I see; in any case it doesn't affect busbar rating.
I think the Code tried to prevent the case when someone puts load breaker with rating exceeding main breaker and possibly melting busbar at the point of contact as both sources could possibly be working into this single 'sink'. The Code could prevent this with simple clause 'no breaker rating should exceed busbar rating' but it doesn't seem to be the case.
If we model busbar with load breakers as split into individual mini-bars all connecting to the main breaker it becomes clear that PV source on the other end can take some of those mini-bars out of original group and as it is closer to the loads those mini bars can be made shorter decreasing total amount of heat produced. Too bad this most common case didn't make into the Code.
I think the Code tried to prevent the case when someone puts load breaker with rating exceeding main breaker and possibly melting busbar at the point of contact as both sources could possibly be working into this single 'sink'. The Code could prevent this with simple clause 'no breaker rating should exceed busbar rating' but it doesn't seem to be the case.
If we model busbar with load breakers as split into individual mini-bars all connecting to the main breaker it becomes clear that PV source on the other end can take some of those mini-bars out of original group and as it is closer to the loads those mini bars can be made shorter decreasing total amount of heat produced. Too bad this most common case didn't make into the Code.