    #16
    Originally posted by HX_Guy
    Amy, I actually only need 6 total fuses, not 8. I have 3 strings in the system...right now the 4th fuse holder (far right) isn't being utilized.
    The box is a MNPV4-MC4, but it's really a PV6 that's pre-wired with MC4 connectors for 4 strings (same box though).
    Don't forget to also order another finger bus bar to combine the 3 negatives. http://www.midnitesolar.com/productP...Order=13&act=p
    Solar Queen
    altE Store

    Comment

    • HX_Guy
      Solar Fanatic
      • Apr 2014
      • 1002

      #17
      Originally posted by Amy@altE
      Don't forget to also order another finger bus bar to combine the 3 negatives. http://www.midnitesolar.com/productP...Order=13&act=p
      Amy, I was actually going to run wire from each fuse holder to the Negative bus bar, like in my photo/diagram earlier (white lines).
      Do you foresee any issue with doing it that way?

      Only reason is because I feel having the PV+ and PV- finger bus bars so close to each other wouldn't be that good of an idea, would it?
      I mean they would literally be millimeters apart with all the fuse holders on the DIN rail.

      Comment

      • Amy@altE
        Solar Fanatic
        • Nov 2014
        • 1023

        #18
        Oh right, I forgot you said that. That should be fine, but it is common with the PV6 to cut the bus bar in 2 and have the 3 strings each go to a separate circuit. With everything tightened down , there won't be any movement causing them to short.
        Solar Queen
        altE Store

        Comment

        • HX_Guy
          Solar Fanatic
          • Apr 2014
          • 1002

          #19
          I guess I was imagining this massive arc happening between them.



          I may still need to go the route I'm thinking only because the wire running from the combiner to the inverter (white wire with red arrow pointing to it) may already be pulled tight, so it wouldn't reach the bus bar. It would obviously be a cleaner looking install with the bus bar, but as long as it's not a safety issue with running wires like I am thinking, I don't mind...it'll all be covered up anyway.

          Comment

          • Amy@altE
            Solar Fanatic
            • Nov 2014
            • 1023

            #20
            I was wondering if there was enough play in that wire to bring it all the way up. If you are seeing enough voltage to jump the space, you have more problems than we can cover here ; )

            http://www.midnitesolar.com/pdfs/MNPV2-3-4-6_manual.pdf page 4 shows cutting the finger bus bar in 2 to make 2 circuits, that's why they make the lug removable on the bus bar, and have a spot on both ends. They do caution on 1000V systems to make sure the gap is big enough, I think they just added that warning recently, so they are used to it being used up to 600V.
            Solar Queen
            altE Store

            Comment

            • HX_Guy
              Solar Fanatic
              • Apr 2014
              • 1002

              #21
              Originally posted by sensij
              Nice. I was going to suggest heat shrink as a clean looking option, but didn't think you would have it available. I would definitely use that instead of a sharpie.
              I told my installer that I was going to put the heat shrink wrap on the white wire to make it black and he said...

              "It is grounded system. Both ground and equipment grounded.. please don't put anything on it...it is meant to b white. If you put anything on it will have to phase tape it white."

              I think he's a bit confused that this is a grounded inverter.

              Comment

              • bcroe
                Solar Fanatic
                • Jan 2012
                • 5243

                #22
                I have a couple questions. First, if you plug into the MC4s in the back row of that box, how
                will you ever get in there with a tool to release them?

                And then, just what is a "transformerless inverter"? My impression is NOT using a big iron
                core running at 60 HZ, but maybe that's not it at all. Bruce Roe


                "In a transformerless inverter, neither the positive nor negative conductor has a bond to
                ground. The result is that you no longer have a grounded current-carrying conductor. This
                requires both conductors in each circuit to be protected with OCPDs and have disconnecting
                means as required in Art. 690, Part III."

                Comment

                • HX_Guy
                  Solar Fanatic
                  • Apr 2014
                  • 1002

                  #23
                  Originally posted by bcroe
                  I have a couple questions. First, if you plug into the MC4s in the back row of that box, how
                  will you ever get in there with a tool to release them?
                  I haven't tried yet but I'm thinking you'd undo the top plugs first and the you can access the bottom row.

