    New member with a question about connecting a generator

    Hello! Greetings to all! I'm just joined the forum a few days ago.

    I have a grid-connected Xantrex system with battery backup. The inverter is model XW6048 and the solar charge controller is the XW-MPPT60. The inverter supplies 240V (two 120V phases) to the house and have an AC input for a generator.

    I also have a small 120V generator that I use after storms (I live in Puerto Rico) when the batteries run out of charge.

    According to the inverter's manual a 240V 2-phase generator is expected on the AC input. My question is: if I switch the inverter to "bypass", can I use my 1-phase generator, connected to the two AC phases of the inverter to supply power to the house, without damaging the inverter? I want is to supply power to the 120V loads with the generator and understand that any 240V load will not work when connected in this way.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    When you switch the breakers to bypass (the inverter does not have a bypass switch, that's in the electrical panel) your 120V generator will only be powering HALF your breakers.

    Here's the best pic I was able to find, of how a split phase breaker box works. Generally, the hot wires (2) are called Line 1 and Line 2 ( not hot 1 hot2 as the pic shows)

    Getting a larger generator that produces 240V split phase, is a preferred solution,

    ws0mU.jpg
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Matoqui
      Junior Member
      • Jul 2020
      • 3

      #3
      Thanks very much for your answer! What I was thinking was to apply the generator output (120V) to both "Hot1" and "Hot2" so that all the house breakers receive power. The 240V breakers are non-critical loads and I assume will not receive power from the generator

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        If you rig something to join the 2 hot wires, you are really risking a failure when grid returns and somebody forgets about the jumper. Even if you build it into the transfer switch = out of sight-out of mind and someday a 240V generator is going to get hooked up. Just step up to a 8kw generator w/240 output and keep that simple. or get a step-up transformer

        > According to the inverter's manual a 240V 2-phase generator is expected on the AC input.
        > My question is: if I switch the inverter to "bypass", can I use my 1-phase generator, connected
        > to the two AC phases of the inverter to supply power to the house, without damaging the inverter?
        NO. The inverter has a big heavy transformer inside, connected across L1 & L2 if you short L1-2 somewhere, something will smoke.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • Matoqui
          Junior Member
          • Jul 2020
          • 3

          #5
          Definitely not a good idea then! Thanks very much!

          Comment

          Working...