PV wires on roof surface

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • GreenCodeInspector
    Junior Member
    • Aug 2014
    • 10

    #16
    Again, thanks to everyone. There's some good things on the web about wire management of PV installations, but the code is a little scant. There are some developed lines of interpretation that require all PV wires be carefully bundled, which is certainly what I like to see. In any case, it's true that they have to be secured/supported at certain intervals, but single-conductors fall in a weird category, since of course they are generally not allowed at all, so they aren't documented as well as all the cable types, for example.

    Comment

    • SunEagle
      Super Moderator
      • Oct 2012
      • 15192

      #17
      Originally posted by GreenCodeInspector
      Again, thanks to everyone. There's some good things on the web about wire management of PV installations, but the code is a little scant. There are some developed lines of interpretation that require all PV wires be carefully bundled, which is certainly what I like to see. In any case, it's true that they have to be secured/supported at certain intervals, but single-conductors fall in a weird category, since of course they are generally not allowed at all, so they aren't documented as well as all the cable types, for example.
      I saw this ad yesterday showing a clip to keep PV wires secured.

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15192

        #18
        Originally posted by GreenCodeInspector
        Again, thanks to everyone. There's some good things on the web about wire management of PV installations, but the code is a little scant. There are some developed lines of interpretation that require all PV wires be carefully bundled, which is certainly what I like to see. In any case, it's true that they have to be secured/supported at certain intervals, but single-conductors fall in a weird category, since of course they are generally not allowed at all, so they aren't documented as well as all the cable types, for example.
        I tried to add a link for a new type of cable clip that retains the PV wire being run from and under the panels.

        Since the link was not approved I will just state that you can check out the article at Electrical Wholesaling. The clips are called "Ty-Rap High Performance Cable Edge Clips" made by T&B which are sized for the #10 awg PV cables and come in a few different orientations.

        Comment

        • inetdog
          Super Moderator
          • May 2012
          • 9909

          #19
          What made you think that the link was not "approved" ? I see it fine and am able to click it in your first post.
          SunnyBoy 3000 US, 18 BP Solar 175B panels.

          Comment

          • SunEagle
            Super Moderator
            • Oct 2012
            • 15192

            #20
            Originally posted by inetdog
            What made you think that the link was not "approved" ? I see it fine and am able to click it in your first post.
            When I first posted on Tuesday with the link to the EW website showing the clip I got a pop up that stated my post would be reviewed and if approved by the moderators then it would be shown.

            Since I do not see that post I thought it had been rejected for some reason.

            Comment

            • inetdog
              Super Moderator
              • May 2012
              • 9909

              #21
              Originally posted by SunEagle
              When I first posted on Tuesday with the link to the EW website showing the clip I got a pop up that stated my post would be reviewed and if approved by the moderators then it would be shown.

              Since I do not see that post I thought it had been rejected for some reason.
              OK.
              It takes some time for a moderator to notice the status of the post and approve it. (We can see it in the normal thread flow even before it is accepted, it just has a status icon that marks it as needing moderation action. This filtering on content and directing to moderation, even for regular users, is a new feature of the software that we are experimenting with.
              Time will tell if we will keep it active, especially since it only seems to be catching about half of the spam posts.
              SunnyBoy 3000 US, 18 BP Solar 175B panels.

              Comment

              • SunEagle
                Super Moderator
                • Oct 2012
                • 15192

                #22
                Originally posted by inetdog
                OK.
                It takes some time for a moderator to notice the status of the post and approve it. (We can see it in the normal thread flow even before it is accepted, it just has a status icon that marks it as needing moderation action. This filtering on content and directing to moderation, even for regular users, is a new feature of the software that we are experimenting with.
                Time will tell if we will keep it active, especially since it only seems to be catching about half of the spam posts.
                I guess I was targeted as a spammer.

                Comment

                • inetdog
                  Super Moderator
                  • May 2012
                  • 9909

                  #23
                  Originally posted by SunEagle
                  I guess I was targeted as a spammer.
                  If it walks like a duck....
                  SunnyBoy 3000 US, 18 BP Solar 175B panels.

                  Comment

                  • GreenCodeInspector
                    Junior Member
                    • Aug 2014
                    • 10

                    #24
                    Pictures? You want pictures?