                  And then, just what is a "transformerless inverter"? My impression is NOT using a big iron
                  core running at 60 HZ, but maybe that's not it at all. Bruce Roe


                  "In a transformerless inverter, neither the positive nor negative conductor has a bond to
                  ground. The result is that you no longer have a grounded current-carrying conductor. This
                  requires both conductors in each circuit to be protected with OCPDs and have disconnecting
                  means as required in Art. 690, Part III."
                  Good question, I have no idea really, doing some reading on it now. I don't even understand how the wiring differs between the two...what does it mean neither has a bond to ground? I'm hoping my installer hooked up everything correctly as he seems a bit confused, I don't think he has any experience with transformerless inverters.

                  Here is a good article explaining the differences:

                  An archive of the complete 31-year history of Home Power magazine. 188 digital back issues capture a three decade history of the renewable energy movement in the U.S. and beyond. Each issue is available for non-commercial use at no cost to registered members of this site.


                  So in a transformer based system, the PV- would be attached to the negative bus bar to ground it? The same bus bar as the equipment ground?
                  I'm hoping my installer didn't do this, and I don't think he did as I don't think the system would be operating.

                  Comment

                  • inetdog
                    Super Moderator
                    • May 2012
                    • 9909

                    #24
                    Originally posted by HX_Guy
                    I haven't tried yet but I'm thinking you'd undo the top plugs first and the you can access the bottom row.



                    Good question, I have no idea really, doing some reading on it now. I don't even understand how the wiring differs between the two...what does it mean neither has a bond to ground? I'm hoping my installer hooked up everything correctly as he seems a bit confused, I don't think he has any experience with transformerless inverters.
                    The transformerless inverter basically uses the PV array to pump up an AC output voltage in the + direction relative to the neutral, with the - of the array temporarily referenced to ground internally and then uses that same panel with the + now referenced to ground instead to pump up a negative voltage to drive the AC line negative with respect to neutral. (For an inverter with only a 240V AC output it is a little more complicated than that, but the principle is the same.

                    if the installer actually bonds the negative to the ground at any point in his wiring, then the inverter will not work, and will actually blow a fuse or trip an internal breaker to indicate the fault.
                    If the installer does not bond the negative to ground (or to either the AC EGC or AC neutral) then during the operation of the inverter the + and - leads will both change voltage with respect to ground, although of course the difference between them will stay constant at the panel Vmp voltage.
                    To deliver AC out a transformerless inverter which has a buck regulator design must get a DC voltage from the panel which is greater than the peak to peak AC output voltage (for a 240V output). For 240V AC that comes to about 350V DC.

                    It sounds like your installer is clinging to his rote learned rules of the past, for grounded arrays, and is not even reading the instructions for the SMA TL model inverter that he is installing. I am not sure at this point how you can best prevent him from doing more damage in a misguided quest to follow his "plan".
                    SunnyBoy 3000 US, 18 BP Solar 175B panels.

                    Comment

                    • HX_Guy
                      Solar Fanatic
                      • Apr 2014
                      • 1002

                      #25
                      Integdog: So is there a chance he wired it wrong? Or since it's working it's wired properly?

                      Is there anything specifically that I can check for in the wiring to make sure it was wired correctly? I assume the only points he could have done wrong wiring is in the combiner box or in the DC disconnect?

                      Comment

                      • sensij
                        Solar Fanatic
                        • Sep 2014
                        • 5074

                        #26
                        Originally posted by HX_Guy
                        Integdog: So is there a chance he wired it wrong? Or since it's working it's wired properly?

