Announcement

Collapse
No announcement yet.

Tesla to build battery in South Australia

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • Tesla to build battery in South Australia

    Hi All,

    Have you heard that Tesla is going to build the worlds biggest battery right here in little ol; South Oz, and he said if he doesn't build it in 100 days its free

    https://www.theguardian.com/australi...outh-australia
    WooHooo looks like we got a big free battery comming down under

  • #2
    100 calendar days or 100 work days ?
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment


    • #3
      This says it all. Sounds just like California.

      Repeated blackouts in SA since September have sparked a political brawl over energy policy
      Translated means our energy policy failed because we were to stupid to build power plants to meet demand.
      MSEE, PE

      Comment


      • #4
        Originally posted by Sunking View Post
        This says it all. Sounds just like California.



        Translated means our energy policy failed because we were to stupid to build power plants to meet demand.
        I give up, this is hopeless- politics over engineering in high technology field

        Comment


        • #5
          Originally posted by max2k View Post

          I give up, this is hopeless- politics over engineering in high technology field
          But in the end, that's just the way it was in the beginning, is now and ever shall be, be world without end. Amen. Looks like you don't yet know how the game is run.

          Comment


          • #6
            Originally posted by max2k View Post
            I give up, this is hopeless- politics over engineering in high technology field
            It's not all bad news. wattclarity.com.au/2017/03/lets-talk-about-fcas/ has some information about the situation, and links to reports about the outage. Sounds like they're reacting appropriately by enlisting more power stations (even wind farms!) to provide frequency control ancillary services, and not just by adding a big battery.

            Comment


            • #7
              Originally posted by J.P.M. View Post

              But in the end, that's just the way it was in the beginning, is now and ever shall be, be world without end. Amen. Looks like you don't yet know how the game is run.
              Let's say I have a feeling but I don't know details, that's true. That feeling is quite enough not to have illusions

              Comment


              • #8
                Originally posted by DanKegel View Post

                It's not all bad news. wattclarity.com.au/2017/03/lets-talk-about-fcas/ has some information about the situation, and links to reports about the outage. Sounds like they're reacting appropriately by enlisting more power stations (even wind farms!) to provide frequency control ancillary services, and not just by adding a big battery.
                not sure I understand how frequency control can help with situation: if there's not enough energy to supply loads changing frequency wouldn't create it unless of course additional sources are connected to adjust the frequency and that has 'side effect' of adding energy to the grid. I was under impression that when grid doesn't have enough supply its output voltage would sag. Looks like it's not the case.

                Comment


                • #9
                  When the grid falls short of overall power, voltage starts to sag, and that starts to affect the RPM of the generators, and the frequency starts to try to change. At some point, the phase locking between different generating units starts to drift and the system then starts to dump " out of spec" generators. This starts the cascade of overloaded generators start to slow down and get booted off the grid, leaving the other generators overloaded and they get booted off too. Only takes a couple seconds to loose it all.
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment


                  • #10
                    Originally posted by solar pete View Post
                    Hi All,

                    Have you heard that Tesla is going to build the worlds biggest battery right here in little ol; South Oz, and he said if he doesn't build it in 100 days its free

                    https://www.theguardian.com/australi...outh-australia
                    WooHooo looks like we got a big free battery comming down under
                    Come on Pete. You know nothing is really free. Some how someone will be paying for that battery. If it isn't Australia it will be the US which will find a way to transfer the debt to someone else.

                    Comment


                    • #11
                      Originally posted by max2k View Post

                      not sure I understand how frequency control can help with situation: if there's not enough energy to supply loads changing frequency wouldn't create it unless of course additional sources are connected to adjust the frequency and that has 'side effect' of adding energy to the grid. I was under impression that when grid doesn't have enough supply its output voltage would sag. Looks like it's not the case.
                      Dan can not answer any question related to electric power.

                      MSEE, PE

                      Comment


                      • #12
                        Originally posted by max2k View Post
                        not sure I understand how frequency control can help with situation: if there's not enough energy to supply loads changing frequency wouldn't create it unless of course additional sources are connected to adjust the frequency and that has 'side effect' of adding energy to the grid. I was under impression that when grid doesn't have enough supply its output voltage would sag. Looks like it's not the case.
                        No you were on the right track until Dan opened his mouth with more non sense. All of the largest power outages in the USA are caused by what is called Under Frequency Disconnects. In the utility biz is called URD (Under Frequency Relay Disconnect) When a generator is over loaded, the load slows the generator down, thus the frequency slows down and voltage sags. Now if it were just one generator would not be a huge problem. However the grid is not just one generator. There are hundreds of them all connected together and in SYNC. So if just one generator slows down and out of sync, The shift in phase angle causes potential differences in the system which in turn cause very large amounts of current in the Generator, transformers, and transmission equipment. To prevent a huge MELTDOWN, the generator shuts down to save itself. That has a domino effect. When one generator shuts down without notice, that loads down adjacent generators and they trip. It can blackout a major portion of a country like the USA has experienced.

