    Today I received the panels and the inverter. I looked at one panel and did not see any other stickers than a serial number and the model number. I was expecting all these stickers with all the certifications. The vendor website info, (see link above) says that model number is UL listed. Is that good enough?

    Comment

    • Naptown
      Solar Fanatic
      • Feb 2011
      • 6880

      #17
      there should be a sticker on the back of the panel near the junction box with the certifications and spec's
      NABCEP certified Technical Sales Professional

      [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

      [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

      [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

      Comment

      • danleaf
        Junior Member
        • Jan 2012
        • 22

        #18
        Originally posted by Naptown
        there should be a sticker on the back of the panel near the junction box with the certifications and spec's
        Here are the pictures of the panel sticker and the pallet sticker. Now I am confused again. Looks like Sunelec remove manufacturer's labels and put their own at a lower rating. What are these panels now?Still JA Solar?


        PanelSticker.jpg

        PalletSticker.jpg

        Comment

        • russ
          Solar Fanatic
          • Jul 2009
          • 10360

          #19
          Originally posted by danleaf
          Here are the pictures of the panel sticker and the pallet sticker. Now I am confused again. Looks like Sunelec remove manufacturer's labels and put their own at a lower rating. What are these panels now?Still JA Solar?


          [ATTACH=CONFIG]2842[/ATTACH]

          [ATTACH=CONFIG]2843[/ATTACH]
          Ask JA Solar - Maybe Sun Elec is playing games? It looks like they would now be responsible for the warranty? If so it is probably meaningless.
          [SIGPIC][/SIGPIC]

          Comment

          • danleaf
            Junior Member
            • Jan 2012
            • 22

            #20
            Originally posted by russ
            Ask JA Solar - Maybe Sun Elec is playing games? It looks like they would now be responsible for the warranty? If so it is probably meaningless.
            It is not the warranty I am worried about, is about passing the inspection.

            Comment

            • russ
              Solar Fanatic
              • Jul 2009
              • 10360

              #21
              Originally posted by danleaf
              It is not the warranty I am worried about, is about passing the inspection.
              Ask JA Solar - This would not appear to be their doing but the end supplier playing games.

              No mention of a UL listing
              Last edited by russ; 04-26-2013, 01:16 AM. Reason: added
              [SIGPIC][/SIGPIC]

              Comment

              • danleaf
                Junior Member
                • Jan 2012
                • 22

                #22
                Panels passed, but I still failed the inspection

                Originally posted by danleaf
                It is not the warranty I am worried about, is about passing the inspection.
                Well the day of the inspection came. Was raining like crazy here and the inspector did not want to go on the roof. So the panels passed based on the catalog information.

                But I still failed the inspection because the Kaco inverter did not have an UL logo on the sticker, because was not "listed". I called Kaco and they say, and I believe they are right, that the TUV Rheinland of North America logo should satisfy the "listed" requirement. The reason that I believe they are right is because TUV is part of the National Recognized Testing Laboratories and is certified in WA state to do UL 1741 testing. Should this new info be enough to pass the inspection?

                Thank you.

                Comment

                • KRenn
                  Solar Fanatic
                  • Dec 2010
                  • 579

                  #23
                  Originally posted by danleaf
                  Well the day of the inspection came. Was raining like crazy here and the inspector did not want to go on the roof. So the panels passed based on the catalog information.

                  But I still failed the inspection because the Kaco inverter did not have an UL logo on the sticker, because was not "listed". I called Kaco and they say, and I believe they are right, that the TUV Rheinland of North America logo should satisfy the "listed" requirement. The reason that I believe they are right is because TUV is part of the National Recognized Testing Laboratories and is certified in WA state to do UL 1741 testing. Should this new info be enough to pass the inspection?

                  Thank you.


                  It all entirely depends on the utility, and your willingness to prove you are within the requirements. Essentially the utility can demand the UL logo.....you can fight them by utilizing current code and showing how the inverter meets their requirements, but that can be some real uphill hand-to-hand combat.


                  Personally I would never recommend a Kaco inverter though, have seen a lot of issues with their inverters malfunctioning....etc.

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #24
                    Originally posted by danleaf
                    But I still failed the inspection because the Kaco inverter did not have an UL logo on the sticker, because was not "listed". I called Kaco and they say, and I believe they are right, that the TUV Rheinland of North America logo should satisfy the "listed" requirement. The reason that I believe they are right is because TUV is part of the National Recognized Testing Laboratories and is certified in WA state to do UL 1741 testing. Should this new info be enough to pass the inspection?
                    No it will not pass no matter how much you or the manufacture wishes it will pass.

                    There are two rules you must remember when working with AHJ (inspectors aka Authority Having Jurisdiction))

                    1. The Inspector is always right.
                    2. When inspector is wrong refer to rule # 1.

                    The inspector has you by the balls, and the code and law on his side. Reference Definitions in NEC:

                    Listed. Equipment
                    , materials, or services included in a list
                    published by an organization that is acceptable to the authority
                    having jurisdiction and concerned with evaluation
                    of products or services
                    , that maintains periodic inspection
                    of production of listed equipment or materials or periodic
                    evaluation of services, and whose listing states that either
                    the equipment, material, or service meets appropriate designated
                    standards or has been tested and found suitable for
                    a specified purpose.

                    FPN: The means for identifying listed equipment may vary
                    for each organization concerned with product evaluation,
                    some of which do not recognize equipment as listed unless
                    it is also labeled. Use of the system employed by the listing
                    organization allows the authority having jurisdiction to
                    identify a listed product.


