Looking to add some panels to my current set up which is 2 strings of 3 200W panels going into a Tristar 60A MPPT CC.
Morningstar's string calculator suggests the below.
Is there an advantage to maximising voltage? I'm not sure but I feel like I set it up this way to get close to the max voltage I can put into the CC but I don't remember why.
Will the 1600W array at 43.44V be better than the current 1200W at 130V?
What are your thoughts on oversizing into the blue range of wattage? Range for blue is 5-30% higher than max nominal power. Morningstar say this might reduce controller life but there is no risk of damage.
Would it make sense to go up to 2000W?
Screenshot from 2021-07-19 18-35-26.png
Morningstar's string calculator suggests the below.
Is there an advantage to maximising voltage? I'm not sure but I feel like I set it up this way to get close to the max voltage I can put into the CC but I don't remember why.
Will the 1600W array at 43.44V be better than the current 1200W at 130V?
What are your thoughts on oversizing into the blue range of wattage? Range for blue is 5-30% higher than max nominal power. Morningstar say this might reduce controller life but there is no risk of damage.
Would it make sense to go up to 2000W?