                        Is there anything specifically that I can check for in the wiring to make sure it was wired correctly? I assume the only points he could have done wrong wiring is in the combiner box or in the DC disconnect?
                        Based on the pictures you've shared, the wiring is ok. The only major thing he could have done wrong (besides using white wire) would have been to connect Dc- to ground. He probably thought he was doing that when he ran the bare ground from the inverter to the electrode, which is why I asked about it earlier. However, all he did was create a somewhat lower impedance path to ground for the EGC. The fact you've generated some power proves this. The solaredge inverter has gfci protection that would have tripped if either dc line was actually grounded.
                        CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                        Comment

                        • Amy@altE
                          Solar Fanatic
                          • Nov 2014
                          • 1023

                          #27
                          Have him RTFM

                          If the installer read the manual, he would have seen that while the metal equipment needs to be grounded with an Equipment Grounding Conductor (EGC), the DC negative is not grounded with a Grounding Electrode Conductor (GEC). That is usually done internal to the inverter through the GFP, so he probably didn't manually do it as well. AS such, both the positive and negative DC lines are current carrying conductors, and therefore the negative is NOT a grounded conductor, and should not be White.

                          http://www.solaredge.us/files/pdfs/p...-manual-na.pdf Page 7, "The supplied Safety Switch meets all requirements for a code-compliant installation of this
                          ungrounded system. The DC section disconnects both the positive and negative conductors. " Page 8, "The inverter input and output circuits are isolated from the enclosure. This system does not include
                          an isolation transformer and should be installed with an ungrounded PV array in accordance with the requirements of NEC Articles 690.35 and 690.43 National Electric Code, ANSI/NFPA 70, 2011 (and Canadian Electrical Code, Part I, for installations in Canada). "
                          Solar Queen
                          altE Store

                          Comment

                          • HX_Guy
                            Solar Fanatic
                            • Apr 2014
                            • 1002

                            #28
                            Thank you to both of you for all the help.

                            I almost wonder if he thought the green wire going from the ground bus bar to the left side in the disconnect by the DC connections was grounding one of the DC conductors? All that does though is ground the DIN rail.

                            As long as that's the only difference between a "grounded" and "ungrounded" install then it sounds like its ok. Wasn't sure if there are differences in how the panels/rails/wiring on the roof are installed.

                            Also, the bare copper wire coming out of the disconnect and going to the existing grounding electrode is not yet connected on the other end. He said that has to be done by the electric company using a irreversible compression type connector? (permit states the same).
                            The main breaker also has not been derated yet, he said the same thing for that, that the electric company has to do that.

                            Comment

                            • Amy@altE
                              Solar Fanatic
                              • Nov 2014
                              • 1023

                              #29
                              Right, the green wire in the picture is the Equipment Grounding Conductor, grounding the metal pieces, not the conductors.

                              Not sure what you mean about derating the main breaker. Do you have a 200A main breaker box? If so, the sum of the Main breaker and the inverter breaker cannot add up to more than 240A (NEC705.12(D)). That is why most residential systems are up to 7.6kW. If you have a 11.4kW inverter, you should have a 60A breaker for it in the Main, which means if you have a 200A breaker box, one way around it is to reduce the 200A breaker to 180A or less. The more common, and expensive thing to do is swap out the 200A breaker box for a 400A box. Is that what you are saying the electric company is doing? I haven't followed all of your posts (as interesting as they are), so I missed that piece of the system.
                              Solar Queen
                              altE Store

                              Comment

                              • HX_Guy
                                Solar Fanatic
                                • Apr 2014
                                • 1002

                                #30
                                Originally posted by Amy@altE
                                Right, the green wire in the picture is the Equipment Grounding Conductor, grounding the metal pieces, not the conductors.

                                Not sure what you mean about derating the main breaker. Do you have a 200A main breaker box? If so, the sum of the Main breaker and the inverter breaker cannot add up to more than 240A (NEC705.12(D)). That is why most residential systems are up to 7.6kW. If you have a 11.4kW inverter, you should have a 60A breaker for it in the Main, which means if you have a 200A breaker box, one way around it is to reduce the 200A breaker to 180A or less. The more common, and expensive thing to do is swap out the 200A breaker box for a 400A box. Is that what you are saying the electric company is doing? I haven't followed all of your posts (as interesting as they are), so I missed that piece of the system.
                                Amy, your first method was correct, the 200A panel is going to be derated to 175A since the solar is using a 60A breaker.
                                A separate permit was required for this, which we got, but again the installer said that is something that APS (our power company) need to come out and do because the power from the street to the main service panel needs to be shut off to do it.