                    1941 Capitol Ave. NE 8.28.14c_800x600.jpg1941 Capitol Ave. NE 8.28.14e_450x600.jpg

                    These actually show a combination of USE-2 wires on the roof, AND THHN/wire nuts outside of a box (THHN isn't even rated for a wet location). Anyway, that one's a no-brainer, it's the loose wires I'm determining the proper course for.

                    Comment

                    • inetdog
                      Super Moderator
                      • May 2012
                      • 9909

                      #25
                      Originally posted by GreenCodeInspector
                      [ATTACH=CONFIG]4772[/ATTACH][ATTACH=CONFIG]4773[/ATTACH]

                      These actually show a combination of USE-2 wires on the roof, AND THHN/wire nuts outside of a box (THHN isn't even rated for a wet location). Anyway, that one's a no-brainer, it's the loose wires I'm determining the proper course for.
                      Most THHN you find is actually dual-rated to THWN or THWN-2, not that that makes it any better outside of a raceway or exposed to sunlight.
                      SunnyBoy 3000 US, 18 BP Solar 175B panels.

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #26
                        Originally posted by GreenCodeInspector
                        [ATTACH=CONFIG]4772[/ATTACH][ATTACH=CONFIG]4773[/ATTACH]

                        These actually show a combination of USE-2 wires on the roof, AND THHN/wire nuts outside of a box (THHN isn't even rated for a wet location). Anyway, that one's a no-brainer, it's the loose wires I'm determining the proper course for.
                        Maybe this will help. With 35 years of experience here is what I have learned to live by. The two golden rules for Inspectors and Wives.

                        1. Inspector and Wife are always right!
                        2. When Inspector or Wife are in error, refer to rule #1

                        If you buck those two rules you are screwed.
                        MSEE, PE

                        Comment

                        • J.P.M.
                          Solar Fanatic
                          • Aug 2013
                          • 15051

                          #27
                          Originally posted by Sunking
                          Maybe this will help. With 35 years of experience here is what I have learned to live by. The two golden rules for Inspectors and Wives.

                          1. Inspector and Wife are always right!
                          2. When Inspector or Wife are in error, refer to rule #1

                          If you buck those two rules you are screwed.
                          Or at least w/wife, probably not.

                          Comment

                          • inetdog
                            Super Moderator
                            • May 2012
                            • 9909

                            #28
                            Originally posted by Sunking
                            Maybe this will help. With 35 years of experience here is what I have learned to live by. The two golden rules for Inspectors and Wives.

                            1. Inspector and Wife are always right!
                            2. When Inspector or Wife are in error, refer to rule #1

                            If you buck those two rules you are screwed.
                            Which I guess GreenCodeInspector (I assume Green as in inexperienced rather than Green as in environmentally obsessed) will get to apply that from the inspector's side. I am sure that if somebody asks him for a Code section citation, he can just refer them to you.
                            SunnyBoy 3000 US, 18 BP Solar 175B panels.

                            Comment

                            • J.P.M.
                              Solar Fanatic
                              • Aug 2013
                              • 15051

                              #29
                              Originally posted by Sunking
                              Maybe this will help. With 35 years of experience here is what I have learned to live by. The two golden rules for Inspectors and Wives.

                              1. Inspector and Wife are always right!
                              2. When Inspector or Wife are in error, refer to rule #1

                              If you buck those two rules you are screwed.
                              When I was a sales rep., I never won an argument with a customer. Never started one. There are other ways to get what needs to be accomplished. Later, as an engineer, I remembered some of what I learned as a peddler when dealing with inspectors/Q.C. folks. They may not be right, but they're always going to inspect. There are other ways.

                              Comment

                              • SunEagle
                                Super Moderator
                                • Oct 2012
                                • 15192

                                #30
                                Originally posted by inetdog
                                Most THHN you find is actually dual-rated to THWN or THWN-2, not that that makes it any better outside of a raceway or exposed to sunlight.
                                Those wires in the first picture look like they have wire nuts and tape. That has to be a code violation. No way are splices allowed outside a box in a wet environment like the roof.

                                Comment

                                Working...