micro-inverters or optimizers when shading is major issue ?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • nwdiver
    Solar Fanatic
    • Mar 2019
    • 422

    #91
    Originally posted by ButchDeal

    As i said pv modules diodes do not ingage at the slightest effect of a shadow.
    I posted pretty clear evidence they do... and if the small shadow isn't enough to trigger the bypass diodes then it's not enough to effect the other panels... MPP is a curve and there's typically more than one MPP within <1% of each other. If the current drops slightly because of a shadow too small to trigger the bypass diodes then voltage increases and power remains the ~same...

    Where did you show there was no cost difference??? You disputed my numbers but never provided yours. RES isn't the only place -41 inverters are available for ~$1200... The Powerstore and Renvu also offer a 5kW SMA -41 inverter for <$1200. The difference is even bigger if rapid shutdown isn't required.

    screen-shot-2018-07-12-at-11-47-44-am-png.316409.png
    Last edited by nwdiver; 10-16-2019, 07:17 PM.

    Comment

    • RShackleford
      Solar Fanatic
      • Sep 2019
      • 311

      #92
      Originally posted by ButchDeal
      also as we already showed it is not a $60 difference but closer to $20 and even less ( to zero) if OP wants to have secure power and rapid shutdown
      Actually, I'e seen TS4-R-O as low as $40, and never P320 for close to that, so no way it's zero, probably not even $20.


      Comment

      • ButchDeal
        Solar Fanatic
        • Apr 2014
        • 3802

        #93
        Originally posted by RShackleford
        Actually, I'e seen TS4-R-O as low as $40, and never P320 for close to that, so no way it's zero, probably not even $20.
        The discussion is optimizer vs non-optimizer. So it would be zero since the SMA TS4-R-0 is almost exactly the same price as the TS4-R-F, so optimizer vs non-optimizer as well as need for the O if OP wants rapid shutdown and secure power.
        nwdriver is trying to claim optimizer vs non-optimizer but is arguing solaredge vs SMA when SMA has optimizers as well.
        OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

        Comment

        • ButchDeal
          Solar Fanatic
          • Apr 2014
          • 3802

          #94
          Originally posted by nwdiver

          I posted pretty clear evidence they do... and if the small shadow isn't enough to trigger the bypass diodes then it's not enough to effect the other panels... MPP is a curve and there's typically more than one MPP within <1% of each other. If the current drops slightly because of a shadow too small to trigger the bypass diodes then voltage increases and power remains the ~same...

          Where did you show there was no cost difference??? You disputed my numbers but never provided yours. RES isn't the only place -41 inverters are available for ~$1200... The Powerstore and Renvu also offer a 5kW SMA -41 inverter for <$1200.
          Ok follow along. SMA makes optimizers, solaredge is not the only optimizer.
          The O optimizer is required for rapid shutdown and secure power, so zero cost difference.

          if a shadow is small the. Power does NOT remain the same, close maybe but not the same
          OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

          Comment

          • nwdiver
            Solar Fanatic
            • Mar 2019
            • 422

            #95
            Originally posted by ButchDeal

            Ok follow along. SMA makes optimizers, solaredge is not the only optimizer.
            The O optimizer is required for rapid shutdown and secure power, so zero cost difference.

            if a shadow is small the. Power does NOT remain the same, close maybe but not the same
            You don't need to 'O' for rapid shutdown. The F or S also fulfill that requirement.

            Sure... power doesn't remain the 'same' just the ~same... not enough to really even think about. Probably <1%. I have a couple Fronius string systems I've installed that have Voltage and Current monitoring. I'm always amazed at how steady power is with fluctuations in voltage. Voltage goes down a bit but current goes up and power doesn't change much at all.

            Originally posted by ButchDeal

            So it would be zero since the SMA TS4-R-0 is almost exactly the same price as the TS4-R-F
            ??? Where are you shopping??? The F is usually ~half the price of the O.
            Last edited by nwdiver; 10-16-2019, 10:12 PM.

            Comment

            • ButchDeal
              Solar Fanatic
              • Apr 2014
              • 3802

              #96
              Originally posted by nwdiver

              You don't need to 'O' for rapid shutdown. The F or S also fulfill that requirement.

              Sure... power doesn't remain the 'same' just the ~same... not enough to really even think about. Probably <1%.
              I said rapid shutdown AND secure power, which OP is interested in.

              it is funny how you always seem to negate the figures to some made up percentage every time a figure doesnt fit with your theory.

