Rather than believing blanket statements about which will perform better various conditions, it can easily be modeled using PVWatts or SAM. The amount lost to clipping can be estimated and valued at the appropriate cost per kWh. The OP in this case is not in the mid-west, and data from those systems in that location seems odd to bring up.Leave a comment:
-
The daily data we have from the logs shows a much different story.
I have a 10KW Enphase I installed and a 10KW Solar Edge installed. Both have zero shading and perfect south views at the same angle.
In the winter the Solar Edge makes 6 to 8kw a day more due to the panel power being so much higher in the cold and the Enphase flat tops.
In the heat of summer there near even. Down south it don't matter but up in the northern Midwest it matters ever winter day.
If a panel in the cold makes over 300 watts -- it's best to be able to use it.
Watching all these systems on line shows the real picture.Leave a comment:
-
Sometime soon I'll share some comparison charts showing SE reported power vs revenue grade measured power, but I'm working on some other analysis at the moment first. Also, just to get in front of a possible objection... the CT's for my revenue grade meter are actually located inside the inverter, so termination or wire resistance shouldn't really be coming into play.
This is a gross consumption chart... the Tecolote Canyon system is using SE 5 min data (power, not energy), and the -Test system is using the EKM Meter (revenue grade) to report solar generation. Gross Consumption is calculated from generation and net consumption. Net consumption comes from an Eagle device, through Wattvision, and is the same for both systems (as you can see during the hours when the sun is down).
You can see early in the day, both systems show about the same gross consumption, and they maintain the same baseline established when the sun wasn't out. Later in the day, the SE generation has drifted slightly higher, pulling up the calculated gross consumption number to compensate, at a level that is higher than the baseline. The revenue grade system is continuing to maintain the same baseline, as might be expected.
The end result was that SE reported more energy than the revenue grade system.
EKM Meter: 20.85 kWh
SE sum of 5 or 15 min Power, multiplied by time: 21.00 kWh (0.7% above EKM)
SE Energy (from the SE portal): 21.63 kWh (3.0% above SE power, 3.7% above EKM)
I changed the parameters of the test after that day, so scrolling to days forward or backward may be comparing different things.Leave a comment:
-
Sometime soon I'll share some comparison charts showing SE reported power vs revenue grade measured power, but I'm working on some other analysis at the moment first. Also, just to get in front of a possible objection... the CT's for my revenue grade meter are actually located inside the inverter, so termination or wire resistance shouldn't really be coming into play.
Really, SE is taking as much liberty with their numbers as they can, and while other inverters (Enphase, SMA) seem to do this a little bit, I think they tend to stick closer to the truth. It doesn't make SE a bad system... just, if accurate monitoring is your thing, SE gets an F for that.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
Yes, that's what I thought. But I can't explain the difference between the end-of-day production reported by the dashboard, and calculation by summing up all the 15-min wattages and divide by 4. The latter is always smaller by roughly 2-3%. I'm hoping you're right that the dashboard is the actual production, but the number seems a little too good comparing to Enphase (which on paper should have efficiency within 1% from SE).
I've come up with no better explanation than SE is trying to make their system look better than the competition's by publishing high energy numbers, but still within the ±5% spec they need to meet to be compliant with CEC, among others. When I've pushed hard enough on the SE tech that I got passed to an engineer, they did not confirm or deny it, they just say that 5% is their spec and revenue grade monitoring is required if you want better.Leave a comment:
-
Leave a comment:
-
In San Diego (the land of expensive electricity), if you're on EV-TOU2 plan, the cost of clipping is currently @ $0.48/KWh. So it can get a little expensive depending where you're and the rate plan you're in.Leave a comment:
-
Leave a comment:
-
FYI for you and I.
My Question:
I am curious, when I look at my portal, I see stuff such as "Yesterdays Energy: 44.34kWh" is this the DC produced energy from all my panels, or is this the DC->AC energy converted by the inverter? I suspect I am viewing the DC... Is there a way to see both metrics?
SE Response:
5/12/2015 2:59 PM | Tom Simpson
What you see on the dashboard is Export to AC what you see on the module level (layout) is DC/DC. The dashboard only shows actual production which is always in AC never DC. You can only export AC not DC. There are no changing the configuration without your own GUI. See sunpec errata if this is something you are interested inLeave a comment:
-
Leave a comment:
-
To throw one more question into the mix. I originally had my system sized on last year's data of 12,484 and $2,746 based on Edison's 4 tier domestic rate I was on. However, since purchasing my Elec vehicle, I was able to switch to TOU-B and move most of my pool pump operation to night time. Also, my wife and I are both at work during the day so the TOU really works well for us. The end result is that this first month of TOU is shaping up to be about the same kWh as this period last year, but $100 less. If this extrapolate's out, I could be looking at around a $1k savings just by changing plans. With that in mind, should I stick with a 25 panel 7.6kW system? Or should I downsize a bit?Leave a comment:
-
I think it happens to everyone with SE. FYI, yesterday my SE shows 33.58KWh, but PVoutput registered 32.57KWh. The difference seems to be around 3% on a clear day and somewhat less on a cloudy day. A wild guess is maybe the inverter is calculating DC wattage, but reports the actual AC wattage in the API (which PVoutput reads), since SE claims 97% efficiency, hence 3% difference. Someone else also speculated that the 15-min update rate has something to do with it, but the symmetry of the bell curve should have taken care of the lagging effect. So for comparison with other brands, it's probably safer to use the PVoutputs data, or takes SE's data and divide 1.03.
My Question:
I am curious, when I look at my portal, I see stuff such as "Yesterdays Energy: 44.34kWh" is this the DC produced energy from all my panels, or is this the DC->AC energy converted by the inverter? I suspect I am viewing the DC... Is there a way to see both metrics?
SE Response:
5/12/2015 2:59 PM | Tom Simpson
What you see on the dashboard is Export to AC what you see on the module level (layout) is DC/DC. The dashboard only shows actual production which is always in AC never DC. You can only export AC not DC. There are no changing the configuration without your own GUI. See sunpec errata if this is something you are interested inLeave a comment: