Not quite what I said.
I said that he shouldn't be too surprised if what he has is 140A for the main breakers, yet HIS panel only has 125A busbar.
ie. it's quite possible that someone overloaded that main panel sometime in the past. So don't rely on the existing 140A to come to the conclusion that the bus bar is at least that.
(at last I'm assuming those are the main breakers - that there isn't a main breaker of 100A or whatever feeding to those two since he said there's only 2.)
Adding a 2nd breaker (the 40A for the AC) would be something I can easily see an A/C installer doing. Adding it would be no different skills than adding a breaker to any panel without shutting off power to the panel.
Fairly easy for the AHJ to see and catch? yes - they would need to know it's a 100A or 125A service and 125A busbar.
Would they see it and catch it? Maybe. I wouldn't bet on it though - it depends on how thorough the inspector is, how many other inspections he has to do, and whether he thinks to look at that particular item and not just look at where the AC unit is and the fuse box or disconnect that's next to the unit.
Since the OP is looking at adding solar, he needs to be sure what he has - and I'm sure that breaker box will be looked at when inspecting for solar / net-metering. But that just means it has to be fixed right before the solar install is finished - not that it was done right N years ago.
I said that he shouldn't be too surprised if what he has is 140A for the main breakers, yet HIS panel only has 125A busbar.
ie. it's quite possible that someone overloaded that main panel sometime in the past. So don't rely on the existing 140A to come to the conclusion that the bus bar is at least that.
(at last I'm assuming those are the main breakers - that there isn't a main breaker of 100A or whatever feeding to those two since he said there's only 2.)
Since a permit and inspection are required in most locations to benefit from net metering or to add new service, and attempting to DIY a second service breaker is stupid, I would doubt many people would get away with overloading the bus. That is just too easy for the AHJ to catch.
Fairly easy for the AHJ to see and catch? yes - they would need to know it's a 100A or 125A service and 125A busbar.
Would they see it and catch it? Maybe. I wouldn't bet on it though - it depends on how thorough the inspector is, how many other inspections he has to do, and whether he thinks to look at that particular item and not just look at where the AC unit is and the fuse box or disconnect that's next to the unit.
Since the OP is looking at adding solar, he needs to be sure what he has - and I'm sure that breaker box will be looked at when inspecting for solar / net-metering. But that just means it has to be fixed right before the solar install is finished - not that it was done right N years ago.