              SMA themselves are making the claim and they sell both optimizers and string systems
              OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

              Comment

              • nwdiver
                Solar Fanatic
                • Mar 2019
                • 422

                #97
                Originally posted by ButchDeal

                I said rapid shutdown AND secure power, which OP is interested in.

                it is funny how you always seem to negate the figures to some made up percentage every time a figure doesnt fit with your theory.

                SMA themselves are making the claim and they sell both optimizers and string systems
                Then the S which isn't much more than the F.

                My sole point with optimization is that if comparing it to string level MPP the only benefit is harvesting energy from shaded panels IF the shade falls across all cell groups. If one cell group is shaded it's ~roughly the same. If that's worth the increased cost... fine. IMO it's almost always more economic to just add more watts instead of squeezing more wh out with optimization. If you're space constrained and REALLY... REALLY want the most kWh you can get ROI be damned... then sure... SE is the way to go.
                Last edited by nwdiver; 10-16-2019, 11:14 PM.

                Comment

                • ButchDeal
                  Solar Fanatic
                  • Apr 2014
                  • 3802

                  #98
                  Originally posted by nwdiver

                  Then the S which isn't much more than the F.

                  My sole point with optimization is that if comparing it to string level MPP the only benefit is harvesting energy from shaded panels IF the shade falls across all cell groups. If one cell group is shaded it's ~roughly the same. If that's worth the increased cost... fine. IMO it's almost always more economic to just add more watts instead of squeezing more wh out with optimization. If you're space constrained and REALLY... REALLY want the most kWh you can get ROI be damned... then sure... SE is the way to go.
                  I think you need the O optimizers to get secure power and they have to be in all the modules.

                  there are other benefits with optimizers as have been pointed out already many times, like monitoring, easy of layout, multiple azimuths, gains from module differences, as well as shadow production improvement.
                  your statements ar just miss leading and dismissive of the differences and constantly making up figures and using "roughly" "almost" etc etc.
                  and you further constantly seem to equate "optimizer" to solardge.

                  and you reliance on bypass diodes is just against industry trends as well as silly. We have seen many modules fail with bypass diode issues there are many many more out here failed that are unnoticed because no one is monitoring or looking.
                  OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                  Comment

                  • RShackleford
                    Solar Fanatic
                    • Sep 2019
                    • 311

                    #99
                    Originally posted by ButchDeal
                    I think you need the O optimizers to get secure power and they have to be in all the modules.
                    That's what I was told on the phone by SMA today.

                    I also think that secure-power and rapid-shutdown cannot co-exist (be on the same system); because rapid-shutdown turns off the TS4-whatever modules when AC power is lost, so there's no DC coming into the inverter.

                    Last edited by RShackleford; 10-17-2019, 12:18 AM.

                    Comment

                    • nwdiver
                      Solar Fanatic
                      • Mar 2019
                      • 422

                      Originally posted by RShackleford
                      That's what I was told on the phone by SMA today.

                      I also think that secure-power and rapid-shutdown cannot co-exist (be on the same system); because rapid-shutdown turns off the TS4-whatever modules when AC power is lost, so there's no DC coming into the inverter.
                      The Rapid Shutdown and SPS issue is confusing. Initially I thought the TS4-Fs would work because it's a simple DC line protocol.

                      Here is the quote from SMA in their press release....

                      'SMA’s proprietary Secure Power Supply function also returns with the new Sunny Boy models. Homeowners can once again access up to 2,000 watts of daytime opportunity power. Secure Power Supply is easily installed, taking only a few minutes, and works with the company’s TS4-R-S and TS4-R-O module-level technologies.'

                      I'd love to know why the Ss and Os work but not the Fs... or if this was an error. Even so... you could run 12v aux power through an E-Stop to provide SPS power with the Fs and still comply with NEC 2017.

                      Originally posted by ButchDeal

                      and you reliance on bypass diodes is just against industry trends as well as silly. We have seen many modules fail with bypass diode issues there are many many more out here failed that are unnoticed because no one is monitoring or looking.
                      When one cell group is shaded in an optimized panel the bypass diode is also triggered. Bypass diodes are relied on in optimized systems too. You can still spot a failed diode with string level MPPT. It's not as easy and may take a few more minutes to find the failure but... once again... not worth the cost.
                      Last edited by nwdiver; 10-17-2019, 12:44 AM.

