Newbie wants to run 24,000 BTU AC

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • peakbagger
    Solar Fanatic
    • Jun 2010
    • 1566

    #16
    I think we need to come up with a home brew ice plant so the PV freezes the water into ice and then cooling come from ice melting

    Comment

    • J.P.M.
      Solar Fanatic
      • Aug 2013
      • 15071

      #17
      Originally posted by peakbagger
      I think we need to come up with a home brew ice plant so the PV freezes the water into ice and then cooling come from ice melting
      Depending on the application and load, that might not be as impractical as it might sound.

      Comment

      • peakbagger
        Solar Fanatic
        • Jun 2010
        • 1566

        #18
        Assuming we work with the latent heat of fusion and ignore sensible heat, its 144 btus per pound of ice so that is 153 pounds of ice to cover one hour of operation of the AC. The volume of the ice is about 57 cubic pounds per cubic foot or 2.68 cubic feet of ice per hour.

        Every time I looked at ICE storage for inlet air cooling on gas turbines, the numbers just would not pencil out. Even on facilities unless the capital cost was offset with grants, they didnt pencil out.

        There was an individual I believe in upper New York State that built an ice chest in the basement surrounded on five sides with water with a very well insulated front door. He installed a coil in the tank run to an outdoor coil filled with refrigerant making sure all the lines were sloped properly.. In the early winter, the freon vapor would rise to the outdoor coil, cool down and condense into liquid and run back down to the basement tank which would gradually freeze solid. The ice storage was sized to last the entire summer. It was in the early days of the internet and I have lost track of the link, it was on a Bild it Solar type site.

        Comment

        • J.P.M.
          Solar Fanatic
          • Aug 2013
          • 15071

          #19
          Originally posted by peakbagger
          Assuming we work with the latent heat of fusion and ignore sensible heat, its 144 btus per pound of ice so that is 153 pounds of ice to cover one hour of operation of the AC. The volume of the ice is about 57 cubic pounds per cubic foot or 2.68 cubic feet of ice per hour.

          Every time I looked at ICE storage for inlet air cooling on gas turbines, the numbers just would not pencil out. Even on facilities unless the capital cost was offset with grants, they didnt pencil out.

          There was an individual I believe in upper New York State that built an ice chest in the basement surrounded on five sides with water with a very well insulated front door. He installed a coil in the tank run to an outdoor coil filled with refrigerant making sure all the lines were sloped properly.. In the early winter, the freon vapor would rise to the outdoor coil, cool down and condense into liquid and run back down to the basement tank which would gradually freeze solid. The ice storage was sized to last the entire summer. It was in the early days of the internet and I have lost track of the link, it was on a Bild it Solar type site.
          I too recall something like that in Mother Earth News from the late '60's - early '70's or so but the past is getting fuzzier as time goes by.

          I piddled around with seasonal storage (but mostly for HVAC heating wet dreams for cold climate applications) and came to the conclusion that it was more hassle, and as a practical matter less likely to work as well as very difficult to accomplish in a cost effective way than other ways of skinning the alternate energy cat.

          If I was looking to cool a space now and wanted to exercise my eccentricity, after I reduced the heat transfer at the boundaries of the conditioned space as much as might be cost effectively possible, and if I had a freezer and a swamp cooler, I'd dump the ice from the freezer into the swamp cooler and let it sublime to vapor and maybe some left over latent heat of evaporation for the remaining melt. Although that melt evaporation probable wouldn't work very effectively in what are probably high dew point Carribean conditions, that will most likely be offset by the idea that the sublimation process of H2O takes place below 0 deg. C under the described conditions.
          Last edited by J.P.M.; 03-19-2024, 11:44 AM.

          Comment

          • J.P.M.
            Solar Fanatic
            • Aug 2013
            • 15071

            #20
            Originally posted by jovenac
            Your plan is underpowered for what you’re trying to do. A 24,000 BTU split usually averages around 1.2 to 2 kW while running, so over six hours you’re realistically looking at 7 to 10 kWh of consumption, not 6 kWh. Your battery sounds large at 1,800 Ah, but at 12 volts and with real usable depth of discharge plus inverter losses, you’re closer to about 10 to 11 kWh usable, which leaves very little margin for daily cycling. The 3 kW inverter is also likely undersized because these units can have higher peak demands, so a 5 kW class inverter would be safer. With only 1.2 kW of solar, you will not reliably replenish what the AC uses each day, so the system may run the load but will steadily drain the battery and struggle to sustain that schedule long term.
            You are responding to an almost 3 year old post.

            Comment

            • sdold
              Moderator
              • Jun 2014
              • 1493

              #21
              Originally posted by jovenac
              Your plan is underpowered for what you’re trying to do. A 24,000 BTU split usually averages ...
              Where are you located? Do you have a solar-related business?

              Comment

              • adrianfen45
                Banned
                • Oct 2026
                • 11

                #22
                The 1,800 Ah battery figure at 12 V is what would worry me most. My brother runs a small camp near Baton Rouge with a 12,000 BTU mini-split and a 24 V lithium bank, and even that struggles through our humid afternoons without generator backup. Scaling to 24,000 BTU on 1.2 kW of solar sounds like a losing race daily. <link removed> , but real-world duty cycle in Louisiana heat is hard to model. Has anyone here actually logged daily kWh on a 2-ton split in this climate?

                Moderator note: No ad links please, thanks
                Last edited by sdold; 11-02-2026, 09:17 AM.

                Comment