Microinverter Surge Protection

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Samsolar
    Member
    • Dec 2014
    • 77

    #1

    Microinverter Surge Protection

    I'm looking to get ideas from people regarding surge protection for a 30 panel install with Enphase M215's

    I'd like to know what you installed (or have seen installed) and where it was installed. I've only found a couple of installs that mention SPDs and in both cases they used Citel's product within the Soladeck box on the roof. Installing within the attic (16" from the Soladeck) or by the main panel would be easier for access, by obviously less than ideal being further from the panels/inverters.

    I'm also curious if people just aren't installing these as they don't seem to be mentioned much in install write ups or offered by online stores.

    Thanks in advance!

    Scott
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    With both the panels and inverters (electronics) up on the roof, lightning protection is nearly impossible. You can install a couple SPD's at the main power meter, anything more requires a tall tower on either side of your house, with a ground cable between them.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #3
      Play the numbers. Stats and chances are 95% of all electrical abnormalities come via your power line in the Differential Mode of operation. The best location for a TVSS is installed right at the Meter Can installed by your POCO. Otherwise look for units that have at least:

      (a) UL 1449 Second Edition listed.
      (b) SVR of 400V or less.
      (c) Rated for 70,000A per phase..
      (d) Have indicator lights and/or audible alarm indicating the device is functional.
      MSEE, PE

      Comment

      • DanS26
        Solar Fanatic
        • Dec 2011
        • 1001

        #4
        In addition, some utilities will install an SPD right on the transformer can. If you are really concerned about lightning induced voltage spikes, might be worth a call to the POCO to inquire.