Grid tied solar system.
Collapse
X
-
-
The model linked does not support split phase operation. The fact that the output connection is only 3 wire (two hots + ground) as opposed to 4 wire (2 hots + neutral + ground) is a good clue.CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment
-
Here is the data sheet showing "Hardwired Connections"
Schneider Electric Global. As a global specialist in energy management, automation and digitalization in more than 100 countries, we offer integrated energy technology solutions across multiple market segments.
I'll admit to not understanding the data sheet they show a circled ground on the input and a bare ground on the output. The difference in ground I don't know but apparently N is neutral and something else.Attached FilesComment
-
As Beroe mentioned earlier an Autotransformer is required generally for load balancing. You just have to pay extra.Attached FilesComment
-
You can indeed use a single ended 120V GTI on a grid connected split phase 120/240 system because the utility grid will provide all of the current on the other hot wire. With a UPS, even a grid interactive UPS, the output goes only to the loads and the utility grid cannot provide the neutral and L2 current needed.Is this not a diagram of a split phase system or is it something else?
http://www.samlexamerica.com/support...chCircuits.pdfSunnyBoy 3000 US, 18 BP Solar 175B panels.Comment