                    This part right here makes the AHJ correct and you cannot fight it. He/she simply does not recognize TUV as a recognized testing Lab. He wants and will only accept UL. End of story. It should have been caught during the permit phase and your permit denied for using unlisted equipment. Bet you $10 a material list was not submitted, or material was substituted.

                    acceptable to the authority having jurisdiction and concerned with evaluation of products or services
                    MSEE, PE

                    Comment

                    • inetdog
                      Super Moderator
                      • May 2012
                      • 9909

                      #25
                      Originally posted by Sunking
                      This part right here makes the AHJ correct and you cannot fight it. He/she simply does not recognize TUV as a recognized testing Lab. He wants and will only accept UL. End of story.
                      And hence the slightly paradoxical phenomenon of state or locally adopted lists of Nationally Recognized Testing Laboratories.

                      Your only hope, and a slim one, is if your state or locality has formally adopted such a list and done it in a way that explicitly trumped the authority of each AHJ or inspector to make that judgement on their own.
                      SunnyBoy 3000 US, 18 BP Solar 175B panels.

                      Comment

                      • danleaf
                        Junior Member
                        • Jan 2012
                        • 22

                        #26
                        Originally posted by inetdog
                        And hence the slightly paradoxical phenomenon of state or locally adopted lists of Nationally Recognized Testing Laboratories.

                        Your only hope, and a slim one, is if your state or locality has formally adopted such a list and done it in a way that explicitly trumped the authority of each AHJ or inspector to make that judgement on their own.
                        I might just be really lucky: http://www.lni.wa.gov/tradeslicensin...st/default.asp
                        WA state does have TUV in their accredited list. The inspector did suggest as a "solution" to get a third party to certify the inverter. But will the third party put the UL mark on it? Or their own mark? TUV does have their mark on the inverter http://www.tuv.com/en/usa/services_u...tion.html#tab3

                        The irony is that I live within a few miles from one of the main UL testing labs.

                        I emailed the inspector, I am now waiting for his reply.

                        Comment

                        • inetdog
                          Super Moderator
                          • May 2012
                          • 9909

                          #27
                          Originally posted by danleaf
                          WA state does have TUV in their accredited list. The inspector did suggest as a "solution" to get a third party to certify the inverter. But will the third party put the UL mark on it? Or their own mark? TUV does have their mark on the inverter
                          All that TUV can do is put a TUV or TUV-NA mark on it and identify the standard to which it was tested (which may be a UL standard.) So what you need may be there already. There are also NRTLs besides UL that are based in the US, and the inspector may be trying to hold out for one of those. If so he is on shaky ground.

                          Now if TUV only tested the inverter to european standards, it would do you no good at all.
                          SunnyBoy 3000 US, 18 BP Solar 175B panels.

                          Comment

                          • danleaf
                            Junior Member
                            • Jan 2012
                            • 22

                            #28
                            Originally posted by Sunking
                            No it will not pass no matter how much you or the manufacture wishes it will pass.

                            There are two rules you must remember when working with AHJ (inspectors aka Authority Having Jurisdiction))

                            1. The Inspector is always right.
                            2. When inspector is wrong refer to rule # 1.

                            The inspector has you by the balls, and the code and law on his side. Reference Definitions in NEC:

                            Listed. Equipment
                            , materials, or services included in a list
                            published by an organization that is acceptable to the authority
                            having jurisdiction and concerned with evaluation
                            of products or services
                            , that maintains periodic inspection
                            of production of listed equipment or materials or periodic
                            evaluation of services, and whose listing states that either
                            the equipment, material, or service meets appropriate designated
                            standards or has been tested and found suitable for
                            a specified purpose.

                            FPN: The means for identifying listed equipment may vary
                            for each organization concerned with product evaluation,
                            some of which do not recognize equipment as listed unless
                            it is also labeled. Use of the system employed by the listing
                            organization allows the authority having jurisdiction to
                            identify a listed product.


                            This part right here makes the AHJ correct and you cannot fight it. He/she simply does not recognize TUV as a recognized testing Lab. He wants and will only accept UL. End of story. It should have been caught during the permit phase and your permit denied for using unlisted equipment. Bet you $10 a material list was not submitted, or material was substituted.
                            It seems to me the inspectors have way to much power, they are still humans not God. The same inspector touched a split bolt grounding connection at the inverter that I believe it was suppose to be irreversible connection. He did not say anything.

                            I did go to their office with all the documentation before I start working and they only looked at the one line and called it good.

                            You say the inverter is not listed, but TUV is recognized by OSHA and WA state to perform UL 1741 standard certifications. So the TUV mark on the inverter shows that it is listed.

                            I still hope that he will accept the TUV mark. The WA state law says he should.

                            Comment

                            • danleaf
                              Junior Member
                              • Jan 2012
                              • 22

                              #29
                              Originally posted by inetdog
                              All that TUV can do is put a TUV or TUV-NA mark on it and identify the standard to which it was tested (which may be a UL standard.) So what you need may be there already. There are also NRTLs besides UL that are based in the US, and the inspector may be trying to hold out for one of those. If so he is on shaky ground.

                              Now if TUV only tested the inverter to european standards, it would do you no good at all.
                              Here is a picture of the sticker:

                              20130522_154125.jpg

                              The certificate in the manual says it was tested to UL 1741.

                              Comment

                              • KRenn
                                Solar Fanatic
                                • Dec 2010
                                • 579

                                #30
                                Originally posted by danleaf
                                Here is a picture of the sticker:

                                [ATTACH=CONFIG]2906[/ATTACH]

                                The certificate in the manual says it was tested to UL 1741.


                                Did you install the system yourself or did have a 3rd party install it?