    Originally posted by Mike90250
    Your panels need to be able to charge and EQ your batteries. That means your PV amps, after the charge controller, need to be about 5-10% of your battery amp capacity.


    Your Array of 2506w will only produce 2,000 W under normal conditions, and with a MPPT converter to battery charging volts of 14.5V, yields 140A. So you could go up to a battery bank of 1400AH.
    2000 watts / 14.5 volts = 138 amps which would be 5.2 % of my battery bank amps. Is just getting by good enough? And Is 14.5 volts the lowest an MPPT charge controller will convert higher volts down to for higher amps?

    If 5.2% is too close for comfort I could afford adding maybe another 3 or 4 hundred more watts of panels.

    2900 watts x 80% = 2320 watts / 14.5 volts = 160 amps.
    That would be 6.05 % of battery bank amps. If 5.2% isn't good enough maybe 6.05%?

    Originally posted by Mike90250
    The 20% discharge overnight, means that after 3 days no sun, you will be about 60% discharged, and while that's past the 50% point, it's occasional, and not regular.
    I calculated for 2 days of no sun because that's really all I need. If needed I have a serious back generator, it's 35 years old but in mint condition, I'm not afraid to fire it up if I have to in order to avoid more than 30 % discharge.

    So what do you think. Is that doable? I can always add more panels later when i can afford it.

    Again thanks so much for your experiential advice.

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #17
      14.5V is a charging voltage for deep cyle batteries. As the batteries charge, the amps will slowly taper off, till the voltage steps up to increase the charge. The float charge is a lower voltage, and supplies little power into the battery.

      Here's some links about Battery Equalization. If you don't have enough amps, you cannot get the eq process to begin working,


      Progressive DynamicsI produces a full line of Electrical products for the RV, marine and specialty industries. No matter the product, at PDI you receive superior quality and customer service. Our product’s are designed,assembled, tested, warranted and serviced in the U.S.A.

      Xantrex power products provide reliable power safely and efficiently, perfect for RVs, marine environments, commercial vehicles & more.


      hope this helps
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • cindynsg
        Member
        • Jan 2010
        • 53

        #18
        Thanks Mike, I appreciate it. I'm looking at the links now.

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #19
          Originally posted by cindynsg
          2000 watts / 14.5 volts = 138 amps .
          Does not work like that. Use the nominal battery voltage of 12 volts. 2000/12 = 167 amps.
          MSEE, PE

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #20
            Originally posted by Sunking
            Does not work like that. Use the nominal battery voltage of 12 volts. 2000/12 = 167 amps.
            I've got to disagree - a 12V battery is charged by a higher voltage, generally 14.5V. Sure, if a battery's' been drained to near death, the charging voltage will be lower, but an even finer point here is, there are no 150+ Amp MPPT chargers, the largest are 80A that I know of. 60A is a common limit for a charger.

            This is a reason many larger systems use 24 or 48V, at 12v, the currents are so large, they become impractical to deal with.

            Mike
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • cindynsg
              Member
              • Jan 2010
              • 53

              #21
              thanks mike that is a relief. just so you know, I would never doubt you.

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #22
                The actual charge rate is determined by your location. A C/10 is a good rule of thumb, but may not be enough in some locations, and overkill in others.

                Here is a good example. Let
                MSEE, PE

                Comment

                • cindynsg
                  Member
                  • Jan 2010
                  • 53

                  #23
                  You do have a solar system right? Tell me what you've got. How long have you had it? How long has your battery bank lasted? What is your calculated D.o.D? How much experience do you have with solar? Pictures?

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #24
                    Originally posted by cindynsg
                    You do have a solar system right?
                    Wrong wouldn't have one where I live. Electricity is cheap, no Net Metering laws, and no incentives.
                    Originally posted by cindynsg
                    Tell me what you've got.
                    I own my own architectural/engineering design firm. PE licensure, and 31 years of electrical generation, transmission, distribution, and battery plant behind me.
                    Originally posted by cindynsg
                    How long have you had it?
                    Think I covered that already
                    Originally posted by cindynsg
                    How long has your battery bank lasted?
                    Well I assume you mean ones used for cycle service like those used in RE applications right? Of the 156 stand alone projects I have designed built never seen a set last more than 5 years before they loose 30% of their capacity.
                    Originally posted by cindynsg
                    What is your calculated D.o.D?
                    Depends on the client and application. In the telcom sector at remote cell tower sites where power outages cannot be tolerated 10% DOD with back-up generators. Otherwise 20% is the default design.
                    Originally posted by cindynsg
                    How much experience do you have with solar?
                    Roughly about 6 years designing and building them mostly for telephone companies, and a few commercial projects like Walmart. Just finished up a design for a new Walmart in Plano TX with a 500 KW grid tied system.
                    MSEE, PE

                    Comment

                    • Sunking
                      Solar Fanatic
                      • Feb 2010
                      • 23301

                      #25
                      Originally posted by Mike90250
                      I've got to disagree - a 12V battery is charged by a higher voltage, generally 14.5V. Sure, if a battery's' been drained to near death, the charging voltage will be lower, but an even finer point here is, there are no 150+ Amp MPPT chargers, the largest are 80A that I know of. 60A is a common limit for a charger.
                      Well I was not referring to the charge cycle. If you are calculating for the charge amps from a standard 12 volt panel using shunt controllers you use the Vmp voltage from the panels which is usually 17 or 18 volts.

                      For MPPT the charge voltage does not approach 14.5 volts until the very end of the charge cycle after the current tapers off to a C.03 rate. For charge voltage 13 to 13.8 is default number used

                      Originally posted by Mike90250
                      This is a reason many larger systems use 24 or 48V, at 12v, the currents are so large, they become impractical to deal with.
                      I agree. But you would be surprized how many DIY's try it cascading controller outputs to get the high amperage.
                      MSEE, PE

                      Comment

                      • Jason
                        Administrator
                        • Dec 2008
                        • 990

                        #26
                        Sunking is a very reputable guy in this industry and we are fortunate to have him here contributing to this board. Let's not run him off!

                        Comment

                        • cindynsg
                          Member
                          • Jan 2010
                          • 53

                          #27
                          Ok, Just couldn't figure out what MSEE or PE stands for. You seem to know what your doing, just wondering what expierience. no harm no fowl meant. Just wondering.

                          Comment

                          • Sunking
                            Solar Fanatic
                            • Feb 2010
                            • 23301

                            #28
                            Originally posted by Jason
                            Sunking is a very reputable guy in this industry and we are fortunate to have him here contributing to this board. Let's not run him off!
                            You can't run me off, my skin is thick
                            MSEE, PE

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #29
                              Originally posted by cindynsg
                              Just couldn't figure out what MSEE or PE stands for. You seem to know what your doing, just wondering what expierience. no harm no fowl meant. Just wondering.
                              No problem, you did not offend me
                              MSEE = Master of Science in Electrical Engineering. A graduate college degree.
                              PE = Professional Engineer.
                              MSEE, PE

                              Comment

                              • cindynsg
                                Member
                                • Jan 2010
                                • 53

                                #30
                                Originally posted by Sunking
                                .

                                So as you can see location means everything in terms of charge rate and more importantly system cost. The rule of thumb (C/10) here would have either fallen way short or way too much overkill.
                                You think C/10 is no good for me? My winter insolation rate is 2 - 3 minimum but is 3 - 4 average . I'm going for 2 days no sun maximum. If need be I've got a serious NO kidding generator if I get below 70% charged.