Hot Water by Solar Electric direct via MPPT ?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • bcroe
    Solar Fanatic
    • Jan 2012
    • 5198

    #46
    Originally posted by Tgriff

    I checked the SSR specs and it claims < 1.5V "on voltage". At 9.5 amps, this would be 9.5 * 1.5 = 135 watts
    power dissipation when on. No wonder they burned up on me!
    Better check your slide rule, mine says 9.5A times 1.5V equals 14.25 watts. Bruce Roe

    Comment

    • Tgriff
      Junior Member
      • Jan 2019
      • 12

      #47
      OK ... thanks for the catch. My calculator must have had another number in the works. Still . . . 14.5 watts per SSR is significant - even if both not on at same time! It makes the need for forced cooling in a closet with a water heater. I'm thinking of using a 5V computer fan for the SSR heat syncs.

      BTW: I watched a video of the recommended installation of conventional solar water heaters, and it required cutting holes in the roof for the plumbing. This alone is a deal-breaker for me - especially with the declining price of solar panels.

      A few years ago, the thought of using solar panels to heat water was considered a huge waste - but not any more. I paid $1 / watt for my panels and it is now less than half that price, making the solar panels a cheaper part of the equation. What other unusual applications can be solar powered? Swimming pools, sub-floor heating, geothermal HVAC (now my passion)?

      Comment

      • PNPmacnab
        Solar Fanatic
        • Nov 2016
        • 424

        #48
        Many electronic wall warts will work on as little as 50V DC. This is at very reduced current, but can easily produce 100ma to run small devices like a micro. Everyone has a few wall warts collecting dust. I buy these 12V 1.2A supplies shipped from China for only $1.50 total and they even come in an aluminum case. One resistor change insures they will start on as little as 40V. I run full DC heater current thru the heaters mechanical thermostat. A circuit keeps the voltage potential across the contacts at no more than 20V ever. Did a demo with a single strand of copper wire imitating the mechanical contact. I tried to make and break the connection as slow as I could a couple dozen times. Not a hint of an arc. Try that normally and you better be wearing a welding helmet to protect your eyes.

        Comment

        • jflorey2
          Solar Fanatic
          • Aug 2015
          • 2331

          #49
          Originally posted by Tgriff
          Arc-fault checking isn't necessary if the supply power is chopped to near-zero several times / second.
          Right. But:

          1) most PWM controllers don't do that (they run slower)
          2) if you are turning the power on and off anyway you don't need a separate switch in the thermostat to switch the current. Just use the thing that's already turning the power on and off.
          3) a PWM controller isn't needed for a heating element anyway. You're not going to overpower it.

          Comment

          • Tgriff
            Junior Member
            • Jan 2019
            • 12

            #50
            Originally posted by jflorey2
            Right. But:

            1) most PWM controllers don't do that (they run slower)
            2) if you are turning the power on and off anyway you don't need a separate switch in the thermostat to switch the current. Just use the thing that's already turning the power on and off.
            3) a PWM controller isn't needed for a heating element anyway. You're not going to overpower it.
            1. I'm not interested in using an "off the shelf" PWM controller, I'm just thinking of driving a SSR from an oscillator to pulse the DC so it will work on an unmodified AC water heater, where the thermostats will regulate the water temperature.
            2. This will use the thermostats already inside the water heater.
            3. But it DID overpower the water heater - it heated the water above the thermostat temperatures, causing the thermostat contacts to open, resulting in an arc that melted the contacts together. I was surprised at the tiny distance the contacts opened for switching 240VAC, no wonder DC arced across the contacts.

            I was heating a 40 gallon water heater with two thermostats, controlling two heating elements with 240VAC. I used 4 solar panels, each with 24V @ 9.5A = 230, for a total of 920 watts. I used this setup as it roughly matched the impedance of one heating element (when operating normally, it powers only one element at a time). It heated slower than 240VAC, but over the course of a summer day, it collected more than enough energy to overheat the water.

