Again, thanks to everyone. There's some good things on the web about wire management of PV installations, but the code is a little scant. There are some developed lines of interpretation that require all PV wires be carefully bundled, which is certainly what I like to see. In any case, it's true that they have to be secured/supported at certain intervals, but single-conductors fall in a weird category, since of course they are generally not allowed at all, so they aren't documented as well as all the cable types, for example.
PV wires on roof surface
Collapse
X
-
-
Again, thanks to everyone. There's some good things on the web about wire management of PV installations, but the code is a little scant. There are some developed lines of interpretation that require all PV wires be carefully bundled, which is certainly what I like to see. In any case, it's true that they have to be secured/supported at certain intervals, but single-conductors fall in a weird category, since of course they are generally not allowed at all, so they aren't documented as well as all the cable types, for example.
Comment
-
Again, thanks to everyone. There's some good things on the web about wire management of PV installations, but the code is a little scant. There are some developed lines of interpretation that require all PV wires be carefully bundled, which is certainly what I like to see. In any case, it's true that they have to be secured/supported at certain intervals, but single-conductors fall in a weird category, since of course they are generally not allowed at all, so they aren't documented as well as all the cable types, for example.
Since the link was not approved I will just state that you can check out the article at Electrical Wholesaling. The clips are called "Ty-Rap High Performance Cable Edge Clips" made by T&B which are sized for the #10 awg PV cables and come in a few different orientations.Comment
-
What made you think that the link was not "approved" ? I see it fine and am able to click it in your first post.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
Since I do not see that post I thought it had been rejected for some reason.Comment
-
It takes some time for a moderator to notice the status of the post and approve it. (We can see it in the normal thread flow even before it is accepted, it just has a status icon that marks it as needing moderation action. This filtering on content and directing to moderation, even for regular users, is a new feature of the software that we are experimenting with.
Time will tell if we will keep it active, especially since it only seems to be catching about half of the spam posts.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
OK.
It takes some time for a moderator to notice the status of the post and approve it. (We can see it in the normal thread flow even before it is accepted, it just has a status icon that marks it as needing moderation action. This filtering on content and directing to moderation, even for regular users, is a new feature of the software that we are experimenting with.
Time will tell if we will keep it active, especially since it only seems to be catching about half of the spam posts.Comment
-
Comment
-
Pictures? You want pictures?
1941 Capitol Ave. NE 8.28.14c_800x600.jpg1941 Capitol Ave. NE 8.28.14e_450x600.jpg
These actually show a combination of USE-2 wires on the roof, AND THHN/wire nuts outside of a box (THHN isn't even rated for a wet location). Anyway, that one's a no-brainer, it's the loose wires I'm determining the proper course for.Comment
-
[ATTACH=CONFIG]4772[/ATTACH][ATTACH=CONFIG]4773[/ATTACH]
These actually show a combination of USE-2 wires on the roof, AND THHN/wire nuts outside of a box (THHN isn't even rated for a wet location). Anyway, that one's a no-brainer, it's the loose wires I'm determining the proper course for.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
[ATTACH=CONFIG]4772[/ATTACH][ATTACH=CONFIG]4773[/ATTACH]
These actually show a combination of USE-2 wires on the roof, AND THHN/wire nuts outside of a box (THHN isn't even rated for a wet location). Anyway, that one's a no-brainer, it's the loose wires I'm determining the proper course for.
1. Inspector and Wife are always right!
2. When Inspector or Wife are in error, refer to rule #1
If you buck those two rules you are screwed.MSEE, PEComment
-
Maybe this will help. With 35 years of experience here is what I have learned to live by. The two golden rules for Inspectors and Wives.
1. Inspector and Wife are always right!
2. When Inspector or Wife are in error, refer to rule #1
If you buck those two rules you are screwed.Comment
-
Maybe this will help. With 35 years of experience here is what I have learned to live by. The two golden rules for Inspectors and Wives.
1. Inspector and Wife are always right!
2. When Inspector or Wife are in error, refer to rule #1
If you buck those two rules you are screwed.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
Maybe this will help. With 35 years of experience here is what I have learned to live by. The two golden rules for Inspectors and Wives.
1. Inspector and Wife are always right!
2. When Inspector or Wife are in error, refer to rule #1
If you buck those two rules you are screwed.Comment
-
Those wires in the first picture look like they have wire nuts and tape. That has to be a code violation. No way are splices allowed outside a box in a wet environment like the roof.Comment
Comment