CTs on bus bar versus wire
  • dapug
    • Sep 2019
    • 29
    Do CT's work around a bus bar compared to round wire conductors, or would there be some accuracy/calibration issue doing this?
    I am upgrading my meter main (load center combo) as part of my solar install. My new meter doesn't feed with wire, just bus bar (see pic).
    I found this post where others have done this, but I'm curious about the results.
    https://www.solarpaneltalk.com/forum...in-panel/page2
    Also, side note, I am disgusted with the quality of Enphase CT's. Check out my second pic here where the clip snapped despite very carefully prying up to get it to open. Wow these clips are insanely thin, brittle, and worthless. CTs must stay completely closed to work properly, that much is for sure. Pathetic engineering here. I'll have to try and get a couple wraps of tape around it just to keep it shut now.
    I find tape creeps, and that a zip tie may be better. Or glass filament strapping tape.
    • Will792
      • Jan 2019
      • 82
      I was also not impressed by the design of Enphase CT. I used Elfa utility knife to lift the clip.
      it might be problematic that CT directly touches bus bar vs insulated wire that electrically isolates CT and wire.
      • bob-n
        • Aug 2019
        • 572
        You should be fairly accurate with a bus bar.
        Note that current transformers are not ideal elements. They try to put out a current proportional to the input but the characteristics of the iron inside them is non-linear enough to produce as much as 1% or more error from light load to heavy load. As long as you understand that limitation, you'll be fine.
          • 5222
          The size and shape of the conductor through the CT do not matter, or if they might
          touch as long as no electrical path is formed. Yea, they are not as accurate as a
          shunt, but a lot easier to add to the circuit. Bruce Roe
          • foo1bar
            • 1833
            I agree - doesn't matter what shape the conductor is as it goes through the CT- whether it's rectangular, square, round, or many small round conductors. What matters is the current passes through the hole in the CT.
            All the CTs that I've dealt with (which is only a few manufacturers) have a non-conductive solid plastic on them. And that keeps the CT from touching the conductors going through it. So whether there's another layer of insulation (like around a wire) or not (like a bus bar) it doesn't matter. There's already a built in insulator that keeps the bus bar / wire from touching the working part of the CT.
              • 15187
              You should be ok using the CT on a bus bar. The critical area is making sure the CT is correctly oriented. Most have a little arrow or dot which is supposed to be pointing to the "load' side of the panel.
              • dapug
                • Sep 2019
                • 29
                ok, in my case, the buss bar is AFTER all loads, between meter and load panel. So I point the arrows toward the loads still, right? "Direction of flow" would be direction FROM Power company TO my loads, correct?
                • bob-n
                  • Aug 2019
                  • 572
                  Correct.
                  • PVAndy
                    • 230
                    CT's have multiple specifications.
                    The more common ones are:
                    voltage or current output
                    Accuracy class
                    Standard or Extended Range (range over which output is linear)
                    A 200:5 (200A to 5 A output) extended range will typically be used up to 400A
                    Burden -impedance of CT winding, wire and measuring instrument.
                    We typically use extended range, 0.3% accurate CT's with correct burden on commercial & utility revenue grade installations
                    Andy
                      • 15187
                      Correct. Your meter should reflect that set up with a positive kwh usage.
                      • foo1bar
                        • 1833