    So, I'm totally new to the solar world, and am currently renting a place that runs off of solar electricity that is grid-tied. It has a Fronius IG Plus inverter that is mounted on the North side of the house, but also on a side that gets a lot of sunlight daily as this property has virtually no shade what so ever.

    So the problem that I am encountering is that every single day since June, the inverter reads "State 207" at around 1:30pm, which I looked up, and I understand indicates that the solar system is not connected to the grid any longer. I called solar city regarding this, and they told me to go check the breaker panel and reset the "Photovoltaic backfeed" breaker. (Which has become a daily routine at this point, in the afternoons) I guess my question is, could this be an issue with the inverter overheating, since its getting direct sunlight all day long, and its been in the 90-100s since early June. (Unusual for Colorado....but it is what it is) Or does anyone else have a sneaky suspicion as to what could be causing this breaker to trip every day, and disconnecting the solar system from the grid?

    Thanks!

    LR

  • #2
    What is the inverter size or model and what is the make and amperage of the circuit breaker that is tripping?
    NABCEP certified Technical Sales Professional

    [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

    [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

    [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

    Comment


    • #3
      Originally posted by Naptown View Post
      What is the inverter size or model and what is the make and amperage of the circuit breaker that is tripping?

      The inverter is a Fronius IG Plus 7.5-1, there was some info that was written on the left hand side from solar city that read

      VOC 444 v
      Vmp 354 v
      Isc 25.7 A
      Imp 2.4 A

      The breaker that keeps tripping is a Square D, type tipo, 10kA, 240 (Amperage?).

      I am no electrical genius so if there is info here that needs clarification let me know and I'll try to clarify as best I can.

      thanks again

      LR

      Comment


      • #4
        Originally posted by LRob View Post
        The inverter is a Fronius IG Plus 7.5-1, there was some info that was written on the left hand side from solar city that read

        VOC 444 v
        Vmp 354 v
        Isc 25.7 A
        Imp 2.4 A

        The breaker that keeps tripping is a Square D, type tipo, 10kA, 240 (Amperage?).

        I am no electrical genius so if there is info here that needs clarification let me know and I'll try to clarify as best I can.

        thanks again

        LR
        What is the number molded into the trip and reset handle?
        It will need to be higher than 30 as that inverter at peak production can put out over 30A
        NABCEP certified Technical Sales Professional

        [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

        [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

        [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

        Comment


        • #5
          Originally posted by Naptown View Post
          What is the number molded into the trip and reset handle?
          It will need to be higher than 30 as that inverter at peak production can put out over 30A
          The trip and reset handle reads "40" and its written in two places (which i thought meant 240?, but maybe I understood it incorrectly)

          Comment


          • #6
            Give the folks at Fronius a call. I have had good luck with them. Have you serial number in hand.

            I expect that it may be a low or high grid voltage issue, I have a friend that had a similiar issue where the utility was allowing the voltage to go out of range. The strange part is that usually a code like that will normally cause the inverter to shut off until the grid is stable, wait five minutes and then go back on line. From your description it sounds like once it shuts down, it stays down until you reset it. If this is the case it sounds like the inverter software is buggy.

            Comment


            • #7
              If it is the breaker in the panel box for the house it may also be a bad breaker that is tripping as things hit peak power.
              call Solar City and schedule a service call or just leave it off they will come running when they see it off for a few days.
              NABCEP certified Technical Sales Professional

              [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

              [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

              [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

              Comment


              • #8
                Sorry, I misunderstood. if the breaker handle is in the off position prior to you doing anything, then I agree its probably a breaker issue. If on the other hand they have you turn it off and then back on again, its probably the inverter.

                Comment


                • #9
                  Originally posted by Naptown View Post
                  If it is the breaker in the panel box for the house it may also be a bad breaker that is tripping as things hit peak power.
                  call Solar City and schedule a service call or just leave it off they will come running when they see it off for a few days.
                  LOL - honestly solar city has been largely unaware of the issue for some reason. The only way we figured this out in the first place was that I logged into the monitoring system and found that there was an error message in the monitoring system that dated back to june 9th. Solar city had done absolutely nothing as far as contacting us went to let us know that there was a problem. Since then there have been a few days here and there that I haven't been home, and the system has popped off the grid for a couple days and again no notification from solar city.


                  thanks for all the help though to everyone who has chimed in.

                  Comment


                  • #10
                    When you have to reset the breaker is the handle in the center position and you have to turn it all the way off then back on again?
                    And this breaker is not in the inverter there aren't any in the inverter.
                    NABCEP certified Technical Sales Professional

                    [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                    [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                    [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                    Comment


                    • #11
                      Originally posted by Naptown View Post
                      When you have to reset the breaker is the handle in the center position and you have to turn it all the way off then back on again?
                      And this breaker is not in the inverter there aren't any in the inverter.
                      This breaker is not in the inverter, it is in the main breaker panel. Yes I do have to pull it all of the way off, and then all the way back "on." I think that I am starting to think that maybe it really just is the breaker itself and not the inverter at all.

                      do you think its possible that the inverter is just pumping out way more electricity than the breaker can handle?

                      LR

                      Comment


                      • #12
                        In theory no it is below the rated capacity of the breaker.
                        this is not to say that the breaker is not defective.
                        Have an electrician replace the breaker and all should be good.
                        NABCEP certified Technical Sales Professional

                        [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                        [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                        [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                        Comment


                        • #13
                          Originally posted by LRob View Post
                          This breaker is not in the inverter, it is in the main breaker panel. Yes I do have to pull it all of the way off, and then all the way back "on." I think that I am starting to think that maybe it really just is the breaker itself and not the inverter at all.

                          do you think its possible that the inverter is just pumping out way more electricity than the breaker can handle?

                          LR


                          Faulty breaker, pretty sure of it..........haven't read the other replies but it could also be an issue where the electric panel should have been upgraded and now the box gets overloaded at times.

                          Comment


                          • #14
                            Does anybody know what the resolution was?

                            I have the same issue with my Fronius IG Plus 7.5K. I have a persistent State 207 error. If I recycle the power to the inverter (with the knob at the bottom of the inverter), it begins the initialization sequence but about 5 seconds into it, goes back to State 207. I don't think the problem has anything to do with the breaker, the AC disconnects or the grid power itself. I measured the AC voltage right at the AC disconnect sitting next to the inverter and the phase to phase voltage was 248. I measured the frequency with an oscilloscope and a high voltage diff probe and the frequency is dead on at 60 Hz. So I believe the problem is in the inverter itself. Does anybody have any experience with this particular failure? Thanks.
                            Last edited by k1rod; 11-03-2014, 12:44 PM. Reason: spelling

                            Comment


                            • #15
                              Originally posted by k1rod View Post
                              I have the same issue with my Fronius IG Plus 7.5K. I have a persistent State 207 error. If I recycle the power to the inverter (with the knob at the bottom of the inverter), it begins the initialization sequence but about 5 seconds into it, goes back to State 207. I don't think the problem has anything to do with the breaker, the AC disconnects or the grid power itself. I measured the AC voltage right at the AC disconnect sitting next to the inverter and the phase to phase voltage was 248. I measured the frequency with an oscilloscope and a high voltage diff probe and the frequency is dead on at 60 Hz. So I believe the problem is in the inverter itself. Does anybody have any experience with this particular failure? Thanks.
                              I have a pair of those inverters. Running at capacity all day, one of them eventually took out
                              its 40A breaker. Code 207 means "no grid voltage detected", could be a breaker fault. I would
                              at least TRY a different circuit breaker to see if it makes any difference. Bruce Roe