    solar panel with 14V with 28cell

    HI, I am Chok here from malaysia. I have recently order some solarpanel range from 100wp to 10wp with 28cell which will produce 14Vmp. I would like to have some ideal either this panel can charge a solar gel battery with capacity 10ah to 100ah ?

    The ideal is because of the weather in malaysia is always hot through out the year, so the battery doesn't required much voltage to charge during the cold weather. And also i am trying not to use MPPT charge controller as mosst of the MPPT charge controller starting doing the job when the voltage up about 15V, can someone correct me!

    Thank you!
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    Hope you are planning on charging 8 volt batteries.
    MSEE, PE

    Comment

    • ckchok
      Junior Member
      • Jan 2011
      • 15

      #3
      Originally posted by Sunking
      Hope you are planning on charging 8 volt batteries.
      Oh No! Mr.Sunking... could you explain this more to me!!!! i can't even can charge the battery to a certain percentage ??

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        A 12V battery, needs about 16V (applied to the battery, from the charge controller) to completely charge. With losses in the controller, you need at least18V from the solar panel, and that is subject to "droop" in hot weather, so many panels are made for 19-21V for 12V battery applications.

        Less than fully charging the battery, will quickly ruin it from Sulfation.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #5
          Mike explained it, you need 36 cells.
          MSEE, PE

          Comment

          • ckchok
            Junior Member
            • Jan 2011
            • 15

            #6
            Originally posted by Mike90250
            A 12V battery, needs about 16V (applied to the battery, from the charge controller) to completely charge. With losses in the controller, you need at least18V from the solar panel, and that is subject to "droop" in hot weather, so many panels are made for 19-21V for 12V battery applications.

            Less than fully charging the battery, will quickly ruin it from Sulfation.
            Thank you very much Mr.Mike.

            Comment

            • ckchok
              Junior Member
              • Jan 2011
              • 15

              #7
              Originally posted by Sunking
              Mike explained it, you need 36 cells.
              Mr.Sunking, thanks for your help!!

              Comment

              • ckchok
                Junior Member
                • Jan 2011
                • 15

                #8
                Originally posted by ckchok
                Mr.Sunking, thanks for your help!!


                As for Battery.. which type of battery is generally working well in a hot country. SLA AGM or Gel type?

                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #9
                  Originally posted by ckchok
                  As for Battery.. which type of battery is generally working well in a hot country. SLA AGM or Gel type?
                  I would go with FLA
                  MSEE, PE

                  Comment

                  • ckchok
                    Junior Member
                    • Jan 2011
                    • 15

                    #10
                    Solar Panel Grounding

                    Originally posted by Sunking
                    I would go with FLA


                    Dear,

                    My simple solar system is as below :

                    1. Solar PV Panel +/- to Charge controller (PV +/-)
                    2. Charge Controller (Batt +/-) to Battery bank (12V)
                    3. Battery to DC12v Car Player and DC/AC Inverter (12V/AC240V - 500W modified sine wave).
                    4. The Inverter load is mainly AC 240V 18w Energy Saving Light

                    The circuit is tested and running well but when i touch the battery terminal or the casing for car player and inverter, i found that the electric shock is strong, it seems like AC current flowing around my system

                    I would like to know , it is i need to ground the system. If yes, how do i ground it ? from battery terminal or the inverter casing ?

                    Thank you!
                    Attached Files

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #11
                      With mod sine inverters, you cannot ground them, as they generate 55 (or 110) VAC from either side of the battery potential . There should be an instruction sheet with your inverter that may say if you can ground the - battery terminal. But generally they have no transformer, and are subject to shocks when something in the system is damaged. Bummer.
                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • ckchok
                        Junior Member
                        • Jan 2011
                        • 15

                        #12
                        Originally posted by Mike90250
                        With mod sine inverters, you cannot ground them, as they generate 55 (or 110) VAC from either side of the battery potential . There should be an instruction sheet with your inverter that may say if you can ground the - battery terminal. But generally they have no transformer, and are subject to shocks when something in the system is damaged. Bummer.
                        Ok Thanks Mr.Mike,

                        If in this case, i planning to replace the inverter to Pure Sine Wave, once i replace can i just simply ground the body of the inverter ?

                        Comment

                        • Mike90250
                          Moderator
                          • May 2009
                          • 16020

                          #13
                          I know for a fact, that the Morningstar SureSine 300 (600W for 10 min) inverter can be grounded. It needs to be wired to both the battery, and to an outlet, it has no built-in outlet. But it does have a ground terminal, but you won't find it a a local outlet store generally, you will have to order it from a supplier. It's also the best small inverter I've found.

                          Mike
                          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                          solar: http://tinyurl.com/LMR-Solar
                          gen: http://tinyurl.com/LMR-Lister

                          Comment

                          • ckchok
                            Junior Member
                            • Jan 2011
                            • 15

                            #14
                            Originally posted by Mike90250
                            I know for a fact, that the Morningstar SureSine 300 (600W for 10 min) inverter can be grounded. It needs to be wired to both the battery, and to an outlet, it has no built-in outlet. But it does have a ground terminal, but you won't find it a a local outlet store generally, you will have to order it from a supplier. It's also the best small inverter I've found.

                            Mike
                            Tks Mr.Mike,

                            The instruction manual for these modified sine wave didn't tell the grounding issue. So, for the time being, can i ground the system in both the positive and negative leg at the battery, or just positive leg ?

                            Comment

                            • Mike90250
                              Moderator
                              • May 2009
                              • 16020

                              #15
                              No grounding on mod sine inverters

                              if you ground + & - on the battery, you create a dangerous short circuit.

                              Often, the battery - is connected to ground in a car, and a mod sine inverter works there, but there is a good reason the manuals for mod sine inverters don't mention grounding, it will blow something up.

                              But getting shocks is not normal, even with mod sine.
                              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                              solar: http://tinyurl.com/LMR-Solar
                              gen: http://tinyurl.com/LMR-Lister