Thanks for the info inetdog!
The Citel SPDs are primarily MOV devices. Citel specifies that they should be connected between hot and EGC, as close to the array as possible. They make a different device that's meant to be connected between Neutral and GEC. However, my array currently doesn't have a GEC; my contractor said that it wasn't required. I'll have to check if I can place that between Neutral and EGC instead. My inverters are also the internally grounded variant which Enphase first introduced on the M250 then retrofitted to the M215 as well.
The Citel SPDs are primarily MOV devices. Citel specifies that they should be connected between hot and EGC, as close to the array as possible. They make a different device that's meant to be connected between Neutral and GEC. However, my array currently doesn't have a GEC; my contractor said that it wasn't required. I'll have to check if I can place that between Neutral and EGC instead. My inverters are also the internally grounded variant which Enphase first introduced on the M250 then retrofitted to the M215 as well.