                      Comment

                      • RShackleford
                        Solar Fanatic
                        • Sep 2019
                        • 311

                        Originally posted by nwdiver
                        Iyou could run 12v aux power through an E-Stop to provide SPS power with the Fs and still comply with NEC 2017.
                        Explain more, please (and what's an "E-stop" ?).

                        Comment

                        • nwdiver
                          Solar Fanatic
                          • Mar 2019
                          • 422

                          Originally posted by RShackleford
                          Explain more, please (and what's an "E-stop" ?).
                          ..... 'E Stop' ....

                          Just has to be labeled for 'Rapid Shutdown'...

                          Comment

                          • ButchDeal
                            Solar Fanatic
                            • Apr 2014
                            • 3802

                            Originally posted by nwdiver
                            When one cell group is shaded in an optimized panel the bypass diode is also triggered. Bypass diodes are relied on in optimized systems too. You can still spot a failed diode with string level MPPT. It's not as easy and may take a few more minutes to find the failure but... once again... not worth the cost.
                            Yes when a whole cell group or most if a cell group are covered, but when one or two cells are partially covered the diode doesn't necessarily activate. Or more likely a cell in ine group, cell or two in another, few cells on a different module, half a cell on another module...

                            in optimizd systems each module is independent and not effecting the MPP of the rest of the string(s). Without optimizers they are effecting the rest of the string(s) by your own words. The difference though is YOUR insistence that it isn't THAT MUCH. And you try to explain how it isnt that much by using best case situations, of full cell group and only one cell group. In real life situations shadows move across and are usually set at an angle hitting multiple cell groups and modules unequally. It is exactly this unequallness that optimizers are helping with.
                            they also tend to repeat every day so the effect of small production differences add up pretty quickly.

                            and yes you can find a failed diode on a system without module level monitoring, but it would be a LOT harder to notice and to find, and would require someone in site testing modules to find. I have noticed and diagnosed, and found failed diodes in optimized systems without setting foot on site, even had replacements shipped under warranty without anyone being in site till the replacements arrive.

                            Here is the best document showing the math (instead of "roughly" or made up percentages as you keep say ) :


                            So for one cell in a string of 10 PV modules you are looking at 96.6% vs 98% with optimizers but this is compounded as more cell groups are affected.
                            and if part of all cell groups in one module then 90% for just blocking diode vs 97% for optimizer... again compounded when multiple modules are affected.

                            but it is clear you do not think any of this is worth the cost. Maybe you make a lot hourly in repairs..
                            Last edited by ButchDeal; 10-17-2019, 08:50 AM.
                            OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                            Comment

                            • bcroe
                              Solar Fanatic
                              • Jan 2012
                              • 5202

                              Originally posted by ButchDeal
                              I have noticed and diagnosed, and found failed diodes in optimized systems
                              without setting foot on site
                              That demonstrates to me a real understanding of the problem.

                              Originally posted by ButchDeal
                              Here is the best document showing the math:
                              solaredge.com/sites/default/files/se_technical_bypass_diode
                              I would say that optimizing PV array output over a wide range of conditions
                              including shading, is a rather complex technical problem. I am not impressed
                              with this explanation. It seems to me to be grossly over simplified, inadequately
                              or poorly explained and justified. I see no curves, pictures of optimizer connections
                              and explanation of their functions, or adequate explanation of inputs to the math shown.
                              Perhaps it is really an attempt to justify the product, not to be carefully scrutinized.
                              Bruce Roe

                              Comment

                              • J.P.M.
                                Solar Fanatic
                                • Aug 2013
                                • 14926

                                Originally posted by bcroe

                                That demonstrates to me a real understanding of the problem.



                                I would say that optimizing PV array output over a wide range of conditions
                                including shading, is a rather complex technical problem. I am not impressed
                                with this explanation. It seems to me to be grossly over simplified, inadequately
                                or poorly explained and justified. I see no curves, pictures of optimizer connections
                                and explanation of their functions, or adequate explanation of inputs to the math shown.
                                Perhaps it is really an attempt to justify the product, not to be carefully scrutinized.
                                Bruce Roe
                                This seems a bit like a duel between titans.

                                Both are experienced and knowledgeable. Something genuinely helpful and informative might come out of it.

                                I plan on staying tuned - hopeful of learning something.