Sunking, I'm open to any recommendations you can give me to correct the misinterpretations I have made or make necessary repairs to above ground components. I'm new to this - and I know that you have spent a lifetime in these fields so I really would appreciate any knowledge transfer.. Below ground, I simply can't see any way I can get to that deep ring without massive work. I tried to follow 780 and LPI 175 as best as I understood what was in the specs - so any knowledge you can give me would be most appreciated. I have the printed 2014 versions.
For my entire solar project I used the printed version of NEC 2014 (and online 2011 since CA was still on 2011), and printed versions of NFPA 780 and LPI 175 and LPI 177 (I found LPI 177 to be a repeat of 175 with no new information). I tried at every step to follow and meet or exceed what I found in those specs. Any mistakes are mine. I also found very little on-line information about real world application of NFPA 780 in relationship to solar other than the references in the 780 spec. As one of the co-authors I am hoping that you have references that can really help everyone out understanding this subject more.
I can't find anything about class B conductors - I don't know what they are. Table 4.1.1.1.1 is class 1 ( <= 75' high structures) and table 4.1.1.12 is class 2 (> 75' high structures).
4.13.1.4 says that bolting, brazing, welding, or high compression connectors listed for purpose.... The ones I used are bolting and they are listed for class 2 (most of Robbins components are class 2). I could not find any elaboration on this section in Appendix A nor in LPI 175 on a best practice so I used the listed ones that Robbinslightning had.
LPI 175.135 says that concrete encased electrodes cannot have more than 2" of concrete around them and must be at least 20 ft long. With the Iron Ridge system, each pipe is in the middle of a 2' hole filled with concrete and for my engineering at least 3'-4" of pipe is in the hole (I have about 3'-8" in each hole). 780.4.13.3.1 contradicts this saying encased in at least 2" of concrete but both say at least 20' long. My guess is the LPI 175.135 is a typo given that 780 matches what NEC 250.52(A)(3) says. In either case I could not see how my 3-1/2' of pipe in concrete could be a considered a valid concrete encased electrode being so short. Even if one added up the four I have per mount that is still under 20' but I was under the impression it was a continuous 20' - not sections.
inetdog you are correct I used the wrong term - its has been a lifetime ago I took AC classes when I was first going for EE but then switched to computer science and never looked back. I will correct the document. Thanks!
For my entire solar project I used the printed version of NEC 2014 (and online 2011 since CA was still on 2011), and printed versions of NFPA 780 and LPI 175 and LPI 177 (I found LPI 177 to be a repeat of 175 with no new information). I tried at every step to follow and meet or exceed what I found in those specs. Any mistakes are mine. I also found very little on-line information about real world application of NFPA 780 in relationship to solar other than the references in the 780 spec. As one of the co-authors I am hoping that you have references that can really help everyone out understanding this subject more.
I can't find anything about class B conductors - I don't know what they are. Table 4.1.1.1.1 is class 1 ( <= 75' high structures) and table 4.1.1.12 is class 2 (> 75' high structures).
4.13.1.4 says that bolting, brazing, welding, or high compression connectors listed for purpose.... The ones I used are bolting and they are listed for class 2 (most of Robbins components are class 2). I could not find any elaboration on this section in Appendix A nor in LPI 175 on a best practice so I used the listed ones that Robbinslightning had.
LPI 175.135 says that concrete encased electrodes cannot have more than 2" of concrete around them and must be at least 20 ft long. With the Iron Ridge system, each pipe is in the middle of a 2' hole filled with concrete and for my engineering at least 3'-4" of pipe is in the hole (I have about 3'-8" in each hole). 780.4.13.3.1 contradicts this saying encased in at least 2" of concrete but both say at least 20' long. My guess is the LPI 175.135 is a typo given that 780 matches what NEC 250.52(A)(3) says. In either case I could not see how my 3-1/2' of pipe in concrete could be a considered a valid concrete encased electrode being so short. Even if one added up the four I have per mount that is still under 20' but I was under the impression it was a continuous 20' - not sections.
inetdog you are correct I used the wrong term - its has been a lifetime ago I took AC classes when I was first going for EE but then switched to computer science and never looked back. I will correct the document. Thanks!