increase.
Anything dishonest about any of that?
If you believe that RE is cheaper then you are being dishonest with yourself. That is the truth.Comment