    Grid tied solar system.

    I have read most peoples opinions on battery back up systems. I understand the cost factor of not getting your money back. I want solar for the independence not money savings. With that being said. I'm looking at installing a 7kw to 8kw system on my house. The location I'm mounting is straight south with zero shade all day. That will provide 80 to 100% of power year around. I want a battery backup that would provide power for critical loads only. 1 freezer, 1 fridge, living room lights and maybe a couple fans. Trying to figure out usage for that stuff now. I live in tornado alley and as a kid seen power go out for over a month. When it hits a town the grid is down for a while. So is there a way to run a hybrid inverter without battery's until needed. The idea being I can go get battery's after disaster. I don't think this is possible but making sure. Or can I trick a regular inverter with solar DC signal to think the POCO has power (with a cut off from POCO of course) Or is there something I can add after the fact to a another inverter that can make if capable of battery back up? Or should I go with smaller system and do battery back up now. Have about 20k to spend for now (me doing most of install). Would just want a system that can be upgraded easy. Such as just adding more panels and battery's. Don't want to change out major components later. I'm here to learn please teach me!
  • solarix
    Super Moderator
    • Apr 2015
    • 1415

    #2
    There are no inverters that you can just add batteries to when the time comes. If they need batteries then, they need batteries now.
    You could go with a hybrid type inverter (SMA Island, Schneider XW, Outback Radian) which only needs a relatively small battery as it operates in grid-tie mode until an outage occurs.
    Since you are looking at a sizable array, how about 2 (or more) SMA TL inverters that during an outage can change modes with the flick of a switch and generate a limited (1500w each when the sun is shining) amount of power without any batteries at all! A couple of these would run your basic critical needs during the day, keep the fridges cold, charge cell phones, etc.
    Plus, could add on the SMA island system later (warning - they are not cheap) to give you real off-grid strength and works with the TL inverter to keep it running as an "island" in a sea of your neighbors that are SOL in an outage.
    BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

    Comment

    • ButchDeal
      Solar Fanatic
      • Apr 2014
      • 3802

      #3
      Originally posted by North Texas
      So is there a way to run a hybrid inverter without battery's until needed. The idea being I can go get battery's after disaster. I don't think this is possible but making sure.
      Or can I trick a regular inverter with solar DC signal to think the POCO has power (with a cut off from POCO of course) Or is there something I can add after the fact to a another inverter that can make if capable of battery back up? Or should I go with smaller system and do battery back up now. Have about 20k to spend for now (me doing most of install). Would just want a system that can be upgraded easy. Such as just adding more panels and battery's. Don't want to change out major components later. I'm here to learn please teach me!
      No to the first. Hybrid systems need batteries to operate though they just keep them topped off till the grid is down.
      On the second sort of, you can get a full hybrid system and us that AC couple a grid tie system but it would need batteries and costs would be even higher.

      Solar is not generally easy to upgrade and particularly hybrid / off grid systems are not easy to upgrade.

      An OutBack Flexpower 2 would make a perfect fit for you with an 8kw system.
      OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Zero out your bill with a grid tie system

        Spend your battery money on a generator

        If winds take out your local wires, the debris will take out your solar panels (glass, outside, in the wind) and your batteries are flat and you will need to run the generator anyway. Work up a safe fuel storage scheme, there are many ways.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • North Texas
          Junior Member
          • Feb 2015
          • 20

          #5
          Originally posted by solarix
          You could go with a hybrid type inverter (SMA Island, Schneider XW, Outback Radian) which only needs a relatively small battery as it operates in grid-tie mode until an outage occurs.
          So i could do this without getting a full battery system ( just one or two batteries?) and add batteries later? Would lack of a full battery bank kill that battery quick?

          Originally posted by solarix
          Since you are looking at a sizable array, how about 2 (or more) SMA TL inverters that during an outage can change modes with the flick of a switch and generate a limited (1500w each when the sun is shining) amount of power without any batteries at all! A couple of these would run your basic critical needs during the day, keep the fridges cold, charge cell phones, etc.
          This may be the way to go! I dont care for much power, mainly just for food. I'm not good with math in electricity, does my numbers add up? I thought all grid tied solar systems became usless in a power outage? Is this capable only cause of the inverters?


          Originally posted by solarix
          Plus, could add on the SMA island system later (warning - they are not cheap) to give you real off-grid strength and works with the TL inverter to keep it running as an "island" in a sea of your neighbors that are SOL in an outage.
          That is pricey as an add on. May as well do a full battery backup instead of this.

          Comment

          • North Texas
            Junior Member
            • Feb 2015
            • 20

            #6
            Originally posted by Mike90250
            Zero out your bill with a grid tie system
            Plan to as close as I can without going to far over. My POCO net meters but doesn't pay anything for extra electricity.

            Originally posted by Mike90250
            Spend your battery money on a generator
            I already have a small generator that can do what i need. Would just plug them directly into that generator.

