Fronius IG4000 Sting Inverter - question regarding string configuration

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • JanS48
    Member
    • Sep 2017
    • 33

    #31
    solar pete

    It's great to hear that someone else is a fan of KISS. Just for the hell of it I'm going to ask the electrical inspector in North Smithfield RI if that is a requirement - but being a home owner and them taking a VERY hard line regarding DIY installations I'm almost 100% sure they say yes it's required. Frankly I'm also very sure it's one of the reasons micro inverters seem to be the norm for new solar installations - near me anyways. Thanks so much for the input solar pete.
    Jan

    Comment

    • J.P.M.
      Solar Fanatic
      • Aug 2013
      • 14926

      #32
      Originally posted by solar pete
      Hi All,

      Rapid shut down, what a crock, we never let it in here and they have given up trying as everyone knows its a crock, I believe there is a ground swell starting in the USA to get rid of it, good luck with that peeps, cheers
      While I tend to agree that rapid shutdown is onerous and probably done for some crappy as well as valid reasons so probably has some of the characteristics of a crock, I've not been tasked with climbing on the roof of a burning building with a PV system on it and not knowing if the system was energized before I start climbing on arrays and chopping holes in roofs.

      Do you have any suggestions as to possible workable solutions that wouldn't be a crock ?

      Comment

      • scrambler
        Solar Fanatic
        • Mar 2019
        • 500

        #33
        Originally posted by JanS48
        I spent the last several hours learning about Rapid Shutdown and all the Tigo offerings - By the time I purchase the modules, and RSS transmitters, and an Initiator - which I had trouble finding and the box to house same and the hookup of wiring for the multiple 12v supplies for the RSS transmitters - I'm better off not using the Fronius string inverter and going with an Enphase 8 system that does it all. Am I missing something here? Apparently I can string up to 11 of my 320 watt panels together and get by with #12 wire in conduit, going back to a double 20 amp breaker. I'll research best practices for the Enphase 8 installations a lot more but it's looking like that is the way to go given the complexity and cost of the Rapid Shutdown required in roof stings - what a blow to roof string installations.
        Jan
        Not sure I follow.
        I have Tigos installed on my array (actually the model with optimizer, rapid shutdown and monitoring as I have shade issues).
        I have one small box at the array, one cable going down to the inverter room, and one box there for the web connection.

        One benefit of having the rapid shutdown and monitoring unit only vs the microinverter, is that the electronics is way simpler so way less prone to failure, and any failure of these units would not affect the production...

        So yes there is a small extra cost but you get code compliance and individual panel monitoring while staying closer to the KISS principle

        Comment

        • JanS48
          Member
          • Sep 2017
          • 33

          #34
          @ scrambler - I guess I'm missing something from what I saw on the Tigos installation you had to have an RSS Transmitter for EACH panel in the array and then an initializer which seemed to be difficult to find. If all I had to purchase was the TS4-A-0 modules and one RSS Transmitter that would certainly be a plus and I'd be able to use my Fronius inverter. Can you outline briefly the components of your installation? How many panels, Inverter used, and any other devices that make up the Tigos installation. I'm really struggling to figure out the best solution here.
          Thanks to all for the comments.
          Jan

          Comment

          • scrambler
            Solar Fanatic
            • Mar 2019
            • 500

            #35
            I have one TS4 module per panel (2 strings of 9 panels each), they connect to the panel controller box, then panels are interconnected in two strings using the TS4 leads rather than the Panel controller leads
            Highlight: How to install Tigo Rapid Shutdown MLPE (TS4-A-F and 2F) - YouTube

            Now at the array, I have one box called the TAP (Tigo Access Point) which collects all the TS4 information. One TAP can collect 300 TS4
            The TAP has a cable going down to where the inverter is and connects to the CCA (Cloud Connect Advanced) unit which interface with the Internet.

            Here is the summary install sheet
            64db95d1d8f20bcfea15ed4a_TS4-A CCA TAP QSG 002-00147-00 1.3 20230728 - EN.pdf (website-files.com)

            Comment

            • scrambler
              Solar Fanatic
              • Mar 2019
              • 500

              #36
              My detailed post above is in moderation because I included the link to the Tigo installation manual.

              My configuration is using one TS4 per panel for monitoring and rapid shutdown and optimization.
              If you have monitoring this requires only two additional components.
              A Tigo Access point (TAP) on the roof collecting the info from all the TS4.
              A Tigo Cloud Connect Access (CCA) beside the inverter to connect to the Web, and with a cable going to the TAP.

