Are you using the Envoy to communicate with them? It looks like you can set the grid profile, and can select / verify that the 208 V settings are correct.
page 41.
If that is all set up right, I would strongly encourage you to measure line voltage when as many of the inverters are operating as possible. If voltage has moved significantly from what it was with zero inverters, your grid connection may not like being unbalanced and/or may not be able to accept the power you are trying to feed.
page 41.
If that is all set up right, I would strongly encourage you to measure line voltage when as many of the inverters are operating as possible. If voltage has moved significantly from what it was with zero inverters, your grid connection may not like being unbalanced and/or may not be able to accept the power you are trying to feed.