            Originally posted by Mike90250
            If winds take out your local wires, the debris will take out your solar panels (glass, outside, in the wind) and your batteries are flat and you will need to run the generator anyway. Work up a safe fuel storage scheme, there are many ways.
            I agree this is a concern. I live on a little bit of land so there would be a little less flying debris but is very likely I loose panels. And if I go with one inverter rather than micro inverters, If I loose one panel in the series, I loose all power from that series? My thinking with having a generator and another source of power is, 3 is 2, 2 is 1, 1 is none.

            Comment

            • North Texas
              Junior Member
              • Feb 2015
              • 20

              #7
              Originally posted by ButchDeal
              On the second sort of, you can get a full hybrid system and us that AC couple a grid tie system but it would need batteries and costs would be even higher.
              So this would be just a grid tied battery system?



              Originally posted by ButchDeal
              An OutBack Flexpower 2 would make a perfect fit for you with an 8kw system.
              For grid tied only? Or for for grid tied battery back up?

              Comment

              • North Texas
                Junior Member
                • Feb 2015
                • 20

                #8
                Usage

                Found usage on frig and freezer. Total for both is 89.5 kwh per month, 2.98 kwh per day. Published numbers, am in the middle of measuring with a kill a watt.

                Comment

                • ButchDeal
                  Solar Fanatic
                  • Apr 2014
                  • 3802

                  #9
                  Originally posted by North Texas
                  For grid tied only? Or for for grid tied battery back up?
                  Outback is Grid tie battery backup
                  OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                  Comment

                  • DanS26
                    Solar Fanatic
                    • Dec 2011
                    • 970

                    #10
                    Originally posted by Mike90250
                    Zero out your bill with a grid tie system

                    Spend your battery money on a generator

                    If winds take out your local wires, the debris will take out your solar panels (glass, outside, in the wind) and your batteries are flat and you will need to run the generator anyway. Work up a safe fuel storage scheme, there are many ways.
                    ++1...this is good advice.

                    Instead of spending money on batteries and all of what that entails, just go out and buy a 500 or 1000 gal propane tank and bury it in close proximity to your propane powered generator. You will save enough money to buy a second backup generator and still have months or more of backup power and much cash in your pocket.

                    After a few years those batteries will be toast as opposed to that LP tank which will probably outlive you.

                    Comment

                    • North Texas
                      Junior Member
                      • Feb 2015
                      • 20

                      #11
                      Will this work?

                      Originally posted by North Texas
                      So i could do this without getting a full battery system ( just one or two batteries?) and add batteries later? Would lack of a full battery bank kill that battery quick?


                      This may be the way to go! I dont care for much power, mainly just for food. I'm not good with math in electricity, does my numbers add up? I thought all grid tied solar systems became usless in a power outage? Is this capable only cause of the inverters?
                      Will the SMA TL inverter thing work for a slow steady output on sunny days without grid? Do I have to have 2? The TL line doesnt seem to start until 7000 Watt. That would be 2 big inverters. Thinking of doing this and propane generator. looking between a 7kwh and and 11 kwh. Have to go up to 11KWH to get 200 amp service I think? What peoples opinions on this?

                      Comment

                      • ButchDeal
                        Solar Fanatic
                        • Apr 2014
                        • 3802

                        #12
                        Originally posted by North Texas
                        Will the SMA TL inverter thing work for a slow steady output on sunny days without grid? Do I have to have 2? The TL line doesnt seem to start until 7000 Watt. That would be 2 big inverters. Thinking of doing this and propane generator. looking between a 7kwh and and 11 kwh. Have to go up to 11KWH to get 200 amp service I think? What peoples opinions on this?
                        it starts at the 3000 up to 7700
                        OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                        Comment

                        • North Texas
                          Junior Member
                          • Feb 2015
                          • 20

                          #13
                          Sma tl

                          Talked to a company that sells the SMA TL inverters and they say that the 1500 watt plug it has wont produce enough for the start power requirements for the fridge or freezer. Any input?

                          Comment

                          • SunEagle
                            Super Moderator
                            • Oct 2012
                            • 15125

                            #14
                            Originally posted by North Texas
                            Talked to a company that sells the SMA TL inverters and they say that the 1500 watt plug it has wont produce enough for the start power requirements for the fridge or freezer. Any input?
                            Unfortunately those SMA inverters while are good quality were only designed to provide some "emergency" power for small critical loads. Refrigerators, freezers and even some window AC systems were not on the list when they sized this system.

                            Comment

                            • inetdog
                              Super Moderator
                              • May 2012
                              • 9909

                              #15
                              Originally posted by North Texas
                              Talked to a company that sells the SMA TL inverters and they say that the 1500 watt plug it has wont produce enough for the start power requirements for the fridge or freezer. Any input?
                              A conventional freezer or refrigerator compressor does have a significant starting surge, and the SMA SPS does not really have surge capability.
                              If you have a soft starting inverter type compressor (not found in standard units) then you might get away with it. But rather than deliver max current and drop the voltage to match the SPS will simply shut down on overload.
                              SunnyBoy 3000 US, 18 BP Solar 175B panels.