                        Look up Blackout of 1965 in the Northeast. 80,000 square miles and 30 million people out of power for 13 hours. After that Black Out Texas disconnected from the national grid and has never reconnected and never will. The only way TX connects to the rest of the world is via HVDC. The whole country could Black Out, but TX will still have lights on. There is no AC connection. TX is an exporter of energy and completely energy independent.

                        So while you think what I said was political, and you think it is engineering. Well both are true. Australia Energy Policy stopped the country from building power plants. Now they are paying the price for a failed Energy Policy. The right solution is to build power plants, not add some huge expensive battery making the crooked manufacture rich. That is pure politics.
                        Last edited by Sunking; 07-22-2017, 11:43 AM.
                        MSEE, PE

                        Comment


                        • #13
                          Originally posted by Sunking View Post

                          No you were on the right track until Dan opened his mouth with more non sense. All of the largest power outages in the USA are caused by what is called Under Frequency Disconnects. In the utility biz is called URD (Under Frequency Relay Disconnect) When a generator is over loaded, the load slows the generator down, thus the frequency slows down and voltage sags. Now if it were just one generator would not be a huge problem. However the grid is not just one generator. There are hundreds of them all connected together and in SYNC. So if just one generator slows down and out of sync, The shift in phase angle causes potential differences in the system which in turn cause very large amounts of current in the Generator, transformers, and transmission equipment. To prevent a huge MELTDOWN, the generator shuts down to save itself. That has a domino effect. When one generator shuts down without notice, that loads down adjacent generators and they trip. It can blackout a major portion of a country like the USA has experienced.

                          Look up Blackout of 1965 in the Northeast. 80,000 square miles and 30 million people out of power for 13 hours. After that Black Out Texas disconnected from the national grid and has never reconnected and never will. The only way TX connects to the rest of the world is via HVDC. The whole country could Black Out, but TX will still have lights on. There is no AC connection. TX is an exporter of energy and completely energy independent.

                          So while you think what I said was political, and you think it is engineering. Well both are true. Australia Energy Policy stopped the country from building power plants. Now they are paying the price for a failed Energy Policy. The right solution is to build power plants, not add some huge expensive battery making the crooked manufacture rich. That is pure politics.
                          Interesting, never really looked into how grid operates and why blackouts happen. Thank you for the detailed explanation.

                          Comment


                          • #14
                            I'm going to present my analogy of the grid generation and a blackout.

                            Imagine dozens of horses in a big harness, pulling a big load. Another horse might run to catch up, hook
                            up, and help pull. Its easy for a horse to catch up without a load. Once hooked up, a horse is never going
                            to pull ahead of the other horses, because he isn't strong enough to pull the load alone; they stay "in sync".

                            When a generator was to go online, it would be spun up under no load, and a light bulb placed across the
                            connect switch. As the generator drifts in and out of phase, the bulb will go from bright out of phase to
                            black when in phase (no difference in voltage). When the light is out, the switch is closed and the throttle
                            thrown open. The generator will pick up load according to its capacity and throttle. It won't get ahead
                            (out of phase), because the load is too much for it to carry alone. It stays "in the harness" with the others.

                            A load increase tends to slow the generators, lowering the frequency. All the governors are very sensitive
                            to frequency, and will increase the throttle to maintain frequency (60 HZ here). If the load starts to reach
                            generation capacity, some throttles will reach their maximum position. More load may cause ALL the
                            throttles to be at max, if additional sources aren't brought in. At that point its on the brink. Any more load
                            will cause the frequency to start dropping. The only thing that can save the system is to cut off some loads,
                            an extremely disruptive action. If the frequency drops very much, the system will be unable to operate
                            and equipment will start to shut down. Once a generator quits, the rest will soon follow, blackout.

                            Its tough to restart from a blackout. All the coolers, sump pumps, wells, and other motors that normally
                            run intermittently, are sitting there waiting to throw a huge starting surge on the line, all at once.

                            One way to reduce the load is gradually reduce the voltage. This is very bad for some loads, esp induction
                            motors. MAYBE a brownout will avoid a blackout.

                            Bruce Roe
                            Last edited by bcroe; 07-22-2017, 05:16 PM.

                            Comment


                            • #15
                              Originally posted by bcroe View Post
                              Its tough to restart from a blackout.
                              It is more than tough. The POCO has to go every Cut Out Switch in the network and open. That is manually done with Hot Sticks. All Sub Stations will have their Switches open and that is mostly done electronically with SCADA from a control center. From the generation plant they close in the first distribution sub-station. Then one by one reclose the Cut-Out switches manually. Then the next Distribution sub-station is closed in and the process repeats until every thing is reconnected.

                              Reason is simple as you pointed out. If you tried to connect the generator with all that load would cause it to trip off again. You have to walk-in the load, and that can take a few days.

                              MSEE, PE

                              Comment

                              Working...
                              X