    Failure solved

    Thanks Bruce for the advice. The problem didn't however turn out to be the breaker. The problem was that the installer (a year and 9 months ago) didn't fully tighten down the AC line connection inside the inverter. The AC terminal on the circuit board in the inverter had a high resistance connection to the AC grid line and burned up. The inverter now needs to be replaced. The repair tech said he had seen this happen several times.

    Comment

    • bcroe
      Solar Fanatic
      • Jan 2012
      • 5213

      #17
      Originally posted by k1rod
      Thanks Bruce for the advice. The problem didn't however turn out to be the breaker. The problem was that the installer (a year and 9 months ago) didn't fully tighten down the AC line connection inside the inverter. The AC terminal on the circuit board in the inverter had a high resistance connection to the AC grid line and burned up. The inverter now needs to be replaced. The repair tech said he had seen this happen several times.
      I think that could happen at any high current terminal. I've gotten into tightening them
      periodically. Also I might run a check near the end of peak power on a long sunny day.
      All wires are checked for excessive heat, esp close to terminals. A thermal non contact
      meter gets used too. There is enough AC current to warm 4 gauge; but it had better not
      be excessive. Perhaps the thermal cycles tend to work loose the connections. Bruce Roe

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15164

        #18
        Originally posted by bcroe
        I think that could happen at any high current terminal. I've gotten into tightening them
        periodically. Also I might run a check near the end of peak power on a long sunny day.
        All wires are checked for excessive heat, esp close to terminals. A thermal non contact
        meter gets used too. There is enough AC current to warm 4 gauge; but it had better not
        be excessive. Perhaps the thermal cycles tend to work loose the connections. Bruce Roe
        One of the best tools I have ever used for electrical PM work is the Infrared camera. It will spot a problem way before a loose connection burns up the wire.

        Comment

        • ronbot
          Junior Member
          • May 2015
          • 1

          #19
          Originally posted by k1rod
          Thanks Bruce for the advice. The problem didn't however turn out to be the breaker. The problem was that the installer (a year and 9 months ago) didn't fully tighten down the AC line connection inside the inverter. The AC terminal on the circuit board in the inverter had a high resistance connection to the AC grid line and burned up. The inverter now needs to be replaced. The repair tech said he had seen this happen several times.