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #51
              The other alternative is to use a cheap mod-sine inverter, with remote control ON/OFF to power your heater elements.

              Much safer than trying to kludge a Pulsed DC (all those OFF periods, are going to cut your heating capacity by 50%) to use a crappy AC thermostat contact.
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • Tgriff
                Junior Member
                • Jan 2019
                • 12

                #52
                I considered using such an inverter, but the impedance wouldn't match. The other consideration is that I'd like to utilize as much solar power as possible - meaning that when the sun is not shining perpendicular to the solar panels, the power will drop off and the inverter will quit working, even though partial power is available. If the panels are connected directly, all of the DC power would be sent to the water.

                Most water heaters are designed to heat a tank of water in roughly 30 minutes and to keep it hot all day long. My goal is to heat one tank of water in one day, as I won't use more than 40 gallons of hot water in a day. Most water heaters are well insulated and the water will stay hot even if not continually heated.

                I'm driving it with 4 of the 230 Watt solar panels, or 920 watts or 96 VDC @ 9.5 A.

                Each of the two elements in the water heater runs at around 5500 watts @ 240V. The heating element is basically a big resistor and impedance can be found like so:

                P = V * I
                V = I * R, therefore P = I^2 * R
                or: R = P / i^2
                In my case: I = 5500 / 240 v or 22.9 A and R = 5500 / 22.9^2 or 10.5 ohms

                There's not enough power to drive it with a 240V inverter, as it demands 5500 watts

                At 120V, it would still demand more power than available:

                P = I * V or P or P = V^2 / R or P = 120^2 / 10.5 = 1371 Watts (more than my 920 Watt array at max power output)

                It may work if I added another panel and would work better if I buffered the power with batteries and a charge controller, but then we're talking about lots more $$$.

                Comment

                • PNPmacnab
                  Solar Fanatic
                  • Nov 2016
                  • 424

                  #53
                  You shouldn't need to put more than 500W into a heating element with solar and 960W of panels is a very good match for that element. With that impedance difference you would always have sufficient dead time for an arc quench. I think you have come to the wrong place for any creative thinking on water heating with PV.

                  Comment

                  • J.P.M.
                    Solar Fanatic
                    • Aug 2013
                    • 14920

                    #54
                    Originally posted by Tgriff
                    I considered using such an inverter, but the impedance wouldn't match. The other consideration is that I'd like to utilize as much solar power as possible - meaning that when the sun is not shining perpendicular to the solar panels, the power will drop off and the inverter will quit working, even though partial power is available. If the panels are connected directly, all of the DC power would be sent to the water.

                    Most water heaters are designed to heat a tank of water in roughly 30 minutes and to keep it hot all day long. My goal is to heat one tank of water in one day, as I won't use more than 40 gallons of hot water in a day. Most water heaters are well insulated and the water will stay hot even if not continually heated.

                    I'm driving it with 4 of the 230 Watt solar panels, or 920 watts or 96 VDC @ 9.5 A.

                    Each of the two elements in the water heater runs at around 5500 watts @ 240V. The heating element is basically a big resistor and impedance can be found like so:

                    P = V * I
                    V = I * R, therefore P = I^2 * R
                    or: R = P / i^2
                    In my case: I = 5500 / 240 v or 22.9 A and R = 5500 / 22.9^2 or 10.5 ohms

                    There's not enough power to drive it with a 240V inverter, as it demands 5500 watts

                    At 120V, it would still demand more power than available:

                    P = I * V or P or P = V^2 / R or P = 120^2 / 10.5 = 1371 Watts (more than my 920 Watt array at max power output)

                    It may work if I added another panel and would work better if I buffered the power with batteries and a charge controller, but then we're talking about lots more $$$.
                    Keeping the goal of heating water in mind, some comments FWIW:

                    1.) Make sure your heating elements are 5,500 W. Some/many residential units, in the U.S. anyway, are 4,500 W.