              If you only have rapid shutdown, as far as I know, you only have one additional component to the TS4s, and it is One RSS transmitter on the Homerun cable from the array.
              But that is probably one per string...
              EDIT: Actually:
              "The transmitter can be configured with one or two cores. Each Core supports up to 10 strings with a maximum of 30 solar panels per string. In summary, each RSS Core handles a maximum of 150A and 300 solar panels (Dual Core 300A and 600 PV panels)."
              Last edited by scrambler; 08-25-2023, 05:19 PM.

              Comment

              • oregon_phil
                Solar Fanatic
                • Jan 2019
                • 497

                #37
                A summary of my string inverter system built to NEC 2017.

                I have an SMA 7.7 -40 with three strings on the same roof plane.

                28 solar panels
                28 Tigo TS4R-O optimizers
                1 Tigo Access Point (TAP) on the roof
                1 Tigo Cloud Connect Advanced (CCA) next to the string inverter
                1 120 vac to 12 VDC transformer to power the CCA.

                My installation uses 600 Volt rated ethernet cable between the TAP and CCA since it is less than 100 ft. See TIGO document "TAP/GATEWAY Communication Cable Types and Installation". The ethernet cable is strung with the DC wires inside of EMT coming down from the roof to the inverter.



                Comment

                • JanS48
                  Member
                  • Sep 2017
                  • 33

                  #38
                  @ scrambler and oregon_phil
                  Thanks so much for the input. This puts things into a different perspective for me. To start with I'm only doing a single string of 10 panels. In looking at pricing on e-bay I'm thinking of the TS4-A-O modules which I can get for approx $ 46. each and I see a TAP and CCA package for approx 240. So for under 1k I'd be good to go?
                  A question regarding the ethernet cable - I can easily run a std ethernet cable from the TAP through the attic and thru the house back to the CCA - do you know if that will be sufficient ?

                  Wiring question: I was planning on having a combiner box on the roof and then using 10 GA THHN wire back to the inverter. My Fronius has DC disconnects built in so I'm thinking that is all that's needed, however I see some installations where they have a DC disconnect in the combiner box - I could put that in the attic if I needed to. My run from the panels to the Fronius will be approx 140 ft.

                  Grounding question: I'm using a std UniRac mounting system with support "L" brackets on ever other rafter (16" on center) the panels with be in two rows of 5 in Portrait orientation, I see some installations where they use #6 bare stranded connected to each array segment and others that use a solid #10 wire (green). It's typically not 'kosha' to run bare wire in metal EMT how did you all handle grounding ?

                  EMT question - should that always be metal or is it ok to use plastic electrical 'grey' PVC on exterior runs?
                  Thanks
                  Jan

                  Comment

                  • oregon_phil
                    Solar Fanatic
                    • Jan 2019
                    • 497

                    #39
                    Originally posted by JanS48
                    @ scrambler and oregon_phil
                    Thanks so much for the input. This puts things into a different perspective for me. To start with I'm only doing a single string of 10 panels. In looking at pricing on e-bay I'm thinking of the TS4-A-O modules which I can get for approx $ 46. each and I see a TAP and CCA package for approx 240. So for under 1k I'd be good to go?
                    A question regarding the ethernet cable - I can easily run a std ethernet cable from the TAP through the attic and thru the house back to the CCA - do you know if that will be sufficient ?

                    Wiring question: I was planning on having a combiner box on the roof and then using 10 GA THHN wire back to the inverter. My Fronius has DC disconnects built in so I'm thinking that is all that's needed, however I see some installations where they have a DC disconnect in the combiner box - I could put that in the attic if I needed to. My run from the panels to the Fronius will be approx 140 ft.

                    Grounding question: I'm using a std UniRac mounting system with support "L" brackets on ever other rafter (16" on center) the panels with be in two rows of 5 in Portrait orientation, I see some installations where they use #6 bare stranded connected to each array segment and others that use a solid #10 wire (green). It's typically not 'kosha' to run bare wire in metal EMT how did you all handle grounding ?

                    EMT question - should that always be metal or is it ok to use plastic electrical 'grey' PVC on exterior runs?
                    Thanks
                    Jan
                    I'm not an electrician nor an installer. I don't specifically know your local codes either so take any advice as potential solutions from me.

                    Regarding Tigo TS4-A-O, TAP and CCA: That should get your going. Just for your information, when you install them, you must assume the TIGO TS4-A-O's are ON for safety's sake. From the factory they are ON until they connect to the TAP and CCA. After that, the TS4-A-O's go on and off with the 12 volt power. just make sure the 12 volt power goes off when the AC shutoff for the inverter is turned off.

