thanks!, my scenario is power outage for a year or something, i also have generator and fuel source that would last "awhile", also i have the emergency outlet on this inverter, i think the max is 2kw output, but was curious how to "trick" the inverter to think it was still grid tieComment
-
Yes you can with any decent pure sine inverter but you need a system that can handle the max watts from all grid tied inverters in your system and you will need to manage excess PV production when your battery is full. For long term outage, it's essentially an off-grid scenario and since you already have a hybrid inverter it's likely more practical to use your inverter in off-grid mode with batteries and generator to charge the batteries when there is not enough PV production.Comment
-
Nothing illegal for sure, i am talking if it is an apocolyspe scenario, so yes , it is essentially making a grid tie system into an off grid system was my question...is it cheaper to just purchase an off grid inverter and swap it and add batteries than to try to trick the existing inverter?Comment
-
Nothing illegal for sure, i am talking if it is an apocolyspe scenario, so yes , it is essentially making a grid tie system into an off grid system was my question...is it cheaper to just purchase an off grid inverter and swap it and add batteries than to try to trick the existing inverter?Comment
-
Don't see anything illegal. It's all done while disconnected from grid. grid tied inverters work just fine with full power provided you have appropriate equipment for an island grid. Just look at Tesla Powerwall when it's disconnected from the utility grid.Comment
-
Nothing illegal for sure, i am talking if it is an apocolyspe scenario, so yes , it is essentially making a grid tie system into an off grid system was my question...is it cheaper to just purchase an off grid inverter and swap it and add batteries than to try to trick the existing inverter?Comment
-
Just remember, when faking a Grid with a small inverter, if you solar array is producing 4,000 watts and you are only consuming 2,000 watts, something is going to happen.
Whatever happens, be sure you understand how your small inverter will respond if it suddenly sees 2000 watts coming into it. Will it shut off ? Will it try to frequency shift to control the larger inverter ? Will the larger inverter respond appropriately ? Will all the magic smoke inside be released ?Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Completely disconnecting from the grid and having your solar charge a battery or power a small load through a special power connection is ok. As you say having the proper equipment to be an island grid is the way to go in the first place.Comment
-
Just remember, when faking a Grid with a small inverter, if you solar array is producing 4,000 watts and you are only consuming 2,000 watts, something is going to happen.
Whatever happens, be sure you understand how your small inverter will respond if it suddenly sees 2000 watts coming into it. Will it shut off ? Will it try to frequency shift to control the larger inverter ? Will the larger inverter respond appropriately ? Will all the magic smoke inside be released ?Comment
-
Otherwise uninformed readers could think this is simple when indeed it is complicated. The word fake is also misleading because what a hybrid inverter does is emulate the grid but replaces the infinite load that the grid presents with the controls that the hybrid uses to vary the output of the GT inverter according to the loads on the system.
To answer your subsequent question using a proper hybrid inverter wired correctly is how it has been done and is currently being done. The most current UL spec is UL 1741 SA.Last edited by Ampster; 03-04-2021, 11:26 AM.9 kW solar, 42kWh LFP storage. EV owner since 2012Comment
-
[QUOTE=Ampster;n423806]
You are defining what a hybrid inverter does when it AC couples to a GT inverter. So the word "decent" should be changed to hybrid and furher clarified by saying UL compliant..
Otherwise uninformed readers could think this is simple when indeed it is complicated. The word fake is also misleading because what a hybrid inverter does is emulate the grid but replaces the infinite load that the grid presents with the controls that the hybrid uses to vary the output of the GT inverter according to the loads on the system.
To answer your subsequent question using a proper hybrid inverter wired correctly is how it has been done and is currently being done. The most current UL spec is UL 1741 SA.[/QUO
so lets say i decide to do another array, i dont want the upkeep of batteries etc, but want to have full power when the sun is shining and it be GT...what i need is to purchase a hybrid inverter, and in the event of loss of grid , i could get both arrays to function?Comment
-
.......
so lets say i decide to do another array, i dont want the upkeep of batteries etc, but want to have full power when the sun is shining and it be GT...what i need is to purchase a hybrid inverter, and in the event of loss of grid , i could get both arrays to function?Last edited by Ampster; 03-04-2021, 12:20 PM.9 kW solar, 42kWh LFP storage. EV owner since 2012Comment
-
You are defining what a hybrid inverter does when it AC couples to a GT inverter. So the word "decent" should be changed to hybrid and furher clarified by saying UL compliant..
Otherwise uninformed readers could think this is simple when indeed it is complicated. The word fake is also misleading because what a hybrid inverter does is emulate the grid but replaces the infinite load that the grid presents with the controls that the hybrid uses to vary the output of the GT inverter according to the loads on the system.
To answer your subsequent question using a proper hybrid inverter wired correctly is how it has been done and is currently being done. The most current UL spec is UL 1741 SA.Comment
-
[QUOTE=mudhole;n423807]You are defining what a hybrid inverter does when it AC couples to a GT inverter. So the word "decent" should be changed to hybrid and furher clarified by saying UL compliant..
Otherwise uninformed readers could think this is simple when indeed it is complicated. The word fake is also misleading because what a hybrid inverter does is emulate the grid but replaces the infinite load that the grid presents with the controls that the hybrid uses to vary the output of the GT inverter according to the loads on the system.
To answer your subsequent question using a proper hybrid inverter wired correctly is how it has been done and is currently being done. The most current UL spec is UL 1741 SA.[/QUO
so lets say i decide to do another array, i dont want the upkeep of batteries etc, but want to have full power when the sun is shining and it be GT...what i need is to purchase a hybrid inverter, and in the event of loss of grid , i could get both arrays to function?Comment