                    2.) Initial heating of 40 gal. of H2O + the tank thermal mass by 60 F. will take ~ 6 kWh of energy.

                    3.) Assuming a pretty standard tank with current insulation standards, and a 60 F. delta T., tank water temp. - to amb. temp. at the tank, I'd plan on the best (lowest) 24 hr. thermal loss from the tank to be something like ~ 1.2-1.4 kWh/day, and probably more unless the piping is designed to stop gravity induced fluid migration dead in its tracks. That translates to roughly 0.5 F./hr. temp. loss, again assuming the tank to amb. temp. diff. is ~ 60 F.

                    So, meeting that ~ 7.3 kWh/day = 2,665 kWh/yr. load. How much of that might be supplied by what you're planning is something like, as a maximum, whatever your PV array puts out annually multiplied by (1- impedance consideration %), less whatever other uses the PV output goes for.

                    4) I'd assume you'll still be using a fair amount of POCO power to supply most of the Hot water load.

                    5.) On a somewhat separate comment you made, I've got a solar thermal flat plate system on my roof. There are no roof penetrations for piping. Solar thermal for DW heating is still more efficient by ~ 2X than PV alone, but about as efficient as a PV/HPWH combination. Still, the solar thermal police won't nab you if you manage to forego roof penetrations.

                    I'd respectfully suggest you not believe everything you see or read or hear, particularly the technical equivalent of jackass videos as seen on the new idiots' bible (utube).

                    Comment

                    • psablo
                      Junior Member
                      • Jan 2019
                      • 8

                      #55
                      Great discussion whether it'll work or not.

                      Tgriff - I appreciate your efforts at solving this because I am a solar installer and have access to as many PV panels as I want for free, but not batteries, inverters, etc.
                      I am not trying to heat water, but would like to heat my pump control house just enough so the pipes don't freeze. The pump house is well insulated and the pressure tank and pipes are within a second insulated space so I shouldn't need much wattage but it can get to -20F where I live.
                      There are plenty of 12VDC heaters (and some 24VDC) for automotive available, as well as this:
                      OEM Heaters carries standard 12 Volt heat cable and 12 Volt electric heating elements. We can also build custom 12 Volt heaters to fit your application needs.

                      But, I am concerned with arc-fusing as well since I would like to go direct from PV through cheap charge controller to resistive load. No thermostat, just a manual switch to disconnect in summer, and only heat when the sun's out (lots of sun here).

                      I couldn't find any other post discussing this so it's probably not done often (if ever).

                      PS, I used similar SSR's to build my rapid shut down relay box for my off-grid PV system and they lasted long enough to pass inspection but failed within a year.

                      Comment

                      • bcroe
                        Solar Fanatic
                        • Jan 2012
                        • 5198

                        #56
                        The efficient design will manage to feed the heaters without inverters. I see the first challenge as matching
                        the impedance of the heater to keeping the panels somewhere near MPPT. If there is plenty of sun keeping
                        the panel output current fairly constant, it may avoid an MPPT device. That leaves some series/parallel
                        combination of panels to match up to varied series/parallel heating elements. I doubt anything in the 12V
                        realm would be practical.

                        As for the control contact arc problem, there are devices to handle the switching, to be controlled by
                        the contact(s). We had some pretty hefty relays in phone offices, and now we have cheap FETs that
                        may easily be paralleled for this sort of thing, I have used 20. Inductive spikes may kill them if no
                        protection is used. Keep in mind, the panels can be shut down by shorting the output, maybe just
                        while a fragile switch is operated. Bruce Roe

                        Comment

                        • Tgriff
                          Junior Member
                          • Jan 2019
                          • 12

                          #57
                          Originally posted by J.P.M.

                          Keeping the goal of heating water in mind, some comments FWIW:

                          1.) Make sure your heating elements are 5,500 W. Some/many residential units, in the U.S. anyway, are 4,500 W.

                          2.) Initial heating of 40 gal. of H2O + the tank thermal mass by 60 F. will take ~ 6 kWh of energy.

                          3.) Assuming a pretty standard tank with current insulation standards, and a 60 F. delta T., tank water temp. - to amb. temp. at the tank, I'd plan on the best (lowest) 24 hr. thermal loss from the tank to be something like ~ 1.2-1.4 kWh/day, and probably more unless the piping is designed to stop gravity induced fluid migration dead in its tracks. That translates to roughly 0.5 F./hr. temp. loss, again assuming the tank to amb. temp. diff. is ~ 60 F.

                          So, meeting that ~ 7.3 kWh/day = 2,665 kWh/yr. load. How much of that might be supplied by what you're planning is something like, as a maximum, whatever your PV array puts out annually multiplied by (1- impedance consideration %), less whatever other uses the PV output goes for.

                          4) I'd assume you'll still be using a fair amount of POCO power to supply most of the Hot water load.

                          5.) On a somewhat separate comment you made, I've got a solar thermal flat plate system on my roof. There are no roof penetrations for piping. Solar thermal for DW heating is still more efficient by ~ 2X than PV alone, but about as efficient as a PV/HPWH combination. Still, the solar thermal police won't nab you if you manage to forego roof penetrations.

                          I'd respectfully suggest you not believe everything you see or read or hear, particularly the technical equivalent of jackass videos as seen on the new idiots' bible (utube).
                          1. It has two elements: the upper is 3800 W and lower 5500 W, with a max of 5500 W (wired so only one element on at a time)

                          2 & 3. I didn't log water temperature or electrical performance for the few weeks I was testing it. I was just glad to have hot water at night and again in the morning - and it did that much well.

                          4. Actually, I used it for weeks without connecting the water heater to POCO - and it always had hot water for me (until the SSRs overheated). This whole discussion has me more interested in resuming where I took off ...

                          5. I know the reliability of using a PV solar system, but have read of problems with pumps & leaks in other systems. Does anybody here have personal experience living with one?

                          Also: I'll have to put in a plug for my YouTube video on a solar irrigation system: Solar Irrigation

                          Comment

                          • J.P.M.
                            Solar Fanatic
                            • Aug 2013
                            • 14920

                            #58
                            Originally posted by Tgriff
                            I know the reliability of using a PV solar system, but have read of problems with pumps & leaks in other systems. Does anybody here have personal experience living with one?
                            If you are referring to solar thermal flat plate DHW systems, yea - me. Designed my own and hired the installation by a licensed plumber. One leaky O ring on a flexible connector in 9 yrs. continuous operation. Lots of operational data. Annual solar DHW fraction ~ >0.95. Cost was $3,200 before tax credit. A nice toy that's probably paid for itself as well as a real learning/confirming tool. Most solar thermal systems don't do as well with respect to performance or reliability mostly due to neglect by owners. As a toy, mine gets a lot of attention.

                            Comment

                            • jflorey2
                              Solar Fanatic
                              • Aug 2015
                              • 2331

                              #59
                              Originally posted by bcroe
                              The efficient design will manage to feed the heaters without inverters. I see the first challenge as matching
                              the impedance of the heater to keeping the panels somewhere near MPPT.
                              At least two companies I know of offer MPPT trackers for this purpose. (DC out to heating element) One of them also provides batteryless 120VAC for emergency use.

                              Comment

                              • bcroe
                                Solar Fanatic
                                • Jan 2012
                                • 5198

                                #60
                                Originally posted by jflorey2
                                At least two companies I know of offer MPPT trackers for this purpose. (DC out
                                to heating element) One of them also provides batteryless 120VAC for emergency use.
                                If an MPPT control is to be used, it could also handle the job of turning power on and off. Bruce Roe

                                Comment