                    That means you could be dealing with 10 x open circuit voltage in the sun. That's why Bruce said he works in the dark. I know installers don't work in the dark. For sure installers have certain insulating practices and orders of connect and disconnect to make sure they don't kill themselves.

                    Roof wiring: You have one string so I don't know why you need a combiner box. My installation using one string as an example, 1 string of 10 panels; Panel 1 factory male MC4 connector, mated to Field terminated female MC4 on 10 ga PV wire red, Red PV wire to SolaDeck terminal block RED, RED SolaDeck terminal block to RED 10 ga THHN to EMT to inverter. Panel 10 factory made Female MC4 connector, mated to Field terminated Male MC4 on 10 ga PV wire Black, Black PV wire to SolaDeck terminal block Black, Black Soladeck Terminal block to Black 10 ga THHN to EMT to inverter. Assume cable glands for cable pass throughs on the soladeck. Flexible metal conduit may be an option for you. check various blogs, forums and your local inspector.

                    I don't have a separate DC shutoff besides what's on the inverter.

                    I don't know about grounding.



                    Comment

                    • scrambler
                      Solar Fanatic
                      • Mar 2019
                      • 500

                      #40
                      Remember that if you do not have any shading issue, you could just use the TS4-A-S (with TAP and CCA) For monitoring and rapid shutdown only, in case that saves you a bit of money.
                      Also less electronics in the box...

                      As far as I can tell the Cable between the CCA and the TAP is a standard but shielded CAT5

                      My only DC disconnect is at the Inverter.
                      Last edited by scrambler; 08-26-2023, 02:11 PM.

                      Comment

                      • JanS48
                        Member
                        • Sep 2017
                        • 33

                        #41
                        Great information guys, I'll need to look into the SolaDeck terminal blocks - sounds like that's the way to go instead of a combiner box. I'm capable of doing the electrical work but at the same time I'm looking at using an electrician that installs the electrical side of solar systems as a consultant for permitting and best practices.
                        Regarding TS4-A-S vs TS4-A-O - I may opt for the A-S. as shading is not much of an issue.
                        In the next couple of weeks I should have the permit applications done for the racking (Solar permit in RI), and the electrical permit for the Inverter wiring and cabling going to the panels.
                        I'll let you know how it all goes.
                        Jan

                        Comment

                        • scrambler
                          Solar Fanatic
                          • Mar 2019
                          • 500

                          #42
                          Just plan ahead. if you say not much, that implies you do have some, and if it can become more over the years with vegetation growth, plan for that

                          Comment

                          • JanS48
                            Member
                            • Sep 2017
                            • 33

                            #43
                            Yes in looking at the overall cost I'm only looking a about 400 more to go with the TS4-A-O's I've not pulled the trigger yet but that's the way I'm leaning.
                            Thanks
                            Jan

                            Comment

                            • JanS48
                              Member
                              • Sep 2017
                              • 33

                              #44
                              Greetings everyone, I'm finally making progress on my Solar Permit - the big obstacle was the PE stamp required for a Solar Permit in RI for the racking. In RI you need to have the PE stamp before you can even start to install your racking. The PE's visit is scheduled for later this week. The charge for this stamp and document is $ 600.00 - does that seem fair?

                              Panel installation: How close to the top of the roof should the uppermost panel be? Is there an acceptable measurement for this? I was planning on about 16 in.
                              Thanks in advance
                              Jan

                              Comment

                              • J.P.M.
                                Solar Fanatic
                                • Aug 2013
                                • 14926

                                #45
                                Originally posted by JanS48
                                Greetings everyone, I'm finally making progress on my Solar Permit - the big obstacle was the PE stamp required for a Solar Permit in RI for the racking. In RI you need to have the PE stamp before you can even start to install your racking. The PE's visit is scheduled for later this week. The charge for this stamp and document is $ 600.00 - does that seem fair?

                                Panel installation: How close to the top of the roof should the uppermost panel be? Is there an acceptable measurement for this? I was planning on about 16 in.
                                Thanks in advance
                                Jan
                                Fire and/or other codes usually/often handle the roof setback.
                                Also, you may want to consider ease or practical access to the array for inspection, cleaning and snow removal - especially snow removal.

                                If your P.E. is worth more than spit and doing his/her job, they would have considered these things and consulted with you.
                                For $600 they ought to give you your money's worth.