I hope you just read the rating on the side of the CT to know what their ratio.
It is the secondary value that determines if they are compatible with the metering device. Common inputs to meter are 1 amp, 5 amp or 333mv.
The primary value will just determine if you are in the bottom, middle or upper part of the measuring scale.Comment
Unfortunatelly, that's not even close and the actual value does not fall anywhere near the typical bracketsComment
I have been purchasing and use CT's for a long time and unless the requirement is very unique most meters accept the 3 standard input values I mentioned.Comment
Are you familiar with the CT-200 that Enphase used for there metering. The only information I can find shows what I think is a 200A to 500mv ratio but I am not sure if that 0.5V is a maximum rating or the actual input requirement to the Enphase meter.Comment
We do a lot of solaredge installs and many with consumption meter. We have often had to use Rogowski coils for these installs as well as with FLEX energy hubs.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
200A@0.4VComment
The Enphase meter may work using a 333mv or .333v input. Sometimes a meter manufacturer provides the max input values but allows you to go a little lower. The problem would be the accuracy could suffer.Comment
You might be right on them wanting you to only use their equipment. Although Flex Core does make some nice and affordable CT's with many different ratios.
there are a few listed on hqmeter with 0.4V output. like the JC16F, JC24F, etc.
http://www.hqmeter.com/split-core-ct.html
which is why I ended up with the custom unit build to my specs