    working space 110.26

    Is there a problem here regarding on working space? i'm adding a new disconnect in an electrical room. Thank you!
    Attached Files
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    AFIK, 3 foot clear in front of every elect panel, for the fireman to swing an Ax !!
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • azdave
      Moderator
      • Oct 2014
      • 803

      #3
      What looks good on paper might not be what your local inspector will accept and guess who has the final word during a review? If you have a local authority who has to sign off on that work then that is who I would be asking for approval to be sure.
      Dave W. Gilbert AZ
      6.63kW grid-tie owner

      Comment

      • solarix
        Super Moderator
        • Apr 2015
        • 1415

        #4
        I once went through a lot of grief in that same situation because the utility meter reader refused to approve it even though the utility plan checkers did. Utilities get to make their own rules when it comes to service installation so be sure and brush up on this phrase: "yez Master, I does what you sez"
        BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15202

          #5
          Originally posted by solarix
          I once went through a lot of grief in that same situation because the utility meter reader refused to approve it even though the utility plan checkers did. Utilities get to make their own rules when it comes to service installation so be sure and brush up on this phrase: "yez Master, I does what you sez"
          I agree. Someone can follow the NEC to the letter but it still comes down to the AHJ who will determine what is good and what isn't. On another aspect if you keep at least 3 foot clearance between an energized bus, wire or terminal and a grounded surface (like a wall or another metal panel) you should be ok. But again it is the AHJ the will say if even that is good.