Your battery vent will do little since the batteries are not boxed, the hydrogen will just rise above it.
You state you you are not worried about the 48v but are about the 600, you should be far more worried about the 48v as it has var more amp potential and flash arc concern, particularly at the terminals which are infused
a batter box or cover would solve both problems.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
Your battery vent will do little since the batteries are not boxed, the hydrogen will just rise above it.
You state you you are not worried about the 48v but are about the 600, you should be far more worried about the 48v as it has var more amp potential and flash arc concern, particularly at the terminals which are infused
a batter box